Electric Panel Problem: Conductive Dust Deionization?

07/12/2007 3:56 AM

I have a problem with 550v electrical panels. They often blow up on top of the circuit breaker when there is excessive current flowing in the circuit due to a faulty load. What i have noted is that the dust around the plant is conductive and the air ionisation rate is high. How do I deionise the air in my panels chemically? The problem is that when we do maintenance our circuit breakers are always live on top.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Jul 2007
Location: Los Angeles
Posts: 23
#1

Re: Electric Panel Problem: Conductive Dust Deionization?

07/12/2007 11:39 PM

Two things come to mind

1) Buy dust proof or NEMA 4 panels. These are usually a completely welded consrtuction with Gasketed doors and covers.

2) the refineries some time have panels that have a positive pressure inside. This prevents any dust or explosive gases from getting inside the panels

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #1

Re: Electric Panel Problem: Conductive Dust Deionization?

07/13/2007 7:03 AM

2) the refineries some time have panels that have a positive pressure inside. This prevents any dust or explosive gases from getting inside the panels

Good point. This method is recognised as an acceptable form of explosion prevention provided the power to the panel is isolated from elsewhere while a purging and pressurising operation takes place using air obtained from outside the hazardous area. BS5345 recognises the method of protection as 'Ex p' and the European community has standardised it as 'EEx p' (Google for more). Lose the internal overpressure and the panel should de-energise until after the purge-pressurise sequence takes place, which makes working on the contents of the panel while live rather awkward.

The original post doesn't specify that the panels are in a hazardous area, though by the problems that are being experienced, the hazards would appear to be caused by something other than a potentially explosive atmosphere!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#2

Re: Electric Panel Problem: Conductive Dust Deionization?

07/13/2007 3:55 AM

dda gave two good solutions.

Get a good panel that is sealed so that the atmosphere outside will not get inside. The problem with some panel installers is that they defeat the NEMA 4 rating by punching holes for the cable entries and not sealing the holes properly.

Injecting air (compressed air) into the panel will also work since the positive pressure will prevent outside air from getting in.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Reply
Participant

Join Date: Jul 2007
Location: Southern Indiana
Posts: 1
#4

Re: Electric Panel Problem: Conductive Dust Deionization?

07/13/2007 7:39 AM

There are a number of issues to be delt with in this question.

#1. ALWAYS wear properly rated Arc Flash PPE when working on LIVE equipment!!!

NFPA 70e will help you choose the right equipment.

#2. Are the breakers all properly sized to the load? Sometimes with old breakers, the thermal unit in the breaker will no longer TRIP the breaker effectively turning the breaker into nothing but a switch and giving plant personnel a false sense of security.

#3. Has a study been done in the plant to classify your particular environment? The National Electric Code (NEC) section 500 discusses Hazardous Areas and requires equipment to be rated for the environment.

As you work through this problem, the short term solution would be as suggested earlier, to provide a positive air pressure with filtered air on the panel.

BE SAFE and WELL

Reply
Active Contributor

Join Date: Apr 2007
Location: North Carolina
Posts: 13
#5

Re: Electric Panel Problem: Conductive Dust Deionization?

07/13/2007 7:51 AM

In North America, we call that a Hazardous Location, probably Class 2, Division 1 in your case. As others have said, you need to make sure the dust does not settle on the circuit breakers. There are many ways to accomplish this.

__________________
Best Regards, G. Smith, NCE
Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2006
Location: Rochester, NY
Posts: 867
Good Answers: 11
#6
In reply to #5

Re: Electric Panel Problem: Conductive Dust Deionization?

07/13/2007 7:59 AM

Agreed on the necessity to put positive pressure into the breaker box or have a completely sealed unit at the least. That means special strain reliefs on the box perimeter as well.

The othe issue might be that the breakers have fatigued with age and use / abuse. You need to do a load analysis of each circuit (the motors will draw more as they age as well) and decide if the conduit can handle the extra load. If it can a bigger breaker might be one solution. If it can't new breakers might minimize the problem.

But the first thing is to get the dust out of the breaker box.

You might want to consider what the dust is doing to your lungs too.

My $0.02...

__________________
Eric
Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#7

Re: Electric Panel Problem: Conductive Dust Deionization?

07/13/2007 8:36 AM

MOVE THE PANEL!

If the dust is conductive why would you expose a worker to it to repair the panel. MOVE IT!

__________________
If you never do anything you never have problems.
Reply
Anonymous Poster
#8

Re: Electric Panel Problem: Conductive Dust Deionization?

07/13/2007 10:33 AM

On top of the dusty condition, you may have the problem with the available magnitude of short current in the plant and the rating of your panel and breakers.

1. Get the study the available short current value

eg. If this transformer taped from MCC which is supplied from 1MVA transformer typical transformer impedance is 5.5% and Z of cable is negligible then

ISC=(1,000,000/(1.73x600)) x 100/5.5 = 17,500Amp

if your equipment is rated for 14kA then it does not properly isolate the fault, it ignites.

2. If the equipment rating is okay get assessement on your hazardous area classification properly done, and specify your requirement based on this classification.

3. If your company ignoring this problem you can talk to your local safety authority to contact your employer.

Reply
Active Contributor

Join Date: Jul 2007
Location: Los Angeles
Posts: 23
#9

Re: Electric Panel Problem: Conductive Dust De ionization?

07/13/2007 11:24 AM

Can someone point him in the right direction how to properly classify the environment. In North America, possible your insurance company ( Factory Mutual, Hartford Boiler Etc) can help.

Until you understand the risk in this conductive dusty environment these panels are in, you should stay out. Could this dust possibly ignite the entire building?

I sounds like this forum went in a direction away from your original inquiry. To the best of my knowledge this industry does not address this situation by treating the air chemically.

There may be a recognized standard for a number of air exchanges per minute to get the conductive dust out of the room. If you know what this dust is, there may be a acceptable Parts per million level that you can address.

Get the panel out of this environment, and think twice about entering it yourself.


Thats my two cents worth. Hopefully someone else in this forum is an expert in this area and can help you out

Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#10

Re: Electric Panel Problem: Conductive Dust Deionization?

07/18/2007 6:24 AM

If the dust is metallic, it means that somewhere the processes in the rest of the area have a problem, either with generating the dust or in containing it. Somewhere, there is value leaking out of the plant! If the dust is conductive, then there is likely to be a metallic nature to it, and there will be a maximum occupational exposure limit for it, and which side of the limit the area is on is the principal concern. So, the first step is to get the dust under control, so that personnel can enter the area safely.

"C.A.T.N.I.P." - cheapest available technology not involving prosecution.

Rather than de-ionising the air, even if it were possible, find a way to contain the dust and thereby eliminate it from the switchroom.

__________________
Good moaning!