In India, consultants specify a withstand of 50kA for one second without much thought, to err on the safe side. A 250A MCCB which you want to use as an incomer, is very very unlikely to have a 50kA breaking capacity. Being an MCCB, it will not have an Icw capacity, so there is no meaning in specifying 50kA for 1 second.
You should study the relevant IEC standards, the catalogues of the MCCB and so on. You should get an overview of the whole system before you go any further.
Good luck.
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
I do agree with Mr Sridhar.Many consultant without any application of mind , they simply indicate SC rating of 50 kA for the board and devices.
There will not be fault flow current to the extent of 50 kA in any normal circuit,
If 250 A MCCB happens to be incomer from transformer of 415 V , then transformer capacity should be less than 175 kVA.The %Z of this transformer will hardly be 4%.Then the prospective fault current will be 25 times the full load current which will be hardly be 7 kA.
Even if you assume this 250 A MCCB is incomer for sub Board, then there will be impedance of the cable which will restrict the flow of fault current and it will not be to the extent of 50 kA, unless this board is located in the Power Station.
Of late what is happening is many consultants simply say system fault level as 50 kA, and big Electrical Project executors ( L&T,Siemens,ABB,Schneider) and others request the switch board fabricators to design the boards for 50 kA irrespective of the location of the board in the Electrical system.