Light Fixture Grounding

08/21/2015 11:48 PM

Immediate disclaimer: not an engineer, not good with DIY (although working on it...)

I'm trying to replace a shorted light fixture that used to hang clear outside my covered back steps. It seems to have shorted due to moisture, so I ended up pulling the extension wire out and planned to install a new fixture at the outlet box inside the porch roof instead, to avoid rain getting in the new fixture. When I took everything apart, though, I found that the extension wire used for the old fixture was grounded only to the box; in other words, the supply coming from the house is 2-wire ungrounded.

I had a contractor over a few weeks ago for an unrelated job and asked him about installing a modern 3-wire grounded fixture using the 2-wire supply, and he sort of shrugged about it. Is it safe to ground the fixture only to the box and connect it to a 2-wire supply?

The supply cable is armored, btw--I wasn't sure if that would serve as ground. That said, the house is 135 years old and the wiring is of different ages in most parts, so I have no idea how old this cable is.

__________________
Nobody realizes that some people expend tremendous energy merely to be normal. -Camus
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#1

Re: Light fixture grounding

08/22/2015 2:42 AM

Some electrical codes do allow for the use of the cable armour as the circuit protective conductor, but it's generally limited by provisos such as earth fault current carrying ability etc. A separate earthing conductor is usually a better choice, however, if you employ double insulated cable from the junction box to the luminaire, and carry that double insulation all the way into the lampholder, then earthing of the fitting can be foregone. Obviously the above does not apply to luminaires that have other exposed metal that may become live such as ballasts etc.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#2

Re: Light fixture grounding

08/22/2015 4:03 AM

I'd call an electrician who knows the codes where you are and has experience with old houses.

If you are going to do this yourself you might make yourself very unhappy if something happens. Don't do it!

Usually lights only have 2 wire supply. They are on a different circuit than the power points. If you need ground you will have to pull a new cable there and connect to the poweer points circuit. And thats where you should better talk to an electrician or hire him straight away to spare you the pain. My take is that if the housing is not grounded properly and its wet and the housing gets live all sorts of things can happen.

Good luck!

__________________
Common Sense Dictates
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#10
In reply to #2

Re: Light fixture grounding

08/24/2015 9:34 AM

Good Answer.

A local Electrician will know the pertinent codes for that region and will be able to do the job correctly and safely.

(In Chicago, we allow grounding to the box, because all wiring has to be inside metal conduit, and all boxes must be metal, so the conduit provides an uninterrupted connection to the fuse box/breaker panel, where the panel's ground is bonded to the cold water supply for the house, said piping running straight into the earth serves as a HUGE ground conductor. Remember, for most circuits, the protective ground is there to insure that any break in a 'hot' wire will immediately cause a short and blow fuses/trip breakers, instead of continuing to spark to ground and potentially cause fires.)

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Light fixture grounding

08/22/2015 5:32 AM

What you propose is safe.

While it may, or may not, meet the latest electrical codes, such as NFPA-70, it is safe.

I would not hesitate to do as you suggest.

Let there be light!

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#4

Re: Light Fixture Grounding

08/22/2015 9:48 AM

Is there metal conduit running from the box back to the breaker panel?

Although I am not quite 135 years old, there was a time when the conduit (if metal) was an acceptable ground path.

Otherwise, if there is NO chance of moisture intrusion into this box, I'd (reluctantly) go with 2 wire.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5

Re: Light Fixture Grounding

08/22/2015 12:10 PM

Any new work should be up to code...the lighting fixture should be grounded to the conduit and the separate ground should feed back to the panel....they can be combined....but you want any short in the light to feed back to the panel ground to avoid shock....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6

Re: Light Fixture Grounding

08/22/2015 6:12 PM

You have not given your location. No one on CR4 can look at the right electrical code.

Other codes may apply - if you are in the UK, the Building Code says that [if you are not a registered electrician], in a residence, a person can only do electrical limited electrical work without notifying the local authority.

This limited work includes adding an outside light connected to an existing circuit, which is your case at worst.

But non-notifiable work is required to comply with the IET Wiring Regulations BS7671 latest issue, currently 2008 amendment 3, 2015: including the required inspection and testing and issue of a minor works certificate.

Having noted that, many lighting fittings are "double insulated" and do not require an earth. These should carry a "two squares, one inside the other" symbol such as appears on mobile phone chargers which do not have an earth pin on the plug or have a plastic earth pin.

Current regulations require an earth terminal to be installed at each light connection point because the fitting could be made of metal and obviously needs an earth. However, since you are only replacing a lamp and are not adding a new circuit, I do not think you are required to add an earth if your fitting is double insulated.

