Accuracy Class for Energy Meters

07/25/2015 6:12 AM

What will be the difference of energy measurement by using CT's of class-1.0 and 0.2 class for the energy meter of Class 0.2

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Accuracy class for energy meters

07/25/2015 6:27 AM

If the meter can't tell the difference, probably nothing. Otherwise, something like the difference in precision/accuracy of the two CTs. And even then, if your class 0.2 CT happens to be "lucky", maybe still no difference.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Accuracy class for energy meters

07/25/2015 9:44 AM

The difference will be either some, or none.

Read this and learn:

Accuracy Limit Factor and Instrument Security Factor of ...

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Accuracy Class for Energy Meters

07/25/2015 6:44 PM

Disregarding the uncertainty introduced by the meter and the PTs, the difference due solely to the CTs will be on average 0.8%. So if this is a residential meter and it reads 1,000 kWh for the year you will be under/over paying for 8 kWh.

In reality the number is probably smaller because as you have more ITs (Instrumentation Transformers) involved the overall statistical error is lower due to the positive errors in some ITs being cancelled by the negative errors in the others.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Participant

Join Date: Feb 2012
Location: India
Posts: 4
Good Answers: 1
#4

Re: Accuracy Class for Energy Meters

07/31/2015 8:10 AM

There are many technical aspects that need to consider before. An digital meter will have certain precision class and range where the meters performance will be as per commited accuracy, also factors like uncertainty which depends on samples per cycle etc.

To simplify answer to your query, system accuracy will depend on sq.root of sum of (instrument transformer accuracy square & meter accuracy square)

This is one way of deriving the final system accuracy of individual instruments/meters.

Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 21
#5
In reply to #4

Re: Accuracy Class for Energy Meters

08/31/2015 1:23 PM

if u use 1.0 class CT then there will be 1% error in measurement and for which exclusively the CT will be responsible..............there will be another 0.2 % measurement error for which the meter will be responsible