Anonymous Poster #1

Starter Recommended for Min to Max KW

05/12/2015 11:53 AM

Dear Friends, Iam looking for IEC or NEC article reference for kWs required ranges Min to Max (KW) to use DOL , Star/Delta , Softsarter.Kindly please if any one have any article reference please support. thanks RG

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Starter Recommended for Min to Max kw

05/12/2015 2:25 PM

Here is some info...

"A direct on line starter can be used if the high inrush current of the motor does not cause excessive voltage drop in the supply circuit. The maximum size of a motor allowed on a direct on line starter may be limited by the supply utility for this reason. For example, a utility may require rural customers to use reduced-voltage starters for motors larger than 10 kW."

https://electricalnotes.wordpress.com/2012/03/13/direct-on-line-starter/

https://www.motorsystems.org/iec-standards

"Traditionally in many supply regions, there has been a requirement to fit a reduced voltage starter on all motors greater than 5HP (4KW). The Star/Delta (or Wye/Delta) starter is one of the lowest cost electromechanical reduced voltage starters that can be applied."

https://electricalnotes.wordpress.com/2012/03/16/star-delta-starter/

http://www2.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/171000/FA171495/en_US/ats22_user_manual_en_bbv51330_02.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Score 1 for Good Answer
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4
In reply to #1

Re: Starter Recommended for Min to Max kw

05/13/2015 7:20 AM

DOL if you have the grunt available to do it and conductors appropriately sized. Cheapest and easiest.

If I need star delta (a type of soft starter as you say) these days I don't. I use a VFD.

Only time start delta is used is if it is extant and needs fixing and is really required.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Starter Recommended for Min to Max kw

05/12/2015 3:55 PM

It depends upon the supply voltage and the resilience of the incoming supply.

British Standard 7671 gives full protocols.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #2
#3

Re: Starter Recommended for Min to Max kw

05/12/2015 5:51 PM

Surely you realise that Min is zero?

Reply Score 1 for Good Answer
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); PWSlack (1); SolarEagle (1); Wal (1)

Previous in Forum: Harmonic Filter Bank Capacitor Terminals Overvoltage   Next in Forum: 10" Display Screens + Sensors

Advertisement