Contact Resistance Test

03/26/2015 1:15 AM

Hi,

i need to ask how i can make contact resistance test for low voltage busbar, after installation and jointing are finish, without the need to check each joint separate because it will take too much time?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
5
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: contact resistance test

03/26/2015 1:23 AM

Apply full power and look for the smoke/flames/arc flash.

Register to Reply Good Answer (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2
In reply to #1

Re: contact resistance test

03/26/2015 2:08 AM

Just add a Cinemascope infrared imaging camera, and look for any hot spots when the full loads are applied.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#14
In reply to #1

Re: contact resistance test

03/26/2015 10:21 AM

Nice paper. It's a shame the OP will not or cannot take the time to study this paper. It answers precisely their question.

Maybe they reject this reality and want to substitute their own.

Maybe they did study the paper and still cannot understand it.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#18
In reply to #14

Re: contact resistance test

03/26/2015 2:10 PM

I know. You can lead a horse to water, but you can't change their spots.

Register to Reply
Participant

Join Date: Mar 2015
Posts: 3
#3

Re: contact resistance test

03/26/2015 2:57 AM

all your answers is not helping, we need to make this test before apply full power, and if we make this test for all line then we will include resistance for busbar it self plus the resistance for joints, but we need to check only the resistance for the joints only, and if we make this test for joints by joints it will take one year to finish, which not acceptable at all, so whats your opinion ??

Register to Reply
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #3

Re: contact resistance test

03/26/2015 3:56 AM

My opinion is that you should get a different job.

Register to Reply Good Answer (Score 2)
Participant

Join Date: Mar 2015
Posts: 3
#5
In reply to #4

Re: contact resistance test

03/26/2015 4:01 AM

Thank you

Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#23
In reply to #5

Re: contact resistance test

03/27/2015 10:16 AM

There are 2 aspects to the question your are asking, the physical aspects and the moral aspects. The physical are simple enough that much elaboration should not be necessary for a qualified individual.

The statement that they don't want to apply full power before this test is complete brings up the moral questions. If it CAN blow up when full power is applied and someone is saying they cannot properly test it, it seems that a huge amount of liability, moral and financial, will come in.

It also seems that A LOT of individual joint tests can be done in a year. If the project is that big they are not done and the project is completed and does not work because of a high joint resistance problem somewhere, if it does not blow up and make it obvious where the problem is, finding the problem may be very difficult and time consuming - expensive. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
2
Commentator

Join Date: Feb 2010
Location: West Yorkshire, UK
Posts: 96
Good Answers: 11
#6

Re: contact resistance test

03/26/2015 4:25 AM

Suggest you check each joint as they are completed i.e. make it part of the assembly process. Trying to measure a whole series of joints in one go will be less accurate, and if you do find a problem with one phase, which joint did you get wrong?

I assume you are talking about a "ductor" test or similar. Should only take a few minutes each joint, including recording the results.

__________________
rogerggbr
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: contact resistance test

03/26/2015 5:51 AM

Is there sufficient time to attend the funerals of the observers that will not have survived the experiment (rhetorical question - NNTR)?

Is there sufficient time to hire additional personnel to carry out the testing, thereby shortening he delivery time (rhetorical question - NNTR)?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: contact resistance test

03/26/2015 6:05 AM

Is the outcome of this experiment going on YouTube, please?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Oct 2013
Location: Texas.Baytown
Posts: 697
Good Answers: 26
#9

Re: Contact Resistance Test

03/26/2015 7:28 AM

VOM when the power is off.

__________________
If you want to know how well a broom works you do not ask the guy selling the broom or the guy who designed the broom, you ask the guy using the broom.
Register to Reply
Associate

Join Date: Mar 2015
Location: Iraq- hot Middle East
Posts: 30
#10

Re: Contact Resistance Test

03/26/2015 8:15 AM

Rami good afternoon any electric device or equipment do you want to test it in order to detect any probable defect .you should subject your doing to real test

this is electric don't say i don't want the job takes a long time. if you ignore such like this important step maybe cost you too much .

wish to you finish your job without problems.

Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#11

Re: Contact Resistance Test

03/26/2015 8:36 AM

With a magic ground bond tester that subtracts the resistance of each bus span from the total resistance accross all the joints.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#12

Re: Contact Resistance Test

03/26/2015 9:18 AM

Apply a reliable, stable DC current source capable of providing maximum rated voltage and current to each bus bar while taking voltage drop readings across each joint using a high resolution VOM to record the readings as they are taken.

After the voltage drop across each and every joint/connection has been recorded, compare the results to identify if and where there are any high resistance connections.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#13

Re: Contact Resistance Test

03/26/2015 9:26 AM

From your post it appears that the installation is being performed now.

