Previous in Forum: Inverter Communication   Next in Forum: Audio Power Amplifier Input Stage
Close
Close
Close
22 comments
Rating: Comments: Nested
Active Contributor

Join Date: Nov 2013
Posts: 11

Energy Meter Not Communicating

06/01/2015 6:25 PM

I have several energy meter connected to my server. A particular energy meter is not communicating sometimes. What could be the problem?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Energy meter is not communicating always.

06/01/2015 6:44 PM

You may have hurt her feelings.

What is her brand/model# and how does she communicate, when she does?

Register to Reply
Guru

Join Date: Apr 2007
Location: Buenos Aires, Argentina
Posts: 1679
Good Answers: 33
#2

Re: Energy meter is not communicating always.

06/01/2015 6:46 PM

Busy line?

__________________
the more I move, the deeper I get stuck !
Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#3

Re: Energy meter is not communicating always.

06/01/2015 7:33 PM

Flat battery, trying to communicate at same time as another, excessive distance for signal transmission, excessive system noise for receiver to recognise "incoming" message, intermittent connection (anywhere in system), ...........

__________________
Just an Engineer from the land down under.
Register to Reply
6
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4

Re: Energy Meter Not Communicating

06/01/2015 8:22 PM

Here are a few of my suggestions for your problem:

Bad wires, bad connector, bad software, bad meter, bad boy, bad power, too long of a cable run, improper VSWR, ESO, sun spots, RTFM, overheating, water infiltration, fungus, tin whiskers, bounced check, data storm, denial of service attack, unhappy bit spiders, you moved the coconuts.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 6)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8
In reply to #4

Re: Energy Meter Not Communicating

06/01/2015 11:00 PM

You forgot potentially faulty meter.

__________________
jack of all trades
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9
In reply to #8

Re: Energy Meter Not Communicating

06/02/2015 9:18 AM

Between bad software and bad boy.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#14
In reply to #9

Re: Energy Meter Not Communicating

06/02/2015 3:39 PM

I took that to mean faulty measurement or diagnostic device.

__________________
jack of all trades
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#12
In reply to #4

Re: Energy Meter Not Communicating

06/02/2015 10:54 AM

Pretty good list of possibilities! We could add Data Crash, Duplicate IP address, prankster, moody meter, cosmic rays (knocks bits from 1 to 0 in RAM), Nearby RF sources, sprung RJ45 spring type connector, strong wind on a loose mounting, oxidation of contacts, kinked cable, and the list goes on, and on, and on...

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru

Join Date: Apr 2007
Location: Buenos Aires, Argentina
Posts: 1679
Good Answers: 33
#5

Re: Energy Meter Not Communicating

06/01/2015 8:33 PM

Perhaps not much to say....

__________________
the more I move, the deeper I get stuck !
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#6

Re: Energy Meter Not Communicating

06/01/2015 8:45 PM

I have a particular answer for a particular energy meter.

Only who will tell that it is definitely the same particular type of meter?

Is it a type with CT's and receiver?

You'll need to dedicate a port and configure your router to allow communication.

Are you allowed to tell us e.g. make and model?

__________________
Plenty of room here
Register to Reply
3
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7

Re: Energy Meter Not Communicating

06/01/2015 10:06 PM

We're sending our top investigator...

He says it's probably Aliens....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 3)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#16
In reply to #7

Re: Energy Meter Not Communicating

06/02/2015 11:04 PM

Love it....

has anyone checked the server?

To the OP, have you paid your internet bill?

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#18
In reply to #7

Re: Energy Meter Not Communicating

06/03/2015 9:09 AM

No, no, no...

"He's not saying it's aliens. But, yeah, aliens."

Gotta get that verbal cadence right.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#20
In reply to #18

Re: Energy Meter Not Communicating

06/03/2015 9:20 AM

What? No. He doesn't look a bit like Elian Gonzalez. He looks more like Londo Mollari.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#10

Re: Energy Meter Not Communicating

06/02/2015 9:37 AM

The polling map/table for all instruments in the loop is not compatible with the loop interrogation communication speed? (Determine polling sequence & priority assignment, identify amount of time needed for interrogating each device, do the math and verify all devices can be polled within one network communication cycle.)

Too many collisions occurring in your network communications? (Bad fiber? Bad copper? Excessive conductor distance? Intermittent device issues? Wrong network topology for polling application? Too many devices in the network? Bad communications equipment?)

High db loss in the communications signal? (Poor connections? Bad equipment? Bad polling sequence? Low voltage supply to communications equipment and/or other devices in the system?)

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#11

Re: Energy Meter Not Communicating

06/02/2015 10:49 AM

Would this meter be using your fire damaged Profibus cable (that you don't know how to test) by any chance?

http://cr4.globalspec.com/thread/88014

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13

Re: Energy Meter Not Communicating

06/02/2015 2:43 PM
  • A loose wire.
  • A faulty meter.
  • A faulty input.
  • A mismatch between the meter and the input.
  • An unwillingness to follow the equipment instructions.
  • An error in the software.
  • An error in the scanning arrangements.
  • Temperature beyond limits.
  • The phases of the moon.
  • The tides.
  • A rodent's activities.
  • Etc., etc.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#15

Re: Energy Meter Not Communicating

06/02/2015 6:30 PM

As usual,

1. Has it ever worked correctly?

2. If so, what has changed which might be causing this?

3. Can you connect it by itself to see if it works then?

Register to Reply Good Answer (Score 2)
2
Guru

Join Date: Oct 2014
Location: Hemet, Land of milk and honey.
Posts: 2365
Good Answers: 36
#17

Re: Energy Meter Not Communicating

06/03/2015 7:29 AM

After 15 posts, in 24 hours, I highly doubt, gupta769 is going to respond.

OK, the guy made a few mistakes on his post, primarily not providing pertinent information.

Sometimes pulling a Patton works, sometimes it doesn't.

There should be a policy of some sort in place.

When a scenario such as this happens, and there is no response by the o p in say 24 hours, an automated message should be sent to o p , and the conversation removed from the cr4 daily digest listing.

Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#19
In reply to #17

Re: Energy Meter Not Communicating

06/03/2015 9:19 AM

Yeah, or posts should have some sort of 'editor review' before they are compiled to the daily digest. Even something as simple as: 12 hours before the digest is posted, the server sends an e-mail to 3-4 editors (to cover cases where someone may be sick or on vacation) with links to the potential items for the daily digest. If there are x slots for featured posts, then there would be 2xpotential submissions, listed in order of priority. so items 1 to x are scheduled to get posted, while items x+1 to 2x are the 'reserves' that will be moved up the chain if items above them get flagged for 'do not put in digest.' With that 12 hour lead time, the editors can make their decisions and flag the ones that shouldn't be on the digest well before posting time.

I believe there's a way for users to 'vote down' a thread to try and keep it from becoming a 'headline,' but it's pretty obvious that that system isn't working as well as it should, either from technical issues, lack or participation, or lack of knowledge in HOW to participate.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#21
In reply to #19

Re: Energy Meter Not Communicating

06/03/2015 9:28 AM

I think the 'keep from headlines' function is part of the 'thread rating' system, items below a certain rating aren't supposed to show up on the front page. However, it appears that items with a ZERO rating (as in 'nobody has rated it yet') are allowed through, on the grounds that it hasn't gotten any 'poor' (1-2 star) votes yet.

So, if everyone was participating in the thread rating, we'd be seeing 4-5 star threads features, with 3-star threads showing up on a slow day, and the 1-2 star threads would be sitting quietly in the background, and not attracting sarcasm like they do now.

Seriously, when poorly worded questions and people asking for detailed instructions how to do things they're clearly not qualified to do safely are the things making the 'Featured Articles' section of the Digest, it makes the whole site look bad.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#22

Re: Energy Meter Not Communicating

06/04/2015 1:49 AM

It is suffering depression?

Register to Reply
Register to Reply 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

adreasler (3); bigg (1); brich (1); dvmdsc (1); IQ (1); jack of all trades (2); Just an Engineer (1); Kilowatt0 (1); lyn (1); NotUrOrdinaryJoe (1); PWSlack (1); r&ddoc (2); redfred (3); SHOCKHISCAN (1); SolarEagle (1); tonyhemet (1)

Previous in Forum: Inverter Communication   Next in Forum: Audio Power Amplifier Input Stage