Transformer Inrush Current Rised to Voltage Dip

07/22/2015 2:57 PM

Sir,

we are having a transformer rated 15/20MVA with 33Kv/6.6Kv voltage rating. During charging of transformer it got tripped in differential. ( settings are 0.14I ). After that i have changed the setting to 1.5I and charged. transformer got charged but given rise to voltage dip at 11KV with 10.2KV ( at generation side ). what might be gone wrong for this situation. can any one help to understand.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: transformer inrush current rised to voltage dip

07/22/2015 3:00 PM

Yes - the transformer manufacturer can. Please advise the outcome of the telephone call that was made to them when this problem first occurred. What were the recommendations that dropped out of that discussion, please?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: transformer inrush current rised to voltage dip

07/22/2015 3:16 PM

This is not something that can be resolved by a student, or intern.

You'll need an electrical engineer who understands transformers and how they work.

Have that person contact the manufacturer of the unit and discuss the problems.

ONLY a qualified engineer can resolve this issue.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3

Re: transformer inrush current rised to voltage dip

07/22/2015 3:22 PM

Things to consider and investigate:

Applied Primary Voltage is greater than 33KV.

Surge arrestors and/or filter capacitors are not properly sized.

Transformer windings turn-to-turn ratio not correct. (Caused by faulty transformer winding or bad assembly process.)

Shorted transformer winding caused by electrical fault or high impact.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#4

Re: Transformer Inrush Current Rised to Voltage Dip

07/22/2015 5:12 PM

Primary and secondary are reversed.

__________________
CRTL-Z
Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5

Re: Transformer Inrush Current Rised to Voltage Dip

07/22/2015 7:02 PM

Nothing has gone wrong, "we" need to increase our understanding of what transformer inrush current is, and how it will affect improperly set protective relaying.

"We" also need to hire someone experienced in commissioning a transformer or you will have a very short career as a consultant.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#6

Re: Transformer Inrush Current Rised to Voltage Dip

07/23/2015 11:03 AM

Who determined what your protective relay settings (including the differential relay) should be to begin with? You should talk to that person first. And what justification do you have for changing the differential relay setting the way you did (except that it prevented the relay from tripping)? Arbitrarily changing relay settings can have catastrophic results when the relay is supposed to pick up for a fault but doesn't because someone incorrectly set it! You will be working for a long time to pay for a transformer of that size if it fails because of your ignorance and capriciousness.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#7

Re: Transformer Inrush Current Rised to Voltage Dip

07/23/2015 5:10 PM

Are the CTs correctly connected? Wrong polarity or even phase cross-over/wrong ratio?

Did anyone do CT polarity & connection checks?

You write "rated 15/20MVA with 33Kv/6.6Kv voltage rating". Where is the 11 kV? - at a too-small generator with step-up to 33kV?

67model

Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2010
Posts: 28
#8

Re: Transformer Inrush Current Rised to Voltage Dip

07/24/2015 9:18 AM

Sir

yes we are having GTG of 29MW ( at present it is loaded at actove power4.26MW and reactive power 2.2MVAR ) it is at 11KV . This 11KV has been stepped up to 33KV and distributed further. IN this distribution one of the transformer 15/20 MVA has been charged.

One of might observation is as GTG is less loaded and possessing very less rective power, as and when a transformer of 15/20MVA charged its reactive power is getting shooted to 6 or 7 MVAR. Is this might be any cause for voltage dip. please explain me in this regards also.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#9
In reply to #8

Re: Transformer Inrush Current Rised to Voltage Dip

07/24/2015 4:33 PM

Why do you find this unusual, after all a transformer is a big inductor, and inductors draw reactive VARs during charging.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#10
In reply to #8

Re: Transformer Inrush Current Rised to Voltage Dip

07/25/2015 4:20 AM

20MVA transformer inrush is big for a 29MW machine.

Typically, the AVR of 29MW GTG is selected to be in 'PF' control mode.

If you can change the selection to 'Voltage' control mode, it improves the speed of AVR response and thus reduce the Voltage dip/duration.

Further, please ensure/confirm that the field forcing circuit (through compounding CTs or otherwise) is commissioned and in service. This boosts the field current instantaneously (as soon as it senses the inrush current in generator power cables) and plays important role in minimising such voltage dips during large motor starts or transformer energisation.

__________________
Raghunath
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#11
In reply to #8

Re: Transformer Inrush Current Rised to Voltage Dip

07/27/2015 5:59 PM

Dear Venu,

Thank you for the additional information. I think the system is like the sketch drawing below :-

I have put in typical impedances for the generator and transformer. Note that X'' for the generator [and the 2% volt drop] applies only for the first cycles of a load application. The settled value after a few seconds will depend on the generator "synchronous reactance", usually Xs on its data sheet, if the excitation is a fixed field current and typically would be a voltage fall of about 20% of 11kV for load MVA of 6 to 7.

It seems your voltage regulator is having some effect, although much better is usual.

Further information would help about the following :-

  1. How do you know the voltage dip is 0.8 kV? If you are looking at an ordinary moving iron "pointer" meter it may overshoot and swing about before settling to a steady value - this gives a dip exceeding the true value.
  2. What is the settled "steady state" voltage & current value at 33 kV after the 15/20 MVA transformer charging [I assume 11.0 kV before transfo charging and you have ammeter & voltmeter in the HV feed to the 15/20 MVA transfo]?
  3. What was the current at 11 kV with no load at 33 kV [that is the steady magnetizing current of the 11/33 kV transfo]??
  4. How long before charging current and generator voltage become steady after closing breaker C.B. ?
  5. What is the final current into the 15/20 MVA transfo? I assume there was no secondary load on this transfo during your test.
  6. What happens to the 33 kV voltage when C.B. is closed?

I note that in a system like this it would often be the 33 kV voltage which is fed back to the generator automatic voltage regulator.

Finally, I write again my opinion that the tripping of the differential relay is due to a wrong wiring somewhere. Your present setting of 1.5 In gives little protection.

It would help if you give the manufacturer and type of the differential relay.

67model

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard