Generator Failure

05/31/2015 8:11 AM

A 0.55 kW borehole pump with a single phase motor having a run capacitor was powered by a diesel generator. The generator specifications are: 10 kVA; 415 V; 3 phase; 50 Hz; 0.8 PF. After about 4 months, the generator AVR and rectifier diodes blew-up. The generator had an unbalanced load i.e. two phases were switched off and only one phase was in operation. The phase in operation was between one live and the neutral at 240 v single phase. The AVR was replaced but it again blew. In my opinion, the likely cause of failure of the alternator is: (1) the unbalanced load; and (2) load with a leading PF due to the motor capacitor.

I will appreciate to get further information on the likely causes of failure; the mechanism of failure (e.g. zero sequel currents, etc); and the suggested solutions.

Kind regards and thank you.

Register to Reply
Pathfinder Tags: Alternator failure
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Engineering Fields - Control Engineering - Control Engineering Technical Fields - Education - Industrial Training Engineering Fields - Manufacturing Engineering - Manufacturing Training Engineering Fields - Electrical Engineering - Electrical engineering Training Engineering Fields - Instrumentation Engineering - Instrumentation Engineering United States - Member - New Member Engineering Fields - Energy Engineering - Become part of the larger group, change your world.

Join Date: Apr 2005
Location: Las Vegas, NV
Posts: 266
Good Answers: 1
#1

Re: Generator Failure

05/31/2015 12:57 PM

The moral being generators should have phase detection/protection. Many problems can be avoided following Author Larry Bush's generator advice and procedures http://www.feedforward.com.au/emergency_power_generator.htm

__________________
AB PLC Training onsite, On-Line, training software and more. BIN95.com
Register to Reply
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4
In reply to #1

Re: Generator Failure

05/31/2015 1:15 PM

What good would phase loss protection do here? OP deliberately operates a single phase motor across one phase to ground, with the other two phases unloaded. He would be better off using a single phase generator to feed a solitary single phase load.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 3)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Generator Failure

05/31/2015 12:58 PM

1. What did the trouble shooting already performed indicate?

2. What did the generator manufacturer's tech service say, when contacted?

3. What did the on-site visit by a service tech indicate?

4. What have you done, so far, to fix the problem?

Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Generator Failure

05/31/2015 1:08 PM

The unbalanced load is probably causing the problem, it's unlikely the run capacitor is causing the problem though it may contribute to it. The pump load (0.55kW) is small relative to the size of the generator, but what we don't know is how the AVR and its diodes are powered from the generator.

In a machine this small the excitation is often derived from a pair of diodes connected across two phases of the generator output and relies upon the residual magnetism in the rotor to build up voltage. If that happens to be the phase that you're starting your motor across, the voltage won't build up properly and the diodes have to pass more current in order push extra current into the field. Do this often enough and the overheating blows the diodes.

If you can provide more detail on the alternator and motor I'll see if this is the case, or if there's any resonant effect with the motor/capacitor combination. More details yield better answers.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#5
In reply to #3

Re: Generator Failure

06/01/2015 4:14 AM

The primary decision making criteria for selecting this oversized 3ph genset for this pump was most probably that it was the one they have on hand.

Maybe after fixing it they should consider some useful dummy loads on the other phases. Small airconditioners perhaps? Have to weigh up fuel costs V frequent repair cost.

It's hot here too. Worksite airconditioning has got to start being part of regular PPE in hot weather.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6
In reply to #5

Re: Generator Failure

06/01/2015 10:03 AM

I agree, but it illustrates the point that the old "the plug fits the socket so it must work ok" mentality often conforms to the Law of Unintended Consequences.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#7

Re: Generator Failure

06/01/2015 10:28 AM

I am less inclined to blame the small single phase load as I am to blame the general lack of load itself.

Very few smaller gensets are all that fussy about phase balancing but I am aware that long duration running at light loads can cause the rotor brushes to glaze over due to running at minimal current levels. I've seen this a number of times in portable welder generator units that spent a lot of time being used on work sites for auxiliary power sources where they would run for days never seeing a load bigger than a few cell phone chargers and cordless tool chargers.

This glazing can cause intermittent open circuit conditions in the rotor which will act like a hugh induction coil causing a high voltage spike to be produced which when high enough will break through the glaze and hit the voltage regulator with a pretty serious spike. Do that enough times and something will have to give which is usually the diodes or the switching devices in the regulator.

The other thought is that the rotor may have an intermittent short to the frame which causes a overloading of the voltage regulator. That too would cause the diodes to explode.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#15
In reply to #7

Re: Generator Failure

06/06/2015 5:00 AM

What brushes?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8

Re: Generator Failure

06/01/2015 5:17 PM

Why don't you check the single phase motor and make sure it or its capacitor isn't faulty.

__________________
jack of all trades
Register to Reply
Associate

Join Date: Mar 2012
Posts: 48
#9

Re: Generator Failure

06/02/2015 1:07 AM

Thank you very much indeed for some very useful responses.

Register to Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#10
In reply to #9

Re: Generator Failure

06/04/2015 6:37 AM

If you have a 3 phase to single phase transformer of the proper voltage rating, use that.

Register to Reply
Associate

Join Date: Mar 2012
Posts: 48
#11
In reply to #10

Re: Generator Failure

06/04/2015 8:40 AM

Thank you for your advise.

Do you have a specification for such a transformer? This will really help me.

Register to Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#12
In reply to #11

Re: Generator Failure

06/04/2015 8:56 AM

Yes. This is called a control transformer. Use a 415 volt 3 phase Primary / 240 volt singe phase secondary with a 10 amp rating. You can also purchase a transformer with a fuse clips mounted for primary and secondary protection.

Register to Reply
Associate

Join Date: Mar 2012
Posts: 48
#13
In reply to #12

Re: Generator Failure

06/04/2015 10:25 AM

Thank you for your time, it is highly appreciated.

I suppose the dedicated single phase generators use such a transformer.

Register to Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#14
In reply to #13

Re: Generator Failure

06/04/2015 10:52 AM

Only if there is a need. A 3 phase generator has a different need than a single phase generator has.

Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: