Generator Synchronization Issue

08/23/2015 4:57 AM

Dear all, request your contributions to clarify a question, ie. There is 2nos. 3.3kV, 2000kVA gensets, CAT, There is a differential protection trip (trips even the setting made to 15%) from control panel when both gensets are synchronized. no any issues when only one is running. now we are testing the synchronization so still no tested with load connected. The supplier tried a lot and finally they said that 'synchronization of gensets in in no load is not possible' but i am not convinced with the statement and im not confident to allow them connect the load for their experiment. there is dummy load bank but it can be used for only one genset at a time, there is interlock. So please share your knowledge to confirm the statement. i believe it is possible to synchronize even there is a limited reverse power.

thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: generator synchronization issue

08/23/2015 7:10 AM

Why would you not believe the supplier?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Jul 2015
Posts: 23
#2

Re: generator synchronization issue

08/23/2015 7:49 AM

What is the model of the controller? Anyhow; I have doubt that the Gen Sets will be synchonized under loading condition if they cannot with no load.

Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#3
In reply to #2

Re: generator synchronization issue

08/23/2015 8:13 AM

symap - bcg,

Register to Reply
Active Contributor

Join Date: Jul 2015
Posts: 23
#4
In reply to #3

Re: generator synchronization issue

08/23/2015 8:31 AM

Is it passive synchronizer?

Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#5
In reply to #4

Re: generator synchronization issue

08/23/2015 8:47 AM

http://www.voltex.com.au/wp-content/uploads/2012/05/SYMAP-Brochure.pdf

model bcg

Register to Reply
Active Contributor

Join Date: Jul 2015
Posts: 23
#6
In reply to #5

Re: generator synchronization issue

08/23/2015 9:19 AM

The solution is to activate 25A(not only 25). That should sort the problem out.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9913
Good Answers: 1141
#7

Re: Generator Synchronization Issue

08/23/2015 7:36 PM

My understanding of the differential protection trip circuit is that you are measuring the neutral current and also the vector sum of the three phase currents. If all is well within the "protected zone", they should sum to zero, or if not, some of the current is returning through ground and the power is shut down.

I understand that if either generator is run by itself, there is no problem, but if they are parallel, then it trips. Is this a new installation, or did it once work properly and is now faulty? A simple schematic would be helpful. If it has never worked, perhaps it is not set up properly. Finally, are you sure it's the differential protection that is causing the shutdown and not another issue like phase reversal on one of the generators?

Just some thoughts. I hope I have not belabored the obvious.

Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#8
In reply to #7

Re: Generator Synchronization Issue

08/24/2015 1:42 AM

thanks, its new installation, under commissioning, it trips in both differential and reverse power. differential protection is individual for each set. if there is any leakage it should trip when it running individually also but it doesnt happens. that means abnormality is only after paralleling. the relay gives closing signal only after checking the parameters and its correct also.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9913
Good Answers: 1141
#10
In reply to #8

Re: Generator Synchronization Issue

08/24/2015 8:18 AM

Are you sure it's the differential that's tripping it?

Two things come to mind which come into play when generators are connected in parallel.

Governor droop allows the generators to share the "real" load (KW). When paralleled, one generator governor should be in "droop" mode. If both governors are "isochronous", a small misadjustment in the throttle settings will allow one generator to assume the whole load and even motorize the other generator.

Cross current compensation in the voltage regulators allows the generators to share the "reactive" load. Reactive load is where the current is out of phase with the voltage, and is not only due to the characteristics of the load, but also can be a result of the voltage levels (excitation) of the two generators not being set to the same value. A possible problem would be if current sensors (CTs) were not wired with the correct polarity for the cross current compensation.

If you have a large amount of current circulating between the two machines, possibly one or more of the current transformers in the differential protection circuit are saturating. If this is happening, it would appear as a ground fault (current imbalance) and trip the circuit.

I hope these ideas are helpful. (It's been a long while since I have worked on generators.)

Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#11
In reply to #10

Re: Generator Synchronization Issue

08/24/2015 9:57 AM

its not only differential but also the reverse power. i will check it. but since it is not loaded yet no any chance to become ct saturated, if any ct polarity is changed tht time also diffntl will work. the cts are tested also prior to the commissioning. because to saturate at least full load current to be flown once it didnt happen yet. any way they will continue next then will come to know.

thanks

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9913
Good Answers: 1141
#13
In reply to #11

Re: Generator Synchronization Issue

08/24/2015 1:06 PM

I was thinking not current flowing towards the load but between the alternators due to unequal governor settings (real current) or unequal excitation (reactive current) or both. Just guessing here.

