Starting Large Motor 2MW with Captive Transformer Using Temporary Transformer

02/19/2015 4:01 AM

Dear all, I need some advices regarding to start large motor cooling water pump 2000kw, 3.3kV(detail info is listed below) using captive transformer 3500kVA (13.8kV/3.3kV).

And IMHO, captive trafo is supplied from temporary transformer 3000kVA (20kV/3.45kV) which sufficient to deliver starting motor 2000kW (I think), but not bigger than the captive tranformer 3500kVA,

This captive trafo also through using backfeed transformer 10MVA, 3.3kV/13.3kV (normal is step down Dyn-11, 13.8kV/3.45kV) which suppose to be use ground protection transformer or zig-zag trafo for delta side of the 10MVA trafo. With this starting scheme, is it sufficient to make start of this motor? Motor data: Pump driven for motor cooling water: 2000kW, BHP: 1760kw, spee: 600rpm, poles :10 LRC motor: 500% PF motor at starting : 0.2 Voltage: 3300kV, 3phase, 50Hz Full load amp: 458Amp temp rise:B Efficiency and pf: 95.5% and 80%at 100% I have calculated that it can work with using captive trafo 3500kV with detail below: Voltage: 13.8kV/3300kV Amp: 146.43/612.34 short circuit impedance: 4 Vector group: Dyn-11 This motor should be normal operated using STG 19MVA,13.8kV But within start up comm this captive trafo will be fed from backfed tranformer 10MVA,with detail data below: Voltage: 3450V/13.8kV Amp: 1673.48/418.37 short circuit impedance: 8%. Vector group: Dyn-11 This trandformer is also energized from temp trafo 3000kVA, with detail below: Voltage: 20000kV/3450kV Amp: 86.6/502.04 short circuit impedance: 7%. vector group: YNyn-6 The utility system is using 20kVA, with short circuit impedance 500MVA, Do you have any experience this scheme, and other advices will be welcome. Thank you, Athan activate javascript

Register to Reply
Pathfinder Tags: large motor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Starting Large Motor 2MW with Captive Transformer Using Temporary Transformer

02/19/2015 11:48 AM

Sounds like you're trying to blackstart a generating station by stringing together a group of sources, but without a SLD and a relaying/control schematic it's tough to follow your logic. It would also help if you labeled each transformer/bus so that the interconnections are more apparent. This is not an exercise for amateurs.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#2

Re: Starting Large Motor 2MW with Captive Transformer Using Temporary Transformer

02/19/2015 4:57 PM

First of all the utility system has to supply 20 kV,of course [not 20 kVA] and a short-circuit apparent power of 500 MVA. Let's try an approximate calculation:

Let's take the base voltage 3.3 kV then we get Zsystem=0.02178 ohm; ZT3MVA=0.2541; ZT1MVA= 0.8712 and ZT3.5MVA= 0.1245 ohm. If we take Zm=3.3/sqrt(3)/(0.458*5)=0.831989 ohm then the start current in this configuration will be [approx.]=3.3/sqrt(3)/2.1035=0.9058kA.

The voltage drop [considering X=Z] DV=SQRT(3)*0.9058*1.2715*SQRT(1-0.2^2)=1.9545[59%].

If you could supply directly from the temporary transformer of 20/3.3 kV then the voltage drop

would be 24% and there is a chance of successful starting.

__________________
Julius
Register to Reply Score 1 for Good Answer
Member

Join Date: Jan 2014
Posts: 6
#3

Re: Starting Large Motor 2MW with Captive Transformer Using Temporary Transformer

02/20/2015 1:02 AM

Too complicated ...but can be started with soft starter...

Register to Reply
Participant

Join Date: Feb 2015
Posts: 2
#4

Re: Starting Large Motor 2MW with Captive Transformer Using Temporary Transformer

02/20/2015 11:23 AM

Thank you 7anoter4, and siva.ee06,

It is good option to make temp power cable from 3.45kV, 3MVA through the motor, for minimizing, the voltage drop.

Siva.ee06, as I explained, I am middle of commissioning phase, that could not again running using soft starter.

Thx

Cheers

Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); atan15 (1); RAMConsult (1); siva.ee06 (1)

Previous in Forum: Reverse Power Protection   Next in Forum: 4017 & 555 Police LED Lights Project (noob question)

Advertisement