I have an APC Symmetra 500kVA (480V) unit which recently failed outright in two successive incidents. The first time it was under about 180kW load. From the logs it appears that it first saw a ground fault on the third phase of the output. Screen shots indicate about 2500A. For some odd reason this fault was passed through to the 800A input breaker which tripped. The short duration was set to 300 msec. The fault was less than 5 ms at the output of the UPS, and of similar duration at the input. No independent monitoring outside of the UPS is present, so those values cannot be corroborated.
Within 5 seconds the UPS had errors on two of the modules, output waveform errors, and then tripped all (7) battery breakers...end of show.
The entire purpose of the UPS was pretty much moot at this point.
Has anyone seen an UPS pass faults through to the input like this?
Oddly enough, to me anyway, the APC tech deleted all of the files when he downloaded the logs. Is that common?
Before that conversation starts...yes, I am in active contact with the manufacturer with whom I have a service and warranty contract.
I want to get as many educated opinions on the matter as I can.
"Almost" Good Answers: