Problem with Level Measurement of a Vessel Under Vacuum Using DP Transmitters

06/01/2015 8:37 PM

Hello Everyone.

We have Rosemount dp transmitters installed for level measurement on a steam turbine condenser. Since it is a dp type measurment with wet leg installation and that too under vaccum, we are frequently having problem with the reading being deviated consequently reaching high level. The issue is fixed by filling the low side (and sometimes high pressure side, too) impluse lines but it won't last for long and we have to watch for the actual level (local glass guage) constantly, in order to ensure what the transmitters read is actual.

We have replaced the transmitters' manifolds and all that could be done to prevent leakages but the problem still persists.

Please have a look at the attached picture and suggest if there is something we can try to fix the issue with the same installation.

Thank you very much.

__________________
Screamingsilence
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Associate
Hobbies - Fishing - New member but have interest and some experience in fishing.

Join Date: Jul 2010
Posts: 44
#1

Re: Problem with level measurement of a vessel under vacuum using dp transmitters?

06/01/2015 9:03 PM

Also, I would appreciate if someone could teach me how to upload an image in full size, because my image is appearing much smaller than it is.

Thank you.

__________________
Screamingsilence
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#4
In reply to #1

Re: Problem with level measurement of a vessel under vacuum using dp transmitters?

06/05/2015 2:13 PM

You can copy/past the image into the message you are editing on CR4, then while still in the edit window for the message, you can click on the image, and some dashed lines and circles (showing object selection) should appear, and from that you can re-size to something more convenient. If using small text fonts for labels on drawings, you can also increase the size of the font relative to the image before pasting.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#2

Re: Problem with Level Measurement of a Vessel Under Vacuum Using DP Transmitters

06/01/2015 10:58 PM

What I see here is a very incomplete fundamental principle diagram:

Closed vessel with no inlet of steam (condensation) product.

No outlet or pressure relief for the water vapor/ steam.

A (liquid) filled line towards your (High position - low P?) input on the rosemount.

In the conceptual drawing, your DP cel will react more on pressure differentials, than the desired Low/ High levels, since the liquid column seems to be pretty much the same height.

__________________
Plenty of room here
Register to Reply
Associate
Hobbies - Fishing - New member but have interest and some experience in fishing.

Join Date: Jul 2010
Posts: 44
#3

Re: Problem with Level Measurement of a Vessel Under Vacuum Using DP Transmitters

06/02/2015 10:54 PM

Thank you for your reply.

The temperature of the water remains 30 - 40 Deg C and also the filled liquid stays inside the tubes, so the process temperature is not likely to affect it anyways.

Pressure 50 - 80 mbar (a), maintained by a set of ejectors on the top.

I realize there are leaks and because of the vacuum, the atmospheric air ingresses into the lines, pushing back the filled water into the condenser.

We are using the same water (condensate) that we have in the condenser.

A guided wave radar is going to fix the issue and we have already been recommended for that but the same installation has worked for a couple of years, it's just now that it has started giving problem.

Is there any way to find a leak (point of ingress) in vacuum system?

Thanks again.

__________________
Screamingsilence
Register to Reply
3
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#5
In reply to #3

Re: Problem with Level Measurement of a Vessel Under Vacuum Using DP Transmitters

06/05/2015 2:36 PM

screamingsilence:

(1) We use dP transmitters on hot wells on all our power generating units.

(2) the main requirement on the reference leg is that it remains full to the level of the return pipe on the hot-well (beneath the condenser tubes). This can be by maintaining the reference leg in a cold state (well below the hotwell temperature). The sensor itself will keep fluid from flowing out of the reference leg (unless it is a faulty sensor with a bad diaphragm or something like that). The flooded (reading) side is just what it sounds like: flooded constantly by liquid condensate from the hot-well that exerted a head pressure dependent upon the level of condensate in the hot-well.

To answer the leak detection question: Yes there are several ways to undergo leak detection:

(1) Make sure the turbine back-pressure is consistent with the observed turbine exhaust temperature - since you are taking vacuum pressure readings on the hot-well/condenser. If not perfectly consistent, then you need to figure out why.

(2) Make sure oxygen is not ingressing the system (and other non-condensible gases) through excessive requirements for make-up water (loss of condensate return, steam leaks, excessive boiler blow-down rate, etc.). This is evidenced by a high residual concentration of oxygen (above an arbitrary number of say 30 ppb oxygen in water solution) in hot-well condensate.

(3) If the source of non-condensibles is not make-up water rate, then you are most likely dealing with a direct air-ingress on the gland seals, at the turbine exhaust, through allowing air leakage into a sub-atmospheric pressure steam extraction (if one exists on your system), but these are seldom employed. Other sources of air ingress can be through leaking condensate pump seals, and even through high pressure boiler feed-pump seals (as a result of a Bernoulli effect at points where high fluid velocity exists). Leak detector systems can be brought on site by selected vendors to diagnose your systems ( I am not offering to provide advertisement for them here).

One old option that was used in power plants back 30-40 years ago (before we got all sophisticated and starting using Mass Spectrometers) was simple shaving cream applied to the area where the leak was "suspected" to exist. If that area is leaking, it will suck in the shaving cream. Now either helium leak detection or sulfur hexafluoride gas is used with a fancy detector, by spraying the test gas near the suspected leak, and waiting for the detector operator to declare a "hit".

This is one area that cannot and should not be ignored with respect to cycle chemistry, in that leaks or air will cost downtime, and already cost in lost power generated. Sufficient air binding can even exist in the larger condensers of big plants, that whole sections of condenser tube become "air-bound", and the exhaust steam from turbine cannot reach cold metal, hence it is as though the condenser were heavily fouled. One can also use effective U coefficient of the condenser as a long-term diagnostic to the quality of vacuum in a system in those cases.

I don't think you will have to apply a cooling coil over the reference tube of the dp transmitter, but if all else fails, that could be an option.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply Good Answer (Score 3)
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#6

Re: Problem with Level Measurement of a Vessel Under Vacuum Using DP Transmitters

06/19/2015 4:49 AM

You could try reversing the DP cell and changing the downstream impulse pipe so it enters the vessel well above top liquid level, with an inverted loop to minimise condensation. Also 3 valves to allow drainage of any condensation you do get without taking the vessel off line.

__________________
Give masochists a fair crack of the whip
Register to Reply
Register to Reply 6 comments