Device 87 Operation

02/20/2015 4:46 AM

Fellow engineers, please what will be some of the contributing factors that will cause a defferential relay ( device 87) to operate any time trying to close the breaker. But after continues trying for about 4 times, the breaker then closes and the votage regulator transformer stays.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: Device 87 operation

02/20/2015 8:48 AM

Perhaps it is designed to do that?

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#2

Re: Device 87 operation

02/20/2015 8:55 AM
__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Device 87 operation

02/20/2015 9:13 AM

ESO

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#4

Re: Device 87 Operation

02/20/2015 10:23 AM

The electrical difference(s) between phases is outside the existing relay protection parameters.

It is important that you identify which element is not in compliance.

Frequency? Phase angle? Voltage level?

I strongly suggest you have a protection system engineer analyze the circuit and relay settings before you attempt another breaker closure.

If you close the breaker and there is too much difference between the systems the breaker can fail causing severe damage and/or personal injury.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Associate

Join Date: Jan 2012
Location: Tema
Posts: 25
#10
In reply to #4

Re: Device 87 Operation

02/21/2015 6:06 PM

Thank you all.But my worry,why does the breaker closes any time after serviral attermt. device 87 operates on first and second,then closes

Register to Reply
Power-User

Join Date: Sep 2012
Location: Seattle, WA, USA
Posts: 147
Good Answers: 9
#5

Re: Device 87 Operation

02/20/2015 10:29 AM

Where can I get a deferential relay for my wife?

__________________
You have to actively participate in the manifestations of your own joys and good fortunes - they are not ready made for the taking, they are available for the making.
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #5

Re: Device 87 Operation

02/20/2015 10:33 AM

Would she use it?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Power-User
Hobbies - Musician - New Member

Join Date: Dec 2014
Posts: 418
Good Answers: 3
#7

Re: Device 87 Operation

02/20/2015 11:31 AM

Too bad, i work on device 88 & 86=]

Cheer, Stu.

__________________
"When I thought I exceeded to be wise but wisdom was far from me" -King Solomon
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8

Re: Device 87 Operation

02/20/2015 6:27 PM

The most likely cause will be installation, commissioning, and testing by someone who does not know how to do all of the above. Your 87 relay operates because the CTs are sensing an imbalance in the current entering and leaving their zone of protection. Usually this indicates a faulty component, but in your case I suspect that no one checked the polarity of the CTs and their wiring from the devices to the relay. Get someone knowledgeable out there before you actually cause an expensive failure.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#9

Re: Device 87 Operation

02/21/2015 11:29 AM

Transformer differential protection you are talking about, if my understanding is right.

The transformer differential protections are known to trip during transformer energisation if 2nd harmonic detection (with appropriate threshold and duration set) and protection block is not enabled.

There are other settings also that are important to make sure that the protection is stable during transformer energisation as well as during normal working that follows.

Review the settings critically with the recommendations given in the relay technical manual. That should help alleviate the problem.

By the way, repeated energisation of transformer when there is differential trip is not an acceptable operating practice in the industry. It could be serious with fatal consequences.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Kilowatt0 (1); Kulas (1); KWASI BIMPONG (1); Mike W (1); NotUrOrdinaryJoe (1); raghun (1); RAMConsult (1); redfred (2); SHOCKHISCAN (1)

Previous in Forum: Cat Generators   Next in Forum: KEWANEE Boiler Relay

Advertisement