05/12/2015 11:53 AM
Dear Friends, Iam looking for IEC or NEC article reference for kWs required ranges Min to Max (KW) to use DOL , Star/Delta , Softsarter.Kindly please if any one have any article reference please support. thanks RG
Re: Starter Recommended for Min to Max kw
05/12/2015 2:25 PM
Here is some info...
"A direct on line starter can be used if the high inrush current of the motor does not cause excessive voltage drop in the supply circuit. The maximum size of a motor allowed on a direct on line starter may be limited by the supply utility for this reason. For example, a utility may require rural customers to use reduced-voltage starters for motors larger than 10 kW."
https://electricalnotes.wordpress.com/2012/03/13/direct-on-line-starter/
https://www.motorsystems.org/iec-standards
"Traditionally in many supply regions, there has been a requirement to fit a reduced voltage starter on all motors greater than 5HP (4KW). The Star/Delta (or Wye/Delta) starter is one of the lowest cost electromechanical reduced voltage starters that can be applied."
https://electricalnotes.wordpress.com/2012/03/16/star-delta-starter/
http://www2.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/171000/FA171495/en_US/ats22_user_manual_en_bbv51330_02.pdf
Good Answers: 102
05/13/2015 7:20 AM
DOL if you have the grunt available to do it and conductors appropriately sized. Cheapest and easiest.
If I need star delta (a type of soft starter as you say) these days I don't. I use a VFD.
Only time start delta is used is if it is extant and needs fixing and is really required.
05/12/2015 3:55 PM
It depends upon the supply voltage and the resilience of the incoming supply.
British Standard 7671 gives full protocols.
Anonymous Poster #2
05/12/2015 5:51 PM
Surely you realise that Min is zero?