Shaded Pole Motor Speed

01/22/2015 7:23 AM

I have a shaded pole motor rated as 240 V/50 Hz,50 mA . Its full load speed is 2750 rpm.

I need to increase its rotational speed, so i plugged it to 240 V/ 60 Hz . As the v/hz ratio is decreasing, i thought the operation is safe and actually it was. But problem is at 60 Hz its speed become less than 50 Hz (2400 RPM). I don't understand the reason for this type of motor behavior. Can anybody explains this to me?? Thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
5
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#1

Re: Shaded pole motor speed.

01/22/2015 7:37 AM

Everything else being equal, it should run faster (unloaded) on 60 Hz. The torque would be less because the current draw is less. If there is a load on the motor, it might be that the lower torque is causing it to run slower.

Any mechanical load has a torque vs speed curve. The motor also has a torque vs speed curve. The speed of the motor with a load is where motor torque equals load torque.

Register to Reply Good Answer (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2
In reply to #1

Re: Shaded pole motor speed.

01/22/2015 8:17 AM

Sounds good to me. I expect everything else will not be equal. I expect the current will not be the same. I suspect an oscilloscope with either a shunt or clamp on ammeter will show that the real power produced will be close to the same because the mechanical load is too big for this motor. I suspect the mechanical load was already creating too much slip at 50 HZ. Increasing only the frequency just created more slip and a very slight decrease in current.

Just to be clear, I'm reinforcing your answer not refuting it.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Participant

Join Date: Jan 2015
Posts: 4
#11
In reply to #1

Re: Shaded pole motor speed.

01/23/2015 1:40 AM

Thanks a lot buddy... but why should the current will deceases at 60 Hz?? can you please explain ???

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#12
In reply to #11

Re: Shaded pole motor speed.

01/23/2015 3:33 AM

Because, being based upon coils of wire, the motor is an inductor. The impedance of inductors increases with frequency, so the current reduces, and available torque is proportional to current. If the torque that your load presents to the motor increases with speed, then the motor will slow down to a place where the load torque and the available motor torque are matched. And that's where it will stay.

Basically, you've now got a mismatch between the motor and the load. A gearbox won't help, so you need to change the motor, which is where you should have started.

__________________
Good moaning!
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jan 2015
Posts: 4
#13
In reply to #12

Re: Shaded pole motor speed.

01/23/2015 3:42 AM

Thanks again.. ok , i will do what you suggested....

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#3

Re: Shaded pole motor speed.

01/22/2015 8:19 AM

carefully worded homework

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4
In reply to #3

Re: Shaded pole motor speed.

01/22/2015 9:19 AM

Very possibly true. However, a carefully reworded homework problem shows that the student does think. Just not clearly enough, yet. I'll help to lift a veil or two for somebody that is showing effort.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Shaded pole motor speed.

01/22/2015 9:48 AM

If it is in overload, as suggested by #1, then its behaviour would suggest that its existing overload protection arrangements are inadequate. If it is run in this way for any period of time, expect it to burn out and need changing for a correctly-rated replacement. In any case, review the protection arrangements and ensure they are appropriate for the motor.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #5

Re: Shaded pole motor speed.

01/22/2015 11:13 AM

This is a shaded pole motor not a water pump motor. Frequently a shaded pole motor (think fan motor) will not need any protection because the heat produced by a locked rotor condition will not overheat the motor with no forced air motion.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7

Re: Shaded Pole Motor Speed.

01/22/2015 6:01 PM

It would seem the motor is undersized...try a PSC motor....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8
In reply to #7

Re: Shaded Pole Motor Speed.

01/22/2015 11:44 PM

His motor is 50mA, about 8.4W or 0.01HP. I doubt there is a PSC motor made that small, in fact I doubt there is any other type of AC motor made that small...

I'd venture to say that this is a muffin fan on the back of his PC, and he has over clocked his CPU, which is making it over heat. So rather than buy a larger fan, he is trying to push more air with it.

When you increase the speed of a fan like that, the load it expresses on the motor increases at the CUBE of the speed change. So just increasing the speed by 20%, the load that the fan impresses on the motor becomes 1.2 cubed, so 172% of what it was. Given that the wires are likely marginally sized, I'd say that the increased speed is causing the fan motor to overload, draw too much current, which drops the voltage due to the overheated wire, then drops the torque of the motor even further until is almost (or will eventually) stall.

There ain't no free lunch. Need to move more air? Buy a bigger muffin fan.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 5)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#9
In reply to #8

Re: Shaded Pole Motor Speed.

01/23/2015 1:10 AM

Yes you are quite right, I didn't read the question properly....maybe something like this...

http://www.newegg.com/Product/Product.aspx?Item=N82E16835553002&cm_sp=Cat-Fans-PC-Cooling_3-_-Pillars-_-COUGAR-CF-V12HP_3

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Participant

Join Date: Jan 2015
Posts: 4
#10
In reply to #8

Re: Shaded Pole Motor Speed.

01/23/2015 1:15 AM

Hell Yeah.... thank you very much...

Register to Reply Off Topic (Score 5)
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); Fredski (1); Hasibul Jamil (3); JRaef (1); PWSlack (1); redfred (3); Rixter (1); SolarEagle (2)