A single tube 48" flourescent strip line is mounted on ceiling with a 5" valence.

Showered etc. in cool bathroom, turned off light. A few minutes later spouse turned the light on but no light. Turned on vent fan. About 5 minutes later the light came on with actuating the switch. This has happened quite a few times over the past year. Never before, however.

Could condensation on the fluorescent tube cause this? Or what else?

__________________
Do Nothing Simply When a Way Can be Found to Make it Complex and Wonderful
Register to Reply
Pathfinder Tags: Fluorescent Behavior
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Fluorescent Behavior

07/11/2007 12:11 PM

A suggestion: could the connections between the vent fan and the light be crossed over? Many fans have two live terminal connections: one runs the fan on the switch and the other sustains the fan after the run connection is de-energised, using a timer inside the fan. If the light feed and the fan feeds had become crossed over at some point then that would explain it, particularly if the timer had a changeover contact and the light feed was derived from it rather than having its own separate circuit (unlikely though perhaps possible in non-UK wiring). Did someone twiddle with it about a year ago and leave it like this?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Nov 2006
Location: KnoxTN
Posts: 1485
Good Answers: 6
#2
In reply to #1

Re: Fluorescent Behavior

07/11/2007 12:58 PM

"A suggestion: could the connections between the vent fan and the light be crossed over?"

No wiring changes since installing vent fan. Both fan and light are controlled via low voltage relays. A big thing when the house was build in '53. The fluorescent strip line was replaced completely due to a bad ballast. Easier & no more cost than ballast alone. Everything works as it should at all other times than shortly after a shower. tube is warm so no condensation there. ???

Very perplexing!

__________________
Do Nothing Simply When a Way Can be Found to Make it Complex and Wonderful
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Fluorescent Behavior

07/12/2007 3:50 AM

Does renewing the fluorescent starter unit make any difference? And is it correctly sized?

What happens when the fluorescent is changed for a filament lamp temporarily?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#8
In reply to #2

Re: Fluorescent Behavior

07/12/2007 11:23 AM

Stan

Make sure your low voltage relay is rated for an inductive load like this fluorescent light; many are rated for resistive loads like incandescent bulbs only

Register to Reply
Anonymous Poster
#4

Re: Fluorescent Behavior

07/12/2007 5:11 AM

A fluorescent fitting would not be allowed in a bathroom in the UK, unless classified for that location, but I doubt if condensation is the cause of problem.

In the absence of a physical wiring mix up, the most likely cause is a loose connection in the light fitting - either a wire, an end cap, starter, or overheating component.

Vibration from the fan might be enough to cause a faulty connection to make or break

Register to Reply
Associate

Join Date: Jun 2007
Location: Lexington, Kentucky, USA
Posts: 33
#5

Re: Fluorescent Behavior

07/12/2007 6:54 AM

Condensation is the correct answer. The moisture on the outside of the lamp makes a current path across the outside of the lamp and current does not flow inside the lamp so it does not light. When the condensation evaporates the lamp is able to light again. Fluorescent lamps are coated with silicon on the out side so that any condensation on the lamp beads up and helps to prevent this problem, but as you have found out it does not always work.

Mike Love

__________________
"A designer knows he has achieved perfection not when there is nothing left to add, but when there is nothing left to take away." Antoine de, Sant-Exupery
Register to Reply
Guru

Join Date: Nov 2006
Location: KnoxTN
Posts: 1485
Good Answers: 6
#6

Re: Fluorescent Behavior

07/12/2007 8:00 AM

Thanks for suggestions to check using a incandescent lamp and condensation.

I had thought of condensation but then the lamp was warm/hot from being on for some time. Only a short time after being turned off it would not come on.

Will try to remember to report findings.

__________________
Do Nothing Simply When a Way Can be Found to Make it Complex and Wonderful
Register to Reply
Power-User

Join Date: Aug 2006
Location: Central Florida in the good old US of A
Posts: 332
Good Answers: 2
#7

Re: Fluorescent Behavior

07/12/2007 8:01 AM

Mr Roboto has probably nailed it. Also, a dusty tube will present the same problem. Most of the time simply wiping the tube off will cause it to lite.

__________________
Eschew obfuscation.
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#9

Re: Fluorescent Behavior

07/12/2007 12:17 PM

Fluorescent lights require the presence of a grounded surface parallel to the tube, along its length. This gives a slight capacitive effect which helps the arc to initially strike. If the change of the fixture was fairly recent, it is possible that you also changed from a core & coil type of ballast to an electronic one. With this change, the heat loss within the ballast compartment and at the ends of the tube would be a lot less than it was previously.

I would not look for problems related to condensation along the tube itself, because it is sufficiently warmer than the surrounding surfaces. This leaves two possibilities -- condensation at the sockets on either end (cooler fixture than before) or elsewhere near the fixture, or a lack of a ground. The house was built in 1953, so I believe that the problem is a lack of a ground to the fixture. Often, this can be quickly checked by touching the metal fixture housing when it is refusing to light, or temporarily testing with a wire from the housing to a nearby ground (a water pipe in a house of that age would probably be sufficient unless plastic lines were installed in the last 15-20 years). The low-voltage relay systems used then, and still available today, (usually Touchplate--spst, or GE--spdt) are very unlikely to be at fault with this type of load.

Fixes--1) ground the fixture. 2) Use an enclosed fixture listed for damp or wet locations.

Another possibility -- double check the ballast and the tube because many new electronic ballasts are supposed to be used with F32T5 bulbs instead of the older F40T8 bulbs. These two tubes are the same length and have the same pin spacings but one is 5/8" diameter and the other 1" diameter. With the dry surroundings, a wrong tube could light, but fail to do so when the condensation is nearby.

Register to Reply
Anonymous Poster
#10
In reply to #9

Re: Fluorescent Behavior

07/12/2007 3:41 PM

A modest correction- T8 and T12 lamps have identical pin spacing, the T12 being the more mature.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#11
In reply to #10

Re: Fluorescent Behavior

07/13/2007 6:56 PM

Thanks, Guest. I should have said: F32T8 and F40T12. Feel welcome to become a member. --jmm

Register to Reply
Register to Reply 11 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); jmueller (2); Kyoto (1); MrRoboto (1); PWSlack (2); Stirling Stan (2)

Previous in Forum: UPS ONGUARD AND ACS BRAND (SAI OR NO BREAK)   Next in Forum: Heating nitinol rod using AC/DC power supply

Advertisement