Anonymous Poster #1

LV Cable Sizing.

02/04/2015 10:16 AM

Hi,

'Calculated load current' is coming as 695.6 amperes. How is 'calculated feeder rating' determined from it? This is a case of LV Cable Sizing.

Regs,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: LV Cable Sizing.

02/04/2015 10:57 AM

The calculated feeder rating is done by knowing the electrical wiring standard for your this location. Since you are neither certified to perform this calculation nor do you know enough to even tell us where you or this wiring are you are not capable of calculating this.

Why don't you try going to a medical forum and ask them how to safely remove a damaged appendix. This will only put one person at risk.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
Popular Science - Weaponology - New Member Fans of Old Computers - PDP 11 - New Member Technical Fields - Architecture - New Member Hobbies - HAM Radio - New Member

Join Date: Oct 2009
Location: Maine, USA
Posts: 2168
Good Answers: 71
#2

Re: LV Cable Sizing.

02/04/2015 10:57 AM
__________________
Tom - "Hoping my ship will come in before the dock rots!"
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: LV Cable Sizing.

02/04/2015 4:21 PM

Simples: using British Standard 7671 in this location.

Cable sizing is one of the Electrical section's most popular topics. It is inconceivable that entering the words "cable sizing" into the box on the right and searching will fail to turn up useful information, information that has been posted dozens of times before.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4
In reply to #3

Re: LV Cable Sizing.

02/04/2015 4:40 PM

Does British Standard 7671 also apply to high temperature superconductors immersed in a LN2 bath?

What about pulse circuit operation like a beam kicker magnet?

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: LV Cable Sizing.

02/04/2015 5:28 PM

One of the options is to obtain a copy, and actually read it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Participant

Join Date: Feb 2015
Posts: 2
#8
In reply to #4

Re: LV Cable Sizing.

02/06/2015 2:13 PM

I have read a few of your posts on here Redfred; and think you need to come down a peg or 10!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!

Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9
In reply to #8

Re: LV Cable Sizing.

02/06/2015 2:58 PM

Your first post here is to criticize a member with nothing to back your opinion.

Have you ever heard of Dale Carnegie?

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 5)
Participant

Join Date: Feb 2015
Posts: 2
#10
In reply to #9

Re: LV Cable Sizing.

02/08/2015 12:03 PM

I do not need to back anything up big head. Take a look at the way you reply to people!!!!!drag your head from out of your arse. If some one is asking for advice; you need not reply in an abrupt, over confident manner.

Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#11
In reply to #10

Re: LV Cable Sizing.

02/08/2015 3:00 PM

You certainly have a strange way to contribute to the community.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6

Re: LV Cable Sizing.

02/04/2015 6:20 PM

If you have to ask, you don't need to know.

Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7

Re: LV Cable Sizing.

02/05/2015 12:31 AM

See-for instance NEC Article 215, 215.2 Minimum Rating and Size. (A) Feeders Not More Than 600 Volts.

See-for instance- IEC 60364-5-52 Annex A Current-carrying capacities.

One could calculate the necessary cable conductor cross section for 100% load factor following IEC 60287 or Neher and McGrath method for different load factor. In this case you have to know if the cable runs: in open air-with or without sun exposure-in underground-how deep, what the RHO is, directly or in conduit or duct- and other important data. And, of course, what kind of cable will be employed-copper, pvc/xlpe/epr insulation, jacketed or not, serving or not and other.

__________________
Julius
Reply
Reply to Forum Thread 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); killer bee (2); lyn (1); PWSlack (2); redfred (4); Tom_Consulting (1)