Anonymous Poster #1

Failure of Tripping Coil in MV Breaker

08/11/2015 3:30 AM

Dear guru;

We face problem in our ABB VD4 11kV breaker , Both tripping coil were faulty on the same time during stopping of 11 kV motor. And motor had to stop by manual push button in the breaker.

The breaker have 2 The tripping coils and also both are having coil supervision relay ; it was showing healthy until command stop command were given from DCS; The 1st and 2nd opening coil both get faulty(winding open) and also free wheel rectifier found faulty.

We check the voltage Supply is normal 115VDC according trip coil operating voltage 110-125V DC.

The breaker had been operated succefully before for around 3 years

Please help me with idea or suggestion what is possible cause of failure of tripping coil if any body have similar experience or knowledge.

We contact to manufacturer and they told still under investigation.

Thanks a lot for who ever share the knowledge and experience.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Failure of tripping coil in MV breaker

08/11/2015 4:08 AM

If the breaker is energize-to-trip, check for loose connections or other open circuits in the trip circuit components and wiring.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Good Answer
Anonymous Poster #1
#2
In reply to #1

Re: Failure of tripping coil in MV breaker

08/11/2015 4:54 AM

Quote"(If the breaker is energize-to-trip, check for loose connections or other open circuits in the trip circuit components and wiring.)"

Thanks for the quick response;

Later on we found mechanism for 2nd opening coil(back up) the engagement lever was detached; that could be the reason for 2nd opening coil faulty because it was continuously energized without opening the breaker; while stop command given .

But for the failure of 1st coil still we can't able to identify the cause.

Reply
Anonymous Poster #2
#3
In reply to #2

Re: Failure of tripping coil in MV breaker

08/11/2015 5:34 AM

Make sure that you have breaker NC aux contacts in series with your trip and close coils.....in that way you should not burn your coils....must I send you a picture how its done or will you manage

Regards

Reply
Anonymous Poster #1
#4
In reply to #3

Re: Failure of tripping coil in MV breaker

08/11/2015 6:15 AM

Quote: "Make sure that you have breaker NC aux contacts in series with your trip and close coils.....in that way you should not burn your coils....must I send you a picture how its done or will you manage"

THANKS FOR THE ANSWER

Yes ;Already NC Aux contact is connected in series with coil to cut the supply when coil has done the job(to drive mechanism to open breaker). That's why the coil is burn because the supply was not cut off before breaker open and activating also Aux. contact.

Reply
2
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#5

Re: Failure of tripping coil in MV breaker

08/11/2015 6:53 AM

You've identified that the "back-up" circuit wasn't workingdue to disconnected mechanical part.

Failure mode of the primary disconnect might be voltage drop in primary energiser circuit. This could be deteriorated wire termination or insulating material in the contactor. If contact face contamination is the cause, then you could now face an intermittant problem as the contacts may not close on that exact piece every time.

Failure of the freewheel diodes indicates some voltage/current related failure. Maybe a high voltage or induced voltage fault has hit the coils and their respective diodes.

You know that the back-up relay mechanical didn't work, so the conduction path was not from that element.

Good luck with your search. STAY SAFE!!!!

__________________
Just an Engineer from the land down under.
Reply Good Answer (Score 2)
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#6

Re: Failure of Tripping Coil in MV Breaker

08/11/2015 9:03 AM

A freewheeling diode provides a path for discharging the very high voltage induced by the collapsing DC field whenever the breaker is opened/tripped.

The freewheeling diode being faulted will allow the induced voltage to circulate within the control voltage circuit(s) and cause failure of the close and/or tripping coil(s) and possibly other components.

If the breaker mechanism was/is mechanically binding, the higher current required to overcome the mechanical load will magnify the collapsing field affect and cause the induced voltage to go even higher.

I would thoroughly clean and PM the breaker following the manufacturer's recommended procedure, replace all of the bad components, then test the breaker electrically and cycle it at least 5 times to ensure it is fully functional.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply Score 1 for Good Answer
3
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#7

Re: Failure of Tripping Coil in MV Breaker

08/11/2015 11:34 AM

One question nobody has asked is what is the mechanical condition of the circuit breaker? When was the last time it had a complete inspection and mechanism maintenance performed? Many people operate their breakers periodically, and assume just because the breaker opened or closed this time it will do it again next time.