In my memory, back 60 years & most time since most lamps have hung on a cord out of reach and holders were made out of insulating material anyhow.

Lots of modern fittings that look like ancient metal ones are actually plastic.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8
In reply to #6

Re: Light Fixture Grounding

08/24/2015 6:37 AM

I should have added [but it was late!] that your double insulated light fitting should be weatherproof (code IP44 or higher numbers, many are IP65) and connected by a cable with an integral insulating oversheath. I would recommend a round section flexible cord rated for outdoor use.

If your house is 115 years old, I would recommend an inspection and test of the electrical installation by an electrician.

In the UK, the regulations which I noted write that a signed Electrical Installation Condition Report, including test results, "shall be given to the person ordering the work", that is you! The report should advise time before next inspection, when the test results will enable deterioration to identified by comparison with previous reports. If you do not get the report, complain to the electrician's certifying authority (reports have been noted more by the omission than presence).

Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1268
Good Answers: 27
#7

Re: Light Fixture Grounding

08/23/2015 10:10 AM

Due to the age of your house, the armored cable or BX cable that currently in place may or may not be solidly connected to earth and grounded back to the main box source. You can use 2 or 3- wires and apply the double insulated approach of wiring as advised and be safe as long as you also will use an all plastic fixtures from the existing electrical junction box. Run the wires thru a small pvc tube to carry the wires to the outside porch.

Double insulated wired devices is an acceptable practice even in hospitals where electrical safety is of utmost importance against minute electrical shocks! Good luck!

__________________
vsar
Register to Reply
Guru
Canada - Member - New Member

Join Date: Jul 2013
Location: Canada but south of 49
Posts: 895
Good Answers: 20
#9

Re: Light Fixture Grounding

08/24/2015 8:42 AM

If you have armored cable, the wiring isn't as old as your house, that's for sure. My house is a similar age - 146 years. The thing you need to watch for is what the cable is connected to inside the house. You may be dealing with some old knob and tube as well. It was not uncommon to connect directly to it. Left undisturbed it will last for many more years, but the minute you start to work on it or with it, or any rodents get at it, it will likely become a problem.

__________________
Never stop learning
Register to Reply
Power-User
Hobbies - Musician - New Member Technical Fields - Technical Writing - New Member

Join Date: Nov 2012
Posts: 431
Good Answers: 6
#12
In reply to #9

Re: Light Fixture Grounding

08/24/2015 12:44 PM

Yeah, the knob and tube is long gone for my house, and all the wiring in the attic (which supplies power out to the stoop) is armored. A lot of the house was rewired as recently as 10 years ago.

__________________
Nobody realizes that some people expend tremendous energy merely to be normal. -Camus
Register to Reply
Guru
Canada - Member - New Member

Join Date: Jul 2013
Location: Canada but south of 49
Posts: 895
Good Answers: 20
#14
In reply to #12

Re: Light Fixture Grounding

08/24/2015 3:09 PM

Good for you. One less thing to put spend your $$ on.

__________________
Never stop learning
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#11

Re: Light Fixture Grounding

08/24/2015 12:38 PM

Warning, codes and lawyers will eventually get us all. It may be code where you are that all outside fixtures have to be ground-fault-interrupted circuits. Very expensive. If you call in an electrician, he will be obliged to run a whole new wire to a very expensive gfci breaker in your box. If your box is not rated for a gfci breaker, you will need a new box. If the wiring to your box is not rated for the new code, you will need a new feeder to the box, and on and on.

For a test, connect the hot wire to a light fixture and the white wire from the fixture to the armored cable. If the light works bright and proper, the armor is grounded. If not, your circuit is not grounded. If possible, run a dedicated wire from the fixture to ground and do the test again. If that's not possible, install a fixture that can't be touched by passers-by. If it can't be touched, you are safe from immediate concern of shocking someone. You are still at risk of fire if the fixture shorts out and the fuse or breaker doesn't trip right away.

__________________
mike k
Register to Reply
Power-User

Join Date: Dec 2007
Posts: 177
Good Answers: 6
#13

Re: Light Fixture Grounding

08/24/2015 2:07 PM

I'd put it on a GFI.

Register to Reply
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (2); adreasler (1); Hannes (1); IdeaSmith (1); Kevin LaPaire (2); lrsheldon (1); lyn (1); mike k (1); SolarEagle (1); spades (1); vsar (1); WJMFIRE (1)

Previous in Forum: Coolant Temperature Sensor   Next in Forum: Generator Synchronization Issue

Advertisement