VT Class Clarification

06/02/2015 5:26 AM

Dear All
I hope you are well
now i want to ask you ,,

what is the meaning of this VT class 0.2 (3P) ??!!
what I know is that secondary is measuring or protecion
but in this class as you see it can be measuring or protection
Kindly revise
I do appreciate your reply
BR

Mohamed Gamal

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#1

Re: VT Class Clarification

06/02/2015 7:54 AM

So, the documentation for the VT is missing...

Ok, the 0.2 means the error class (0.2%) and the 3P reffers to a protection secondary, with a saturation factor of 3.

Anyone has anything to add?

__________________
The time is ......now
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#2

Re: VT Class Clarification

06/05/2015 3:32 AM

Unlike CTs, VTs can be rated for dual accuracy - measurement as well as protection. 0.2 class means when used for metering purpose, the error doesn't exceed 0.2% and 3P means when used for protection purposes, the error doesn't exceed 3%.

The difference here is we are interested in accuracy around rated secondary voltage in case of measurement circuits and that near zero volts when it comes to protection circuits.

In case of CTs, a 5P CT will have only 1% error in the operating load range and 5% at the ALF. Yet, the protection CTs are not widely used for metering (unlike the VTs) for the simple reason that the protection CTs cannot meet Instrument Security Factor (ISF or Fs) requirements of analog meters.

__________________
Raghunath