The Input Rating and also Three Phase Power Supply

04/13/2015 11:42 AM

Hi guys, I have few questions here regarding power supplies.
I have two models of power supplies and from the data sheet of the power supplies.
and I would like to enquiry on one of the model.
If i have to feed the load(Panel switchgear) fully 30/60V DC, 120Amp continuously for several hours.
Please explain what is the input rating needed for the model.
Can this power supply is able to fit with standard 3 phase 415V supply from Main switch board without the need of any voltage transformer.
Also, please recommend the fuse/mcb rating for the psu.
Attached along is the specification of the power supply.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - New Member

Join Date: Oct 2007
Location: Sour Lake, TX 30°08'59.68"N 94°19'42.81"W
Posts: 675
Good Answers: 13
#1

Re: The input rating and also three phase power supply

04/13/2015 1:08 PM

Well, son, here, in Texas,when you see a rattlesnake you leave it alone, you don't challenge it.

Your electrical problem is a big rattlesnake!

__________________
Bridge rule #1: Nobody is as good as he thinks about himself nor as dumb, as his partner thinks...
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: The input rating and also three phase power supply

04/13/2015 1:32 PM

Download the data sheet(linked) and contact the company support....

http://www.element14.com/community/docs/DOC-27080/l/669xa-series-data-sheet

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: The input rating and also three phase power supply

04/13/2015 2:08 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#4

Re: The input rating and also three phase power supply

04/13/2015 2:08 PM

I suggest you contact the manufacturer of the power supply you need and give them your specifications.

They should be able to sell you whatever you need!

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
2
Anonymous Poster #1
#5

Re: The Input Rating and also Three Phase Power Supply

04/13/2015 4:22 PM

Dears,

I have a loaded pistol. Not sure what kind it is.

How do I know which end the bullets come out?

Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: The Input Rating and also Three Phase Power Supply

04/13/2015 4:27 PM

Try it once or twice!

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster #2
#7
In reply to #5

Re: The Input Rating and also Three Phase Power Supply

04/13/2015 4:51 PM

Look into the long end and see if the bullets are in there?

Register to Reply
Anonymous Poster #1
#8
In reply to #7

Re: The Input Rating and also Three Phase Power Supply

04/13/2015 6:51 PM

It's dark in there.

If I pull the little curved thingy, I think they called it a chigger, will that let the light in?

Register to Reply
Anonymous Poster #2
#9
In reply to #8

Re: The Input Rating and also Three Phase Power Supply

04/14/2015 9:12 AM

Yes, it will let the light in..... However, it may also turn your lights out too!

Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#10

Re: The Input Rating and also Three Phase Power Supply

04/14/2015 10:40 AM

You have some good information in your post:

  • You're telling us what the load requires. (30/60V DC 120A)
  • You're telling us what the local power main is (415V 3P)
  • You're providing us with the tech sheets on the power supplies you're looking at.

Here is some information you may not have realized:

  • 30/60V DC at 120 Amps is 3.6Kw/7.4Kw of power than is more power than an untrained person should be playing with, by a few orders of magnitude.
  • You are not telling us which country the project is being done in. Local electrical codes vary, and what may be allowed in Sampledorf may not be allowed in Ollieandstan.
  • You are telling us 'between the lines' that this is a new construction, not a case of replacing a damaged/defective part. (If it were a matter of replacing what is broken, you simply make sure the new matches the rating of the old) You are also telling us that this project is not well planned out, since the designers would have determined the right component based on the load and the local rules and regulations on industry.
  • You are also telling us 'between the lines' that you may not have all the skills required to fully understand the project, as the fuse selection is rather simple. If the fuse is on the load side of the PSU it would need to be a 120 Amp fuse, id the fuse is on the supply side it would need to be, as a rough guess (60V x 120A = 7.4Kw || 7.4Kw / 415 V = 17.25A give or take) 18 Amps.

And all that adds up to one thing:

  • You are asking a semi-anonymous group of people for help on a serious safety issue that will have severe liability consequences should something go wrong.

I would strongly recommend that you consult with a local Electrical Engineer for assistance, he could look at the whole project and give better advice than we can from here.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply Good Answer (Score 2)
Participant

Join Date: Apr 2015
Posts: 2
#11
In reply to #10

Re: The Input Rating and also Three Phase Power Supply

04/15/2015 11:11 AM

Hi adreasler,

True indeed. alot of anonymous are here making annoying answers.

Anyway, Thank you so much for your reply. I do appreciate it.

Register to Reply Score 1 for Off Topic
Anonymous Poster #3
#12
In reply to #11

Re: The Input Rating and also Three Phase Power Supply

04/15/2015 12:14 PM

True indeed. alot of anonymous are here making annoying answers.

--

Hey! I resemble that remark!

Or is it resent?

Maybe it's both.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#13
In reply to #11

Re: The Input Rating and also Three Phase Power Supply

04/30/2015 1:54 PM

As far as the 'annoying' tone in the annon replies, you should realize that this forum sees several questions like this every week, sometimes several in one day, many with even less information than you supplied. Some people have limits on how many times they can say "I can tell from here that you are in way over your head, you need to get a skilled person over there before you injure/kill someone by making a blind guess." before they start to get, well, 'less than polite.' They don't mean it as an attack against you specifically (at least I hope they don't), they are simply 'raging at the heavens' at an extended situation that looks, to them, like 'babies playing with live hand grenades.'

Nobody is intending to humiliate or insult you, it's just that some of the members have gone too many 'bad situation' questions without sleep or booze, or videogames, whatever they use to 'drain away' their growing crankiness.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

adreasler (2); Anonymous Poster (5); cjong_lwc (1); indel (1); Original_Macgyver (1); SolarEagle (2); Tornado (1)

Previous in Forum: Challenge: Control of Latching Relay (Contactor)   Next in Forum: Lockout Relay and Diode

Advertisement