Further info on Electric Shock Drowning...

07/02/2015 11:11 AM

Some time ago we had a discussion around electric shock drowning that was prompted by the death of that young Russian woman in a bath tub where a cell phone charger was involved.

I recently came across material on this subject through an NFPA Journal artical on this issue. This may be interesting reading for those who want to understand this issue more completely.

Click Here

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#1

Re: Further info on Electric Shock Drowning...

07/02/2015 12:23 PM

I think American standards require power outlets in the bathroom, kitchen, and outdoors to be protected by a GFI device.

http://ecmweb.com/code-basics/nec-requirements-ground-fault-circuit-interrupters-gfci

Register to Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3
In reply to #1

Re: Further info on Electric Shock Drowning...

07/02/2015 12:57 PM

In Canada... (the US is the same I am pretty sure), all receptacles within 1.5m of a sink (bathrooms, kitchen counter plugs and laundry room plugs) must be protected by a Class A GFI device.

A bathroom or a washroom must have a receptacle located within 1m of a sink. That receptacle, where practicable, shall be at least 1m from a shower stall or bath tub, and in no case may be within 500mm of the shower stall or bathtub.

All exterior receptacles within 2.5m of finished grade must be protected by a Class A GFI device, unless marked as being exclusively meant for a car block heater.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Further info on Electric Shock Drowning...

07/02/2015 12:31 PM

Power outlets in the bathroom? Perish the thought! Under BS7671, the only socket allowable in a bathroom is an electric shaver socket, which must be isolated from earth and must not take a regular plug; shaver plugs are a different pin configuration from a regular UK power plug.

In shower rooms, the regulations are more relaxed, though there are minimum distance criteria between any socket and the various water fittings and a requirement for circuits to be fed via a 30mA RCCD [GFCI on the west side of the Atlantic].

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster #1
#4
In reply to #2

Re: Further info on Electric Shock Drowning...

07/02/2015 1:14 PM

This BS7671 was generated by a guy who had a female room mate and who (the room mate) was drying her hair in the nude! No outlet in the bathroom for the drier, she had to get out of the bathroom, bend, plug the hair drier, and go back to the bath room, keeping the door open (for the drier cord).

I am ashamed to publish it under my name....

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#7
In reply to #4

Re: Further info on Electric Shock Drowning...

07/02/2015 3:17 PM

I thought it was published by the British Standards Institution, then, I'm funny that way.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#10
In reply to #4

Re: Further info on Electric Shock Drowning...

07/02/2015 9:10 PM

Why are you ashamed? There is nothing wrong with the standard.

__________________
Common Sense Dictates
Register to Reply
Guru

Join Date: Dec 2007
Location: Haverhill, MA
Posts: 1149
Good Answers: 151
#5

Re: Further info on Electric Shock Drowning...

07/02/2015 2:04 PM

This article contains important information both for boat owners and owners of waterfront property. I wonder haw many privately owned docks, built before modern standards were in force, exist today, and how well any electrical installations have been maintained over the years.

__________________
The older I am, the better I used to be
Register to Reply
2
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#6
In reply to #5

Re: Further info on Electric Shock Drowning...

07/02/2015 2:08 PM

The rather sad part of it all is that a rather inexpensive device like a GFI breaker or receptacle can prevent these tragedies.

I am willing to bet there are hundreds of hazards like this out there that will only get discovered when someone pays for it with thir life.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11
In reply to #6

Re: Further info on Electric Shock Drowning...

07/03/2015 2:48 AM

GA

I am amazed how people and code requirements appear to only think that people get shocked in bathrooms and near sinks, a total fallacy, they get shocked EVERYWHERE!!!

That is why I have one on each of the 3 phases coming into my house. Its still not a requirement here.....

That should be done for ANY electrical installation.....but especially in private houses and private garages/workshops....

You would think that anyone/everyone here on CR4, with just a modicum of intelligence had it already installed!!! New house builds in the UK have had it as a requirement for many years, but do ALL houses in the UK have it today????

