Transformer Turn Ratio Deviation

01/23/2015 7:45 AM

Dear All,

We have tested TURN RATIO for many distribution trasnformers last week and the percentage difference was found less than 0.5% and as per my assumption the results are ok. but our consultant is asking to submit him some IEC or IEEE standard reference. will anyone can help me from where I can get the standard reference?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#1

Re: Transformer Turn Ratio Deviation

01/24/2015 12:10 AM

60076-1 Power transformers -Part 1: General Table 1 - Tolerances

2. Voltage ratio at no load on principal tapping for a specified first pair of windings

The lower of the following values:

a) ±0,5 % of declared ratio

b) ±1/10 of the actual percentage impedance on the

principal tapping

Voltage ratio on other tappings, same pair and

Voltage ratio for further pairs:

To be agreed, but not less than the lesser of the values

in a) and b) above.

__________________
Julius
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Aug 2008
Posts: 19
#2
In reply to #1

Re: Transformer Turn Ratio Deviation

01/24/2015 12:28 AM

Dear Julius, Thanks a lot. I appreciate your assistance. Thanks once again.