  1. Your buss bar installation contractor should be testing the integrity of every joint after the connection is made and give you a report of every test!
  2. If the joint integrity test is not being performed, then someone went cheap and the final test will be a "power on" test.
  3. Let the person who specified "no testing required" flip the power switch for the first time!
  4. Stand back and video the results! Post on YOUTUBE and hope it goes viral!
__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#15

Re: Contact Resistance Test

03/26/2015 10:49 AM

Do a search on the term "Ductor test". Ductor was (is?) the brand name of an instrument made by Megger designed specifically for this purpose, essentially a micro-ohmmeter. The values to look for vary by the type of bus material and connection method, but a Ductor used to come with a book that listed typical values one could expect. When I used one in making MCCs with tin plated copper bus bars, we were always looking for 10 micro-ohms or less across each joint. But I can't tell you if that is appropriate for your situation, you will have to finish your own research on that.

I don't know of a test that would be of value for getting around testing each joint. I suppose if you determined the total number of joints in a series string and measured the total micro-ohmic resistance of the entire string, you could calculate what the total series resistance should be, including the natural resistance of the total length of bus bar material and if your value is higher, it indicates a problem. But that would not tell you which joint is the problem, or if it is more than one, etc. etc. That could actually lead to taking LONGER than just having the right instrument handy when assembling the bus joints, testing it the moment the joint is done, and move on. What are you adding, 30 seconds per joint? Why are you trying to shave off those seconds?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#16

Re: Contact Resistance Test

03/26/2015 10:55 AM

It might be possible to use a Time Domain Reflectometer as a "go-no go" test.

This type of meter if adaptable, would indicate the distance(s) from the point of applied signal to the high impedance connection point(s).

There is a myriad of this type of meter available from Fluke, Tektronic, Toshiba, Biddle, ?

A call to any technical support group of your preferred vendor would be a good place to start.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9911
Good Answers: 1141
#17

Re: Contact Resistance Test

03/26/2015 1:16 PM

The contact resistance between two joined bus bars can generate heat and power loss when there is large current. To measure a relatively low resistance, you need to use the 4 point method. Two probes supply a constant current through the contact and the other two are connected to a voltmeter to measure the voltage drop. This allows you to measure a low resistance without consideration of the probe contact and lead resistance.

http://en.wikipedia.org/wiki/Four-terminal_sensing

Register to Reply
Associate

Join Date: Mar 2015
Location: Iraq- hot Middle East
Posts: 30
#19
In reply to #17

Re: Contact Resistance Test

03/26/2015 5:32 PM

What test manner is this and how much current will pass through the bus bar and what

a battery could hold on for a time while you are busy to look for a drop voltage at points (2,3) or others on bus bar i am sure you will see the huge spark immediately if you close this circuit and the voltmeter will not read.any thing .

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9911
Good Answers: 1141
#26
In reply to #19

Re: Contact Resistance Test

03/30/2015 3:34 PM

The point is to run a measured current through the bus bar via terminals 1 and 4. Across each junction (2 and 3) measure the voltage. For example, if the current (1 and 4) is 10A, then if the voltage (2 and 3) is 0.5 volt, then the junction between 2 and 3 is 0.05 ohms.

If you instead measured across 2 and 3 with an ohmmeter, you would be measuring the junction resistance plus the resistance of the leads and the connections at 2 and 3. The added resistance is unknown and may well be larger than the junction resistance that you want to measure.

The "Four point method" avoids this problem because almost no current flows through the voltmeter.

Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#20

Re: Contact Resistance Test

03/26/2015 11:52 PM

I wonder what the drawings specify?

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#21

Re: Contact Resistance Test

03/27/2015 12:46 AM

Rami, if the the joints are performed in a local industry acceptable manner for the busbar size and there are no connection errors eg shorts, then passing current through the bars replete with joints and using thermal imaging will identify any loose connections. That is what you are looking for? You don't have to do this at Imax.

The resistance check doesn't test the design it tests the assembly.

If everything gets hot then the design is flawed or you have exceeded the design Imax.

Curiously....Cu or Al busbars?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
2
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#22

Re: Contact Resistance Test

03/27/2015 7:03 AM

The problem with applying a common test to all joints is that it does not locate the faulty joint. You then have to make further tests to home in on where the fault is located. The faulty joint then has to be remade but remaking any busbar joint will disturb the adjacent joints so they then have to be retested. You cannot determine before the initial test how many tests you will need or the length of time it will take. This is why joints are normally tested immediately after they are made, and any remedial work is carried out without disturbing adjacent joints. I am surprised that this was not part of the original contract specification for your installation. If you have further joints to complete, change the procedure to include testing as each joint is completed. If you already have many joints completed, preform an initial test on serial groups of 8 joints. If a fault exists within that group you can test groups of 4 then 2 then 1 to locate the fault. If there are many faults drop the first test to four joints and if there are very few increase it to 16 joints. You need to retest the 8 joints again after any joint has been remade. You may have disturbed other joints remaking the fault or there may have been two faults within the group. If there are no faults on the whole installation you only have to perform 12½% of the tests. A month rather than a year. (a week with 4 teams each taking ¼ of the installation) For each fault you need to do a further 4 tests, 3 to isolate the fault and 1 retest. After a few days you will be able to estimate the % of faulty joints and thus work out how long all the testing will take to complete.

