Effect Of Under Ground HV Transmission Cables On Earthing

03/30/2015 2:26 AM

what is the effect of underground HT/LT transmission cables on earthing, especially on public area surveillance systems. We are facing lot variation earth resistance values in New Delhi, India at various market places where cctv surveillance are installed. The earth pits near the HT cables showing high resistive values. Pl. Guide

Register to Reply
Pathfinder Tags: Earhing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Effect of under ground HV transmission cables on earthing

03/30/2015 2:43 AM

Provided all cables are installed in accordance with the relevant national electrical code, there will be no effect.

If earth pit resistances are too high then among the solutions is tipping a conductive liquid, such as seawater, into the pit.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
4
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#2

Re: Effect of under ground HV transmission cables on earthing

03/30/2015 5:06 AM

An underground HV transmission line will have a protective steel jacket that will be earthed.

To prevent unacceptable touch voltages due to inductance and capacitance from being present in the sheath, it is connected to earth at both ends.

This allows ground loop currents to circulate in the sheath and the earthing conductors of nearby electronic devices, this can manifest as interference with external electronic equipment such as video and audio particularly if the transmitter and the receiver are connected to different earthing points which will necessarily be the case with a remote monitoring system such as yours. It often appears as scrolling horizontal lines on the screen of a video receiver.

The fitting of isolation transformers on the coaxial cables of the video equipment generally solves the problem.

Register to Reply Good Answer (Score 4)
Member

Join Date: Mar 2015
Posts: 8
#4
In reply to #2

Re: Effect of under ground HV transmission cables on earthing

03/30/2015 5:15 AM

Thanks for the details

Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#7
In reply to #2

Re: Effect of under ground HV transmission cables on earthing

03/31/2015 8:40 AM

I am familiar on with US practices, and then only in the Southeast and Southwest areas. We were always careful to only ground the sheath at one point and monitor the current flow at that point. Many installation also monitored the voltage at the remote end of the cable also. If it is not done in this way, a circulating current can be produced that is basically a cable loss and can get high enough to trip relays due to leakage detection. The OP does not state what voltage he considers HV or HT levels. I think of 15000 volts as Medium Voltage (or MV) and when I think of HV I think of 69 KV and above, but usually above 138 KV. I would be concerned with connecting both ends of cable to ground, but I have no idea of the code or practice in Australia. I have thoughts that the HV or HT levels the OP is interested in are quite possible in the realm of low voltage (under 1100 volts) If that is the case, ignore my comments because I don't have much experience there, but I still think that grounding both ends of a sheath is a poor practice and can result in erroneous errors in relaying.

Register to Reply Score 1 for Good Answer
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#8
In reply to #7

Re: Effect of under ground HV transmission cables on earthing

03/31/2015 9:45 AM

Thank you, well stated and accurate. Especially the last sentence.

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#9
In reply to #7

Re: Effect of under ground HV transmission cables on earthing

03/31/2015 6:15 PM

I agree that grounding at only one end would be a better way to control ground loops, hence my comment re. the loops. That method is acceptable for short lengths of cable, but the practice allows quite high voltage differences to be present in the sheath on longer runs where the standing voltage between the sheath and earth at the unconnected end can be significant and will be a function of the length of the run, spacing of the cores and the current being carried. Ground fault conditions (even if only in the vicinity of the cable but not associated directly with it), and induction from trains, trams, lightning, etc can raise that figure significantly.

For this reason, single point bonded systems are generally limited to less than 500 metre length and employ an earth cable run parallel to and alongside the phase conductors to carry those fault currents and limit sheath voltage rise to acceptable limits. In these installations transposition of either the phase conductors or the parallel bond is employed to limit circulating currents, and a sheath voltage limiter must be fitted at the unbonded end.

Where circulating currents or cable heating are a concern then cross bonding techniques can be employed to reduce these.

Here is a link to one of our national authority discussions on the subject. Section 2 discusses screen earthing and 2.2.2 states their policy to bond both ends of cable sheaths. I would expect that they employ best practice which is likely the same in most developed countries.

Register to Reply
Participant

Join Date: Feb 2015
Posts: 1
#3

Re: Effect of under ground HV transmission cables on earthing

03/30/2015 5:08 AM

You can decrease the Resistance value by adding some new earthing pits in parellel.

As we know that 1/R = 1/R1 + 1/R2 + 1/R3 + ....., where R= Total Resistance value, R1= Resistance value of Pit no 1, R2= Resistance value of pit no 2 and .....

And also you may decrease the Resistance value of Existing pits by pouring salty water in to the pits.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#5

Re: Effect Of Under Ground HV Transmission Cables On Earthing

03/31/2015 12:30 AM

The different ground resistance measurements are nothing to do with HT cables proximity to your electrodes

The backfill around the cable is most likely sand and that's what your electrode is driven through. Try longer electrodes to get into the native soil below and you may start getting the same R readings as those in undisturbed soil situations where no cable is buried.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#6

Re: Effect Of Under Ground HV Transmission Cables On Earthing

03/31/2015 2:49 AM

here soil resistance is very high, so to get the required grounding we auger the ground rod ("spike") holes minimum 100mm diameter and backfill with low ohm cement

__________________
BSEE but always learning
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#10

Re: Effect Of Under Ground HV Transmission Cables On Earthing

04/07/2015 1:29 PM

If cables are directly underground laid the earth around the cable is drying due to the heat evacuated from.

This drying usually produces an earth thermal resistance rising but an electrical one could be expected also.

__________________
Julius
Register to Reply
Member

Join Date: Mar 2015
Posts: 8
#11
In reply to #10

Re: Effect Of Under Ground HV Transmission Cables On Earthing

04/08/2015 5:19 AM

First link is not available

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#12
In reply to #11

Re: Effect Of Under Ground HV Transmission Cables On Earthing

04/08/2015 7:18 AM

I see. However, if you will type the link in Google Chrome window it will open.

__________________
Julius
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (1); 4wsilver (1); 7anoter4 (2); D S R RAJU (2); JWthetech (1); PWSlack (1); spades (2); virendrambd (1); Wal (1)