3300xl Probe Gap Adjustment

04/03/2015 12:25 PM

Why we adjust the probe gap specifically at 50 mils?

and what is the advantages?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#1

Re: 3300xl probe gap adjustment

04/03/2015 12:53 PM
__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: 3300xl probe gap adjustment

04/03/2015 4:28 PM

Because, if you bothered to read the manual it would tell you to adjust it to 50.

Anonymous posters are a pain!

Reply
2
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3

Re: 3300xl probe gap adjustment

04/03/2015 5:45 PM

So that the sensor part of the probe is within the specified distance required to properly monitor the process and accurately provide feedback to the PLC, DCS, or other control equipment.

If it is not within the specified gap the sensing operation will not be accurate and the process system controls will not function correctly.

Depending on the application, the result could be catastrophic to humans and equipment.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply Good Answer (Score 2)
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: 3300xl Probe Gap Adjustment

04/04/2015 12:34 PM

Because 49 is too little and 51 is too much.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Good Answer (Score 2)
Reply to Forum Thread 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

lyn (1); Original_Macgyver (1); SHOCKHISCAN (1); Tornado (1)

Previous in Forum: Labview Movement Control of ATS-545 ThermoStream   Next in Forum: Minimum Differential Pressure Across Orifice Plate

Advertisement