But I bet in reality less than 1 in 10 here on CR4 actually has put his money where his mouth is and installed such equipment!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Guru
Hobbies - Musician - New Member Hobbies - Car Customizing - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2007
Location: FL Space Coast
Posts: 536
Good Answers: 14
#14
In reply to #6

Re: Further info on Electric Shock Drowning...

07/03/2015 7:14 AM

I agree, almost totally, with your statement. I would hazard to guess though, that your estimation of hundreds of hazards like this out there, is probably orders of magnitude greater, in practice. ;-) I think of both sites, that pre-dated the standards, that have been grandfathered, as well as the bungling of weekend warriors, that have defeated these important safety devices. All of which I see, rather commonly, in my travels. Scary stuff.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8

Re: Further info on Electric Shock Drowning...

07/02/2015 3:28 PM

Nice piece of literature which thankfully avoided the discussion of how much current is lethal. Most of the private marinas that I've been in are pretty diligent about the condition of their dockside systems, but many of the publicly run ones can be pretty scary, covers/gaskets/blanking plugs missing, cracked/missing insulation, improperly terminated connectors, etc. I would never recommend going into the water between a boat and the dock in any facility.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#9

Re: Further info on Electric Shock Drowning...

07/02/2015 3:58 PM

The protection of people from shock hazards involving 240 and 480V three phase equipment, in particular, submersible equipment,is one of the most vague areas of electrical codes, the main problem being nuisance trips, with the word "nuisance" being open for discussion.

__________________
CRTL-Z
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#12
In reply to #9

Re: Further info on Electric Shock Drowning...

07/03/2015 3:02 AM

Nuisance "trips" were all in my (limited) experience, an indication of something (sometimes TWO somethings in parallel) that were simply far less than 1 Meg Ohm to ground.....

In fact they were usually heating elements, that were porous.....kettles and water heaters......also, due to being on time switches and thermostats, which sometimes made fault finding slightly more difficult....

I have always lived in hard water areas, which may have a bearing on the matter of course....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#13
In reply to #12

Re: Further info on Electric Shock Drowning...

07/03/2015 5:36 AM

AS 3000 makes the installation of ELCBs (GFI) mandatory for all circuits, EXCEPT, those prone to nuisance trips like HWS and fridges which have separate circuits. As mentioned above a nuisance trip is nothing more than a number of tolerable faults (normal operating phenomena) happening simultaneously.

My incoming mains goes through an ELCB and the branch GPO circuits all have their own that trip before the main does. I have NO circuits without GFI protection and have only had one or two nuisance trips in 20 years involving wet welders and ants chewing out insulation. You could argue whether or not these were nuisances.

As for GPOs in bathrooms AS 3000 and all others I'm sure, have exclusion areas specifically identified that stipulate distances from basins and so on in wet rooms.

You can't work on a building site (in Oz) with power tools unless they are protected by an ELCB and it is the contractors responsibility to have one.

Here's an Ozzy one..

Now, I don't live in Oz anymore but the habits stick, and I haven't killed anyone or burnt anything down, so I keep those habits,...my personal habits are another issue. Point being is that all new electrical switchboard enclosures (load centres) have 2 neutral links insulated from the enclosure in addition to the earth link. Not knowing which neutral to connect where by most folk keeps rice on the table.

Then there's the electrician ( who should know better, not me another very experienced highly trained senior dude, ELCBs are still new to some electricians even in the west, odd) ) takes the neutral from two different ELCBs and ends up with a lost neutral and 3 phases still hot with the voltages on the other circuit shot up to buggery (with accompanying smoke reeking of money) without that reference when a bloody light is turned on somewhere else....

ELCBs are great, some knowledge is required to make them work properly. Fortunately if they are mal-installed they normally remain in permanent nuisance state till remedied.

Crikey, I bunged on for a bit there. Sorry.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#15
In reply to #12

Re: Further info on Electric Shock Drowning...

07/03/2015 9:26 AM

There are two thresholds, one for people and one for equipment. Nuisance trips for equipment can indicate a deadly condition for people. To give an example, 60 kW submersible 480v pumps in a metal tank on a movie set, along with divers. Protection of the divers is possible and expensive, but not written into codes, other than not permitting divers and operation of the pumps simultaneously. It becomes a "special case" and an AHJD issue.

