36kva Genset Failure

04/07/2015 10:11 AM

I have 36kva FGWILSON GENSET, the generator is not able to take any load, as it shut down immediately once loaded.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#1

Re: 36kva Genset failure

04/07/2015 11:12 AM

Contact the MANUFACTURER!

https://www.fgwilson.com/generator_sets

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#2

Re: 36kva Genset Failure

04/07/2015 11:53 AM

My condolences. Try using a telephone on the manufacturer's number.

__________________
Good moaning!
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#3

Re: 36kva Genset Failure

04/07/2015 12:05 PM

Dear Mr.Sinan,

Your posting should express/spell out the events observed, but not so.

The reasons for stoppage/shut down of generator are plenty both in terms of Mechanical Aspect and in terms of Electrical Aspect.

A.On Mechanical Aspect

1. Diesel Filter Choked. preventing diesel flow to the pump.

2. Air Lock in the Diesel Injection, hence fuel supply to engine cylinders is not sufficient.

3. Inadequate Air supply for engine.

4. Incomplete combustion of fuel, high CO content in the exhaust gas.

5. Less compression of air inside the cylinder due to leakage past the piston rings.

6. Adulteration/water mixing in the diesel.

7. Poor Automisation of Diesel from the Diesel Injector/Automiser

8. Improper suction and exhaust valve opening/closing timings.

9. High volumetric clearance of the cylinder Head.

10. Leaky gasket.

11. Starting Torque demand is higher than what the generator can sustain.

B. On Electrical Aspect.

1. High starting current than what the Generator can handle.

2. The equipment to be started is on load i.e., the motor is started against the load and hence draws more current.

3. Partial Short Circuit is occuring.

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: 36kva Genset Failure

04/08/2015 2:45 AM

By "any load" you mean one that is less than the genset's rating? Overloading a genset will shut one down too.

You are either out of fuel or your filter/pump/governor/controller is wallaby-ted.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#5

Re: 36kva Genset Failure

04/08/2015 5:54 PM

It's probably broke. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

Circuit Breaker (1); Crabtree (1); dhayanandhan (1); Original_Macgyver (1); Wal (1)

Previous in Forum: The Size Of Sold State Relay   Next in Forum: Metal Halide Lights

Advertisement