Voltage Regulation Problem

07/23/2015 9:47 AM

Hi, all of you

I am inviting you to give your valuable solution and advice on my problem is :-

Before going to my problem I would like to introduce the subsystem and loads -I have 500kva/400volts transformer and 250kva/400volts power generator

the peak load of my important work is 170kva

the problem is :-voltage regulation,the power available here is some time vary 280volts to 420volts in three phase due to unbalance load. I want to install an automatice voltage regulator or stabilizer or new onload tap changer.so I need your advice or solutions

thanking you.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Voltage Regulation Problem

07/23/2015 1:07 PM

Try balancing the single phase loads better across the phases, first.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Voltage Regulation Problem

07/23/2015 1:19 PM

What's missing is if you are also connected to an external source of power or the 250kVA generator is the only source of power. What follows is based on a stand-alone generator.

Some generators have excellent AVRs (Automatic Voltage Regulator), some don't. The less sophisticated ones usually sense the generator voltage using only two wires. Two wire sensing might cause your problem because if you have an unbalanced load on the phases other than the one where the sensing wires are attached, then the AVR will not respond as the other phase voltages change due to the varying loads.

A simple solution would be to move the single phase loads around until you get them on the phase where the sensing leads are.

When you provide more information other solutions may be available.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 3)
Associate

Join Date: Jan 2007
Location: Melbourne, Australia
Posts: 51
Good Answers: 5
#3
In reply to #2

Re: Voltage Regulation Problem

07/23/2015 10:37 PM

I agree with the comments about good load balancing and the need for 3 phase voltage regulation. You have not mentioned whether the problem is worse when parts of the load are switched in or out.

We have found that in general for an internal combustion engine powered generator (diesel, petrol or gas) the capacity of the generator must be at least twice the load for a fully balanced load to give a stable supply.

If the load is unbalanced a higher ratio is preferred.

The larger engine / generator capacity will also have greater inertia and give better frequency control.

I believe that 250 kVA for a 170 kVA load is too small.

If significant portions of the load are switched independently the inrush current of attached equipment must also be allowed for.

__________________
fsmit@dyne.com.au
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #3

Re: Voltage Regulation Problem

07/24/2015 1:34 AM

can you publish the study showing why you need such a large engine and alternator.

__________________
pnaban
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9
In reply to #3

Re: Voltage Regulation Problem

07/24/2015 6:04 AM

Have to agree with Pnaban's call mate.

100% overhead is ridiculously oversized, even with starting currents considered.

What you say may be true for small machines under 10kVA but not a generator with enough mechanical inertia for the start surges.

Running a DG at only 50% load long term leads to other issues for the primemover, alternator doesn't care.

"We" have found that a genset loading of around 80% steady state is fine. eg 800kVA load has a 1000kVA DG pushing it. OP's 70% loading is OK too.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#4

Re: Voltage Regulation Problem

07/23/2015 10:43 PM

Dear Mr. manvendra,

Have you measured the current in each phase, and it should be near to equal in each phase and if not try to shift the load to the other phase and narrow down the difference.

Pl. check the AVR whether it is functioning properly, it appears - response time for the AVR is much slow. If so this response time should be improved.

What is the Power Factor, if it is less than 0.8, try to improve to 0.9 or so.

Stabilizer will be expensive for your Load. Replacing AVR will be economical option.

Pl. inform this Forum, how the prolem was sorted out.

DHAYANANDHAN.S

Register to Reply
Associate

Join Date: Aug 2010
Location: bhubaneswar
Posts: 34
Good Answers: 1
#8
In reply to #4

Re: Voltage Regulation and balancing Problem during unbalance load

07/24/2015 1:42 AM

good morning sir, thanking for your comments

sir normally as my observation it is happening in night time normally and I think it it due to unbalance load but the use of load is not in my hand so as normal I have balance the load but use of load I can not decide sir because it has other user also so if stabilizer is the solution so I will think about after economical analysis. avr is ok sir, I think avr is not responsible for balance the voltge, it is for excitation of generator for voltage regulation

sorry sir it may be the topic of title is not convening my problem.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#5

Re: Voltage Regulation Problem

07/23/2015 11:26 PM

What I understand from the information you gave is that your power supply from Electricity Board is varying from 250 V, 3 phase to 420 volts depending on load conditions and voltage in all the three phases are almost balanced. It is presumed that your local generator is regulated correctly at 420 Volts. The other information we will need to know is are you using the local generator only as a stand by power supply to take over when the Electricity board's supply is not available. Please confirm these points so that proper advice can be given.

Register to Reply
Associate

Join Date: Aug 2010
Location: bhubaneswar
Posts: 34
Good Answers: 1
#6
In reply to #5

Re: Voltage Regulation Problem

07/24/2015 1:32 AM

sir,I am using generator when state board power is not available

and one things sir generator has also different other load which is balance but all load are not used at a time in each phase so some time it is also vary from 300 to 400 volts while we need 5%max regulation.

thanking you

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#14
In reply to #6

Re: Voltage Regulation Problem

08/03/2015 5:33 PM

Sorry to "drop a stone in the pond", but if you have 250 kVA generator and 170 kVA load which is unbalanced a supplementary voltage regulator on a phase which is at 280V when it should be 400V will not help. You will just increase the current on the overloaded phase and bring its volts down even lower and risk tripping the current overload device or damaging the winding.

You have not given any examples of voltage and current on each phase in your undervoltage events - so we cannot judge if there really is a potentially damaging current overload.

You may have to try telling those users who are overloading at night that you may have to cut them off to prevent generator damage - which would leave them without power for ??? till the generator is repaired. They should only use essential loads. You are replacing an inadequate mains supply with your generator - the users cannot expect miracles.

67model

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#10

Re: Voltage Regulation Problem

07/24/2015 6:05 AM

Where are you measuring these voltages? At source or at the load?

Is the neutral grounded/earthed/decked?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#11

Re: Voltage Regulation Problem

07/24/2015 9:37 PM

You have already been told what the nature of the problem is, please stop wasting our time ignoring it and purchase an adequately sized UPS system, it is the quickest and most reliable solution to your problems short of finding an old antiquated ferroresonant voltage stabilizer.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#12

Re: Voltage Regulation Problem

07/24/2015 9:54 PM

I would find a voltage regulator large enough to keep your power supply clean enough to keep what you service constant (ahead of the generator). The load your generator is suppling will take care of the load.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#13

Re: Voltage Regulation Problem

07/27/2015 1:14 AM

In my opinion, your problem is if your stand-by generator will be your single source- if no supply from the transformer is available.

In this case if you'll try to start a big induction motor-mainly D.O.L. it will be a problem: the dip of 120 [400-280] V it could happened if you try to start D.O.L. an induction motor of-let's say- 75 kW if the only source is this generator.

Starting the same motor on transformer the voltage will stay 400 V.

In my opinion, no AVR will help you. Try to fit a VFD on this big motor.

__________________
Julius
Register to Reply
Register to Reply 14 comments