Principle And Operational Working For Electronic Drum Level Indicator

02/02/2015 5:52 AM

What is measuring principle and operational working for Electronic Drum level Indicator/ Hydrastep for Boiler Drum?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: principle and operational working for Electronic Drum level Indicator

02/02/2015 5:54 AM

Dunno. What did the manufacturer say when you called?

__________________
Good moaning!
Register to Reply
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#2

Re: Principle And Operational Working For Electronic Drum Level Indicator

02/02/2015 8:54 AM

Google: three element drum level control

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Principle And Operational Working For Electronic Drum Level Indicator

02/02/2015 10:23 AM

Do some basic research, on your own!

Then, you will posses knowledge, not just questions.

Here's a start:

Electronic Drum Level Indicator - YouTube

I hope this helped you, as much as it did me.

Register to Reply
Associate

Join Date: Oct 2014
Posts: 25
#6
In reply to #4

Re: Principle And Operational Working For Electronic Drum Level Indicator

02/03/2015 10:25 PM

Thank you Hilton

Register to Reply
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#7
In reply to #6

Re: Principle And Operational Working For Electronic Drum Level Indicator

02/04/2015 5:23 AM

Your'e welcome!

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#5

Re: Principle And Operational Working For Electronic Drum Level Indicator

02/03/2015 1:04 PM

It's all pretty much based on light, mirrors, and transmission of said light through the column of either steam or water in a gauge glass of a boiler. If the water is present, one source ( typically red ) will be transmitted through for that "bulb", and if not, then the other one (typically green) will transmit through. It tells approximate water level in the steam drum without having to go physically look at the gauge glass.

The other way to do this is with a calibrated differential pressure gauge where one leg is full to the normal top attachment for where a gauge glass would be, and the other is direct coupled to the bottom level of said gauge glass port. The difference in column pressures is XMT to the control room, and the HMI sorts it out as to what that means in terms of boiler level, as in -12, 0, or +8.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Participant

Join Date: Mar 2015
Posts: 4
#8

Re: Principle And Operational Working For Electronic Drum Level Indicator

03/30/2015 4:16 PM

The Hydrastep uses conductivity to determine the water/steam interface. I work at Emerson, so let me know if you need anything more on this device.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Oct 2014
Posts: 25
#9
In reply to #8

Re: Principle And Operational Working For Electronic Drum Level Indicator

03/30/2015 11:35 PM

Thanks Lydia..

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#11
In reply to #9

Re: Principle And Operational Working For Electronic Drum Level Indicator

03/31/2015 9:30 AM

Yarway apparently offers the same electronic remote sensing of boiler drum level by conductivity probes, and also still offers the optical version of this also.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Participant

Join Date: Mar 2015
Posts: 4
#12
In reply to #9

Re: Principle And Operational Working For Electronic Drum Level Indicator

04/27/2015 5:24 PM

You are welcome.

There is also a short animation that shows how the hydrastep displays the information from the electrodes using the LEDs on the display. See page 4 at the bottom left if you are interested. http://mydigimag.rrd.com/publication/?i=220714

These have been around a long time and have not really changed. They have always been conductivity based, but they are made up of a water column with electrodes inserted at points along the column. If you are between points, you only know you are above one and below another. You don't know exactly where in between those two points you are. We have a white paper that talks about optimizing your control loop.

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#10
In reply to #8

Re: Principle And Operational Working For Electronic Drum Level Indicator

03/31/2015 9:09 AM

Maybe the new models of hydrastep use conductivity, but not the old ones, as they use the optical path to either deflect a beam of light or not. This is a discrete element type of sensor with a number of elements, so the operator only has an approximate actual level. Other drum level sensing is done based on differential pressure between an outside reference column filled with condensate, and the internal column that is the drum level actual.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 12 comments

"Almost" Good Answers: