May I use the APFC at DG?

03/26/2015 2:57 AM

We are using 750 kva DG for 200 TPH crusher during full load operation we are observed at DG display pf is 0.58 . now my question is.

1. may I use power factor correction panel like APFC in dg's out put?

2. if apfc (automatic power factor controller) can be connected with that, means is there any advancetage for fuel efficiency @ 80 % load?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: May i use the APFC at DG?

03/26/2015 5:48 AM

How close to full capacity is the power cable between the D and the TPH crusher? If there is capacity in hand on the cable, a PF unit buys nothing.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: May I use the APFC at DG?

03/26/2015 6:43 AM

Some of the heat dissipated in the cable might be reduced. An economic calculation would determine whether PF correction is worth the investment.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: May I use the APFC at DG?

03/26/2015 9:41 AM

Yes and yes....generally speaking, that you understand the reactive power conditions that can exist and your APFC is equipped to deal with reactive power limiting requirement and ensure that under actual operating conditions the kW loading and current loading is not exceeded, which could damage the generator windings....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: May I use the APFC at DG?

03/26/2015 1:15 PM

<...current loading is not exceeded...> That's what fuses and breakers are for!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: May I use the APFC at DG?

03/26/2015 2:37 PM

I would not bother with APFC however. I would just turn on PFC caps with the crusher motor. That's the only significant load that will affect the PF.

But to that point, it's a complete waste of time and effort to judge the PF on an unloaded crusher motor. Without it being loaded with rocks, the motor is just a spinning mass and the PF will be low. That is essentially meaningless though, because why do you care what the PF is when the machine is doing no work? You just shut it off! So start using your crusher and load it to its maximum capacity, THEN measure the PF. If it is still low, then determine the amount of kVARs you need to correct it UNDER LOAD, and have them turn on only when the crusher is running and is getting rock fed into it. The simplest method is to use an aux. contact of the crusher starter, in series with an aux. contact of the infeed conveyor, to control the coil of a suitable contactor that brings in the PFC capacitors. You don't need anything more complicated or expensive.

Please send me your PayPal account information, I'd like to send you my bill for consultancy.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#6
In reply to #5

Re: May I use the APFC at DG?

03/26/2015 9:28 PM

I may be missing something here, but why do you suggest the observed pf is at no load when the OP's statement indicates otherwise?
"We are using 750 kva DG for 200 TPH crusher during full load operation we are observed at DG display pf is 0.58"

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10
In reply to #6

Re: May I use the APFC at DG?

03/27/2015 9:51 AM

Because I am blind as a bat and missed that...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#7

Re: May I use the APFC at DG?

03/26/2015 9:55 PM

Altering the pf will have little effect on fuel consumption.

If your genset has an input fuel monitor, then you can see for yourself by adjusting the AVR control to shift VAR up and down and observe the change in fuel delivery. The exciter will obviously produce more or less power in response to excitation, but the changes in fuel usage will be minimal.

The greatest benefit in raising the pf closer to unity (0.8 pf is what most gensets are rated at) may be in reducing voltage drop on the connecting cabling and therefore improving the efficiency of the crusher. It might be argued that the crusher will then get more work done for a given amount of fuel, and so you have indirectly reduced consumption.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8

Re: May I use the APFC at DG?

03/27/2015 1:43 AM

PFC will save diesel.

Wait till the price of fuel goes up again to get a faster ROI.

I'm paying USD 0.70 for diesel now. Would take a long time to break even through savings with an APFC.

The fixed PFC at the motor idea is a good one.

You don't ever connect this load to the utility supply do you?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9
In reply to #8

Re: May I use the APFC at DG?

03/27/2015 2:04 AM

The fuel savings is due to lower I@R losses, ie lower current, less loss, less heat.... ergo less fuel for same work performed. Around 1% saving I saw quoted somewhere....not much but it depends what it is 1% of. The way fuel prices are going we'll be getting paid to use it soon (...a man's allowed to dream...)

Read this and look at the "further reading" too...all short, sweet and easy to read.

http://www.reliableplant.com/Read/13339/power-factor-correction

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#11

Re: May I use the APFC at DG?

03/28/2015 1:51 AM

There should be no resonance between generator reactance & capacitors.

__________________
pnaban
Register to Reply