We can throw out ideas of what we think might be going on, but someone on site really needs to look into it. (I've done troubleshooting remotely on equipment I was intimately familiar with and it's still tricky.) If your vendor "owns" it until it's accepted, you're best to go along with his suggestions, imho.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9

Re: Generator Synchronization Issue

08/24/2015 2:59 AM

Synchronisation is half the story load sharing is the other.....

When the gensets are synchronised and tied they should both be feeding into the dummy load bank on the bus, no?

We need more information about the synchro panel and controller you are using.

Let them try.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#12
In reply to #9

Re: Generator Synchronization Issue

08/24/2015 10:01 AM

the relay is symap BCG. pls refer

http://www.voltex.com.au/wp-content/uploads/2012/05/SYMAP-Brochure.pdf

since there is one common load bank only for both gensets it cant be loaded during parallel operation, there is interlock. thanks

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#14

Re: Generator Synchronization Issue

08/24/2015 6:42 PM

and hand speed control

Synchronisation not possible.

Trips on breaker close.

Is it certain sets have same phase sequence at the breaker generator sides?

Unloaded gensets certainly can be paralleled.

Does the differential relay indicate which phase?

Have you tried synchronising lamps; synchroscope, or other elementary check with breaker close coil disconnected and hand speed control before trying actual close?

Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#16
In reply to #14

Re: Generator Synchronization Issue

08/25/2015 5:08 AM

we done the synchronisation using symap relay in auto and by sychroscope in manual also (control panel having both mode of operation. its working fine prblm happens only after parallel operation. any way we stopped the testing and CAT will send their experts to sort out the issue. as you said they also confirmed that sets can be paralleled in no load. thanks

Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#15

Re: Generator Synchronization Issue

08/24/2015 11:48 PM

More than likely there is some crossed wiring in the CT circuits. Just because you see that the polarity markings are correct does not ensure that the interconnecting wiring is correct, you must check the polarity of all CTs and PTs from their terminals all the way through any intermediate terminal blocks back to the relaying and control panels.

Properly set up differential relaying should only operate if there is a fault within the differential zone or a huge amount of transformer inrush current, but you haven't gotten that far yet. Uneducated changing of relay settings until it is trip-free will probably leave you without any protection if a true fault occurs. You should never subject a DG set to any reverse power, but the fact that you get a trip indicates a pair of reversed leads somewhere.

Your supplier's statements indicates that it is as clueless as you are; therefore it is necessary for you to contact Caterpillar directly and have them send out a team of knowledgeable commissioning engineers before your constant uneducated operation of the equipment finally causes it to fail catastrophically. All else is folly.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#17
In reply to #15

Re: Generator Synchronization Issue

08/25/2015 5:20 AM

you are right sir cross wiring in ct circuits always operate unbalance relays. we faced in another 415V stand alone set. as you said it was clueless statement, we stopped the testing and they will send their experts to solve it. thanks

Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#18
In reply to #17

Re: Generator Synchronization Issue

08/25/2015 8:54 AM

Thank for the feedback! The forum always like to hear that its "remote diagnostics" were on point and that its "suggestions" are actually acted upon. Glad we could help.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#19
In reply to #18

Re: Generator Synchronization Issue

02/15/2016 1:46 PM

dear sir, would you please reply for a question. there are 4nos 3.3kv 2000kva gensets are running in parallel no load, while running on no load what is the permissible current in each genset. because while connecting gen-1 and 2 it works fine no current or power. but if the 3 or 4 are added to this, or 3 and 4 only connected and runs parallelly, the meter shows current up to 100A and power 2 to 30kw it varies also. its cat genset. all 4 sets are having the same ratings and parameters. the supplier says its normal and doesnt make any harm to the system.

thank you

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#20
In reply to #19

Re: Generator Synchronization Issue

02/15/2016 3:35 PM

If only sets 3 and 4 behave like this and all units are identical, then 3 and 4 have the same fault or most likely, wrong wiring again. It is not normal and it will do harm if left.

Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#21
In reply to #19

Re: Generator Synchronization Issue

02/15/2016 7:43 PM

The units may be identical, but are the settings for the AVR, engine control, and both droops? That mysterious 100A is probably a circulating current traveling between units, as is the 2 to 30kW.

The supplier is wrong, contact Caterpillar directly and tell them what their representative told you.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#22
In reply to #21

Re: Generator Synchronization Issue

02/16