Control Valve, Cavitation
04/15/2015 2:37 AM
Dear All,
1)If Cavitation index
Sigma Value ( Process ) < Sigma Value ( Manufactuers Recomended Value )
Can We conclude that valve will not cavitate
2 ) Due to High DP, we expect Cavitation to Occur at minimum flow, multistage let down trim has been selected with Stellite overlay.
How can we judge that cavitation at minimum flow is ok ?
Regards
Jose
Re: Control Valve , Cavitation
04/15/2015 3:40 AM
The judgement can be made by discussing the situation with the valve manufacturer over the telephone AND it will be by far the quickest way too.
Re: Control Valve, Cavitation
04/15/2015 12:53 PM
This explains Sigma as it applies to cavitation. I hope that helps...
https://www.fwwebb.com/docs/processcontrols/ControlValveCavitation.pdf
04/16/2015 11:03 AM
Not really enough info ...
For Starters: (Assuming the medium is liquid)
1. What type of valve?
2. What's your calculated sigma value?
-What's the upstream pressure? How far upstream of the valve was it measured?
- What's the downstream pressure? How far downstream from the valve was it measured?
3. Any detail on the system (flow and pressure ranges)?
A multistage trim will reduce pressure drop at the vena contracta, which will then tolerate a lower cavitation index, but without knowing more details of your situation a conclusion can't really be made yet.