Interlocking Requirement Between Grounding Systems

06/29/2015 3:00 AM

In the below single line diagram, I need clarification for the interlock requirement between grounding of 2 transformers (red indicated).

The power can flow in both direction through the (13.8KV/34.5KV) transformer.

Example:

In case the power is feed through transformer XFR-1, so the disconnect switch DSW-1 is closed, is there any requirement to open disconnect switch DSW-2 at the zig zag transformer of XFR-2?

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Interlocking Requirement Between Grounding Systems

06/29/2015 10:08 AM

The purpose of the switches is to ensure that only one neutral is ever connected to ground/earth at any time, as has been stated in this forum earlier today and many times before. The reason is to eliminate the risk of currents circulating in the neutral conductor.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Oct 2014
Posts: 14
#7
In reply to #1

Re: Interlocking Requirement Between Grounding Systems

07/05/2015 5:15 AM

If we refer to the phasor diagram of delta-start transformer, and delta zig zag transformer, we will find out that the neutral point for star grounded transformer, and zig zag transformer are at same location.

So there should not be voltage difference between the 2 neutral points, and no circulating currents at the normal conditions.

What could be the reasons that will make a voltage difference between the 2 neutral points, and thus create a circulating current?

Thanks

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8
In reply to #7

Re: Interlocking Requirement Between Grounding Systems

07/05/2015 6:46 AM

Distance.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Interlocking Requirement Between Grounding Systems

06/30/2015 12:16 AM

As long as you can ensure that both sources cannot be simultaneously connected to the bus then there is no need for the interlock. However, since you stated that "...power can flow in both direction through the (13.8KV/34.5KV) transformer..." you have implied that both sources can indeed be connected at the same time.

If that mode of operation is allowed then the interlock is part of a larger scheme to ensure that both feeder breakers cannot be closed until a key (indicating an open ground/disconnect) is released from one of the grounding means. This is done to prevent reducing the effective grounding impedance in the doubly-fed configuration (essentially the parallel combination of the two grounding means) from becoming so low that the available short circuit current from both systems exceeds the interrupting capacity of the breakers, the mechanical withstand capacity of the bus, and/or the downstream system.

Of course the interlock system should also include logic to never allow operation if both grounding means are open.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Oct 2014
Posts: 14
#3

Re: Interlocking Requirement Between Grounding Systems

06/30/2015 6:44 AM

Regarding the circulating current:

If we refer to the phasor diagram of delta-start transformer, and delta zig zag transformer, we will find out that the neutral point for star grounded transformer, and zig zag transformer are at same location.

So there should not be voltage difference between the 2 neutral points, and no circulating currents at the normal conditions.

What could be the reasons that will make a voltage difference between the 2 neutral points, and thus create a circulating current?

Register to Reply
Participant

Join Date: Jun 2015
Posts: 1
#4

Re: Interlocking Requirement Between Grounding Systems

06/30/2015 12:54 PM

I need more clarification for this question.For what purpose you are using this Sig Sa transformer in Delta side of the TFRMR - 2 ?

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#5
In reply to #4

Re: Interlocking Requirement Between Grounding Systems

07/01/2015 12:33 AM

Provides a reference for ground fault clearance on the Δ feeder side if that transformer is connected to a supply.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Active Contributor

Join Date: Oct 2014
Posts: 14
#6

Re: Interlocking Requirement Between Grounding Systems

07/02/2015 1:23 AM

What could be the reasons that will make a voltage difference between the 2 neutral points (star neutral point, and the zig zag neutral point), and thus create a circulating current?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #6

Re: Interlocking Requirement Between Grounding Systems

08/15/2024 10:00 AM

See #8⇑.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 9 comments