Register to Reply Good Answer (Score 2)
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#24

Re: Contact Resistance Test

03/27/2015 10:19 AM

I suggest you measure the resistance of the complete bus with any instrument that provides the required accuracy and sensitivity. That measurement should be the benchmark for subsequent assemblies. Any assembly that shows a reduced resistance should become the new benchmark, and any assembly that shows increased resistance should be viewed as suspicious and tagged for detailed study.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2014
Posts: 204
Good Answers: 3
#25

Re: Contact Resistance Test

03/27/2015 11:03 AM

An LM317, a resistor, and a heat sink mount will provide you with a usable current source. ( I like 200mA )

Measure the voltage drop across each connection to find poor ones. You cannot isolate a bad contact without individually testing it.

Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#27
In reply to #25

Re: Contact Resistance Test

03/30/2015 4:17 PM

O.P. has not said anything about isolating or testing individual joints. If I understood his question correctly, he wants to verify the resistance of a bus assembly. This can be done by measuring individual joints, or by summing them. Also, most of the bus assemblies we test are powered by at least 100 amps. Highly unlikely that an accurate measurement could be made at 200 mA.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#28
In reply to #27

Re: Contact Resistance Test

03/31/2015 3:43 AM

The fact that he has not said anything about testing individual joints does not mean that he does not have to do it. If on testing the whole system he finds a fault, what do you propose that he does to solve the problem?

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#29
In reply to #28

Re: Contact Resistance Test

03/31/2015 9:27 AM

I propose the use of PETN detonation cord to remove the faulty metal. Then replace the missing conductor with a new conductor. This now makes two junctions where there were once one.

What lame, boring technique would you use? Would you follow the engineering documentation? How quaint.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#31
In reply to #29

Re: Contact Resistance Test

03/31/2015 7:09 PM

In an attempt to provide a constructive answer to the OP who clearly has a problem, either self inflicted or caused by a third party, I have already detailed my suggested lame, boring, technique in post 22. I designed busbar systems for many years so I was the person generating all than quaint engineering documentation. Yes, I would follow the documentation and not get myself into the mess that the OP now finds himself in. So I would not have posted the problem and had to suffer a barrage of snide remarks and sarcasm. I am on CR4 to try to help, obviously one of us is in the wrong place.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#32
In reply to #31

Re: Contact Resistance Test

03/31/2015 10:19 PM

There is such a pleasingly old fashioned feeling about following the engineering documentation that was agreed upon in the contract. It also feels great when the engineering document I labored over to make sure it was clear, concise and out of necessity boring as hell to write gets followed. Don't you agree.

This statement leads me to the critical unspoken questions for our OP.

Does the engineering documentation for this project stipulate testing of joints as they are assembled? If it does then why didn't QA catch this mistake early? If it does not then who pays for this engineering change after the fact?

I almost forgot. Your technique in #22 is a very good, after the fact, testing approach. I've given you a belated GA. When I've used a similar technique after the fact I've rarely finished this kind of testing. One of two scenarios quickly happen. Either a systemic flaw in the assembly technique quickly becomes apparent. This causes the whole assembly to be dismantled and then properly installed. Or the time keepers of the project insist the random check just performed with only passing results is sufficient. Turn it ON.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#30
In reply to #28

Re: Contact Resistance Test

03/31/2015 12:36 PM

Without knowledge of O.P's detailed requirements, it is difficult to come up with detailed recommendations. I would suggest that the bus assemblies be sorted into as many bins as required, and that the customer select from the low resistance bins. If higher resistance bins are encountered, they can be reworked or disposed of as warranted. The objective, as I understand it, is to speed the testing process and this is an accepted method.

Register to Reply
Register to Reply 32 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Brave Sir Robin (1); Circuit Breaker (1); classic (2); jhhassociates (3); JRaef (1); lyn (3); Original_Macgyver (1); PWSlack (2); Rami.Wishahi (2); redfred (3); Rixter (2); rogerggbr (1); SHOCKHISCAN (2); texasron (1); Tornado (1); Wal (1); welderman (3); Yahlasit (1); zzorb (1)