__________________
CRTL-Z
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#16
In reply to #15

Re: Further info on Electric Shock Drowning...

07/03/2015 9:50 AM

The Canadian code, by the way, does address the situation you describe.

Any submersible pump in a body of water, I would consider the tank you mention to be a "body of water", must be protected by a GFI device rated to trip at no more than 10ma of leakage current and have a response time of no longer than 2.7 seconds.

As well, any pump in a body of water that is energized by a source with a voltage higher than 150 volts to ground, may only be done by special permission and must be maintained by trained electrical workers. This ensure that the AHJ is aware of such an installation and as such, can ensure it is done properly and is safe to be used.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#17
In reply to #16

Re: Further info on Electric Shock Drowning...

07/03/2015 11:30 AM

Those thresholds for current and time are above the limits for personnel protection according to the NEC. The Canadian code accepts portable submersible pumps as equipment for use in (801) hazardous locations, but with the stipulations you mention. CSA requires HiPot testing for every unit sold into Canada.

__________________
CRTL-Z
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#18
In reply to #12

Re: Further info on Electric Shock Drowning...

07/05/2015 6:26 PM

I'm almost too ashamed to admit living with a nuisance trip issue for too many years in my house. I have two exterior 120VAC outlets that tripped the panel mounted GFI circuit breaker. After several years I finally took the time to open up the outlets and found the box filled with cobwebs. With the outlet box open I finally got smart and replaced the outlets with new receptacles. Problem solved!

Out of curiosity, I took apart one of the outlets and discovered that it was also filled with cobwebs. No wonder the GFI breaker kept tripping. It was trying to tell me something. I'm sorry it took me so many years and wasted trips to the basement panelboard resetting the breaker to figure it out.

I guess it serves me right for being a dumb mechanical engineer!

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#19
In reply to #18

Re: Further info on Electric Shock Drowning...

07/06/2015 1:40 AM

GFIs are good that way. They even trip if the neutral is decked.

Cobwebs? How are the spiders entering? Ants are my big headache here. PVC must taste good, rats love it too.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#24
In reply to #19

Re: Further info on Electric Shock Drowning...

07/16/2015 8:57 AM

I guess that baby spiders move in, then move out when the housing gets too cramped?

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#20
In reply to #18

Re: Further info on Electric Shock Drowning...

07/06/2015 9:03 AM

Lovely story, thanks for sharing.

But you are not dumb, I have met people that would bad mouth such breakers (met some in the UK years ago!),and put dozens of people off them completely.

Also, they would just replace it with one just current orientated, and then would proudly say "Problem solved"!

NOW THAT IS TRULY DUMB, you were just a bit lazy like most of us here....sorry!!

We have an old saying here which I will translate:-

"Those who do not have a brain, need to use their feet far more often!"

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#23
In reply to #20

Re: Further info on Electric Shock Drowning...

07/16/2015 8:52 AM

Ah, but I did use my feet a lot resetting a breaker, when the receptacle was to blame. I finally learned how to save a bunch of steps!

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Guru
Hobbies - Musician - New Member Hobbies - Car Customizing - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2007
Location: FL Space Coast
Posts: 536
Good Answers: 14
#22
In reply to #18

Re: Further info on Electric Shock Drowning...

07/07/2015 6:44 AM

"I guess it serves me right for being a dumb mechanical engineer!"

That's ok. We electrical engineers forgive you for your transgression. lol

Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#21

Re: Further info on Electric Shock Drowning...

07/06/2015 9:55 AM

NEMA gives horsepower ratings to outlets and plugs with the intention of limiting inductive loads, where the plug is the sole means of disconnection/connection, yet the GFI outlets are not HP rated for when the tripping action opens a motor loaded circuit. It is good practice to test these outlets routinely, especially in marine environments.

__________________
CRTL-Z
Register to Reply
Register to Reply 24 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (3); Anonymous Poster (1); Crabtree (1); gringogreg (1); IanR (2); IdeaSmith (1); North of 60 (3); PWSlack (1); RAMConsult (1); Ried (3); Rixter (1); Unredundant (4); Wal (2)

Previous in Forum: DC Motor   Next in Forum: A Weird Dilemma

Advertisement