Query Regarding Double Bus System

04/22/2015 8:19 AM

Dear all,

In Specification of MV Switchgear panel having double bus bar system with single breaker the bus bar rated current is mentioned as 5000 Amps. My query is that there will be 2 sets busbars inside the switchgear Bus A & Bus B. Does it mean that each busbar is capable of carrying 5000 Amps (Bus A is capable of carrying 5000 Amps and Bus B is also capable of carrying 5000 A) or is it 5000/2=2500 Amps for each bus. (Bus A 2500 Amps and Bus B 2500 Amps). I have searched in internet but not able to get the answer.Please provide the answer if you know.

Please forgive me if the question sounds stupid. I thought it will be better to get this clarified rather than keeping this in mind..

Regards

John

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#1

Re: Query Regarding Double Bus System

04/22/2015 10:09 AM

You need to contact the OEM switchgear manufacturer technical support for clarification and answers.

The maximum amperage allowed on Bus A and Bus B collectively will be determined by the main breaker size which you have stated is a single unit feeding both busses.

Only the switchgear OEM can correctly answer your questions without being on site at the location.

The only other way for anyone else to reasonably answer your question would be to perform bus conductor physical measurements, identify conductor spacing, define thermal dynamics, and identify bus material composition to calculate each allowable bus ampacity.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply Good Answer (Score 2)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2
In reply to #1

Re: Query Regarding Double Bus System

04/22/2015 1:30 PM

Well said, have a GA point on me.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3

Re: Query Regarding Double Bus System

04/23/2015 12:33 AM

General understanding of Double Busbar system is there will be two sources of supply and each source will be connected to separate Busbar through circuit breaker. Outgoing to load will be tapped from both the buses through interlocked switches such that at any given time only one switch will be switched on and the respective load will get supply from any one of the buses. Busbar capacity depends on the loads connected to the bus or the capacity of the source. Supposing the double Busbar system gets supply from 1000 kVA transformer 415 V as source 1 and 500 kVA , 415 V DG set as source 2 then the Busbar 1 will be rated for 1600 amps and bus bar 2 will be rated for 800 Amps. Hope this clarifies.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#4

Re: Query Regarding Double Bus System

04/23/2015 12:53 AM

It is simple, the maximum current at any point in the bus bar must be limited to 5000 amps load. You might be able to load each bus separately, but if you have a bus tie, you must limit the current at any point on the bus bar to 5000 amps. If the two buses are totally separated without a tie breaker, then each would be limited to 5000 but you could not tie them together in any way. You really need to look at current flow.

Reply
Participant

Join Date: Apr 2015
Posts: 2
#5

Re: Query Regarding Double Bus System

04/24/2015 7:58 AM

hi,

Useally double bus bar system is used for redunt and also for load sharing ...

as you said each bus can be able of carring the full load of havinfg the 5000A ..

at the time of redunt or any service condition of the other bus

Reply
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

4wsilver (1); gkrishna06 (1); North of 60 (1); ramvinod (1); SHOCKHISCAN (1)

Previous in Forum: Current Transformer Types   Next in Forum: Motor Rotation Direction

Advertisement