In my experience, one of the most common causes of trip coil failure is that the breaker mechanism lubrication has thickened or been worn away to the point that the mech sticks. In that case, the the trip coil solenoid is unable to cause the latch to release the springs (or other energy storage) to cause the breaker to trip. The coil then sits there trying to trip the breaker until it burns up, and the owner wonders why it happened since the breaker worked fine the previous time.

The breaker mechanism has many rotating and pivoting parts, as well as cams and bearing surfaces, that need periodic lubrication. When the grease or oil ages or is worn away, the friction can increase dramatically, and a mechanism that operated freely last week will stick and sit immovable today.

Get a qualified service organization to do a complete maintenance on your breaker. I'm willing to be that they find it to be gummed up to where it won't operate.

__________________
To get the right answers, first you need to ask the right questions.
Reply Good Answer (Score 3)
Anonymous Poster #1
#8
In reply to #7

Re: Failure of Tripping Coil in MV Breaker

08/12/2015 3:28 AM

Quote "One question nobody has asked is what is the mechanical condition of the circuit breaker? When was the last time it had a complete inspection and mechanism maintenance performed? Many people operate their breakers periodically, and assume just because the breaker opened or closed this time it will do it again next time.In my experience, one of the most common causes of trip coil failure is that the breaker mechanism lubrication has thickened or been worn away to the point that the mech sticks. In that case, the trip coil solenoid is unable to cause the latch to release the springs (or other energy storage) to cause the breaker to trip. The coil then sits there trying to trip the breaker until it burns up, and the owner wonders why it happened since the breaker worked fine the previous time.

The breaker mechanism has many rotating and pivoting parts, as well as cams and bearing surfaces, that need periodic lubrication. When the grease or oil ages or is worn away, the friction can increase dramatically, and a mechanism that operated freely last week will stick and sit immovable today.

Get a qualified service organization to do a complete maintenance on your breaker. I'm willing to be that they find it to be gummed up to where it won't operate."

THANKS FOR SHARING GREAT IDEA! Your point of view is very useful for us

Reply
Participant

Join Date: Jul 2015
Location: South Africa, Limpopo Province, Tzaneen town
Posts: 3
#9

Re: Failure of Tripping Coil in MV Breaker

08/12/2015 3:30 AM

Hi,

I am sitting with the same problem on metal-clad switchgear. I keep on loosing a blocking diode, burning a output 1 contact and burning the trip coil. It happens on different schemes all in the same station. I also took station earthing into consideration but to no avail. I also have a linear resistor/snubber to protect against contact burning and the diodes is supposed to be able to handle the back EMF.

I have attached a couple of documents for you to see that the circuit is simple but the damage is extensive.

Any help or advise would be appreciated taking into account that I did have the mechanical part of the breakers maintained and tested.

Thank you in advance

Reply Score 1 for Good Answer
3
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#10
In reply to #9

Re: Failure of Tripping Coil in MV Breaker

08/12/2015 9:03 AM

It is difficult to read the print but it appears that there is an MOV in parallel with one of the devices.

An MOV which consists of back-to-back diode configuration works well with AC to limit voltage levels by shorting the circuit but it cannot/will not perform well in a DC circuit.

A simple reversed-biased diode placed across the terminals of any coil that is at-risk will keep the induced voltage level to a minimum. In cases of very high current it may be necessary to add a resistor in series with the diode to prevent the diode from being burned open.

I would attach a high speed recording oscilloscope directly across the coil terminals and operate the breaker to identify what is happening.

Be sure to set the scope up at maximum volts-per-division as the induced voltage from the collapsing DC magnetic field will be in the thousands of volts range.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply Good Answer (Score 3)
Participant

Join Date: Jul 2015
Location: South Africa, Limpopo Province, Tzaneen town
Posts: 3
#11
In reply to #10

Re: Failure of Tripping Coil in MV Breaker

08/13/2015 8:46 AM

Thanks for the advise. I did arrange for the scope before your answer but I am impressed with the "retrofitting" of the MOV. I will keep you updated on the progress.

South African Thanks

Reply
Reply to Forum Thread 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: