I have a Lincoln 230 VAC Welder that has an excessive no-loan current draw that I can't eliminate. I haven't used the welder for more than 20 years. The last time I tried to use it I had it hooked up to a small gas generator hoping to be able to make a low current (90 Amp) weld. The arc struck but the welder quit working. I have a need for the welder now and I tried to get it fixed. One of the diodes in the rectifier was blown and is not available from Lincoln but this can be handled OK. The real problem I discovered was an excessive no-load current. I started to disconnect different components trying to isolate the problem. The welder has three capacitors across the 230 VAC input lines labeled "Power Factor Condenser" that was drawing a large amount of current for some reason. I had the condensers checked and was told they are fine but I have my doubts. Any suggestions?
The Welder is a Lincoln Idealarc 250, 1 phase, 60 cycle, 230-460 volt. Model: 250-250, Code: 8039-C, Ser.#: AC-463529.
Condensers: "Mallory Bionol Capacitor", 25 MFD, 460VAC, M-13707-2.
Current draw with all three Condensers hooked up: 23.5 amps, All readings at 240 VAC
Current draw with only two Condensers hooked up: 15.1 amps
Current draw with only one condenser hooked up: 7.3 amps
Current draw with no condensers hooked up: 5.2 amps
There is a cooling fan that uses 1.2 amps @ 115 VAC
Good Answers: