3-Phase 4-Wires System

08/07/2015 8:07 AM

Hi, Had a doubt for 3-phase 4-wires systems in american practice. I have been taught that the term 3-phase 4-wires is referring to how the secondary of distribution transformer (feeding the switchgear) is configured. I mean 3Ph /4W is giving the evidence that the xmer secondary windings are configured as solidly grounded star. My question is: Must the neutral star point be brought to the switchgear even if i have just 3 phase 3 wires loads? If yes, Can i use the ground bus (inside buseay) for this purpose? Thanking you in advance. Mark

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: 3-phase 4-wires System

08/07/2015 9:37 AM

The term "3 phase 4 wire" does not mean it must be a wye system. It could be a delta system where there is a center tap on one of the transformer windings. You need to know the voltage levels of the system to decide if it is wye or not.

To get the advantage of a solidly grounded system on a wye system (or on any 4 wire system) you need to ground the 4th wire somewhere. Without a doubt, doing so at the switchgear is the best place to do that.

From there on... if the neutral is not needed at downstream loads, there is no need to extend the neutral conductor to those loads.

The ground bus inside the switch gear is for bonding, use the neutral bus inside the switchgear.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 4)
Active Contributor

Join Date: Jul 2015
Posts: 23
#2
In reply to #1

Re: 3-phase 4-wires System

08/07/2015 10:32 AM

Many many thanks North60. That was a fantastic answer which cleared most of my doubt. As 4 wires are referring to the live three phases +neutral (i.e. The ground does not count), I understood from your answer that the fourth wire (neutral) shall be extended to the entery equupment and grounded somoeewhere there if the loads are 4 wires ( i.e the nwutral bus bar is not provided inside the switchgear). Kr Am I right? Shall I use the ground bus, provided inside the busway,for extending the forth conductor inside the switchgear? Deeply appreciating your answer. Mark

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3
In reply to #2

Re: 3-phase 4-wires System

08/07/2015 11:32 AM

You need to understand how the switchgear you have is configured. If it is 3p 4w switchgear, you should have 3 busbars for the phases and a neutral bus and you may also have a bonding bus.

Evaluate the switchgear you have to see if it is suitable for your use under the codes and standards in effect in your jurisdiction and then proceed as required by those documents.

As I can not "see" the switchgear from here, it would be reckless on my part to say "yes" or "no" to what you are asking.

You may want to get someone to do this for you if you cannot do so yourself.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 127
Good Answers: 3
#11
In reply to #2

Re: 3-phase 4-wires System

08/17/2015 9:23 AM

We always run an Equipment Grounding Conductor (EGC) from the switchgear to the load, along with the Load Conductors. (I have encountered SO many damaged or loose conduits and EMT).

This EGC may or may not be required to be bonded to neutral in the main switchgear. However, such bonding is a Most common practice, and is the default unless the electrical engineer has compelling reasons.

If the load is designed to not use a neutral load conductor (delta-configured), it may be possible to omit neutral on the branch circuit, but first check your local Code requirements. Finally, consider whether the load may be replaced at a later date with one that does require neutral.

__________________
avid0g
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 127
Good Answers: 3
#12
In reply to #11

Re: 3-phase 4-wires System

08/17/2015 10:12 AM

Correction, as North of Sixty said, you may omit neutral on feeders and branch circuits that do not have neutral load currents. And I emphasize his other point: there are great advantages to bonding the source's neutral conductor to Equipment Ground, even though no load uses neutral.

__________________
avid0g
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9913
Good Answers: 1141
#6
In reply to #1

Re: 3-phase 4-wires System

08/07/2015 2:18 PM

Measure your voltages. If the 4 wire system is 3 phases + neutral (Y), you should have the same voltage reading between each of the three phases and the neutral. The phase to phase voltage should be 1.732 times the phase to neutral voltage.

If the fourth wire is a centertap between two phases, the voltage between it and these two phases would be 1/2 the phase-to-phase voltage. The voltage to the remaining phase would be about 1.07 times the phase-to-phase voltage.

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#7
In reply to #1

Re: 3-phase 4-wires System

08/08/2015 9:58 AM

Excellent answer.

I'm surprised, considering where your location is, that you've seen 3 phase voltages. Isn't that single phase only territory up there?

Is that 600V way up there like the areas south of you? I'm designing/building a control system for that part of Canada, and have found some major companies rate their equipment to 600V but only test it to 480V. Had to change some of my stocked components to a different brand.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#8
In reply to #7

Re: 3-phase 4-wires System

08/10/2015 10:21 AM

Please tell me you are joking...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#9
In reply to #8

Re: 3-phase 4-wires System

08/10/2015 10:26 AM

Of course I'm joking.

However, not about the 600V AC. You got that way up there? That makes life difficult for 480VAC panel designers/builders when you realize your stock products are only recommended for 480VAC service.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#10
In reply to #9

Re: 3-phase 4-wires System

08/10/2015 11:22 AM

Phew... you had me worried.

Most 3 phase installations here are 208Y/120 volt installations. Some of our new larger buildings do have 600Y/347 volt systems in them or in the process of being installed, such as a few of the larger schools, Qikitanni General Hospital, new airport, new Iqaluit Aquatic Center and new Canadian High Arctic Research Center.

As to 480Y/277 volt systems, there are very few of them (I can think of only a handful) and those are limited to specific utilization equipment and not building services (the utility will not supply a 480V consumer service). So... step up transformers are needed to get the 480 volt source for the equipment in question.

Ya... ya have to watch this issue. If you are making and selling stuff meant for use in Canada on 600 volt systems, it is advisable to get it certifed to the proper Part II standard or we reject it upon inspection. The 480 volt standards do not cut it.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: 3-Phase 4-Wires System

08/07/2015 1:06 PM

But to answer your other question, you may NOT use the ground bus as a neutral bus. They must remain separate. The ground is for safety, the neutral is considered a current carrying conductor. The neutral may or may not be bonded to ground depending on the specifics of the installation, you cannot assume it is..

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5
In reply to #4

Re: 3-Phase 4-Wires System

08/07/2015 1:43 PM

I agree fully. I decided not to include that info as I am not quite sure if the OP is looking at a ground rail or a bond rail.

I truly wish that the industry would retire the term "ground bus" from use. After the neutral to ground connection point, any conductor or busbar (other than the actual neutral bus or a neutral conductor) that extends from that point any further should be considered a "bonding bus" or a "bonding conductor" that serves to "bond" something to the neutral/ground connection point.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Feb 2010
Posts: 127
Good Answers: 3
#13
In reply to #5

Re: 3-Phase 4-Wires System

08/17/2015 10:53 AM

Since we still have ungrounded or high impedance grounded systems, the terminology requires more complexity. I prefer to say "Equipment Ground Bus", since that works all ways.

In fact, this discussion thread is based on the question of whether that bonding is necessary. Some system designs emphasize fault tolerance over every other consideration and, thus, are "ungrounded".

__________________
avid0g
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#14
In reply to #13

Re: 3-Phase 4-Wires System

08/17/2015 11:01 AM

Agreed... it is very common for systems that require "up time" be not gounded, such as sewage transfer staions. But... they require ground fault indication equipment and skilled resources to deal with any issues that crop up.

Often... the 1st line to ground fault is ignored, and a subsequent fault will be at the elevated fault currents present during a line to line fault event.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Active Contributor

Join Date: Jul 2015
Posts: 23
#15

Re: 3-Phase 4-Wires System

08/17/2015 12:17 PM

In ungrounded systems, one ground fault can be detected by ANSI 64. VAMP265 (SCHNEIDER) will be working nicely for this.

Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

avid0g (3); JRaef (1); Mark1234567 (2); North of 60 (6); Phys (2); Rixter (1)

Previous in Forum: Earth Leakage Relay   Next in Forum: Using Photocell with a Dimmer or Potentiometer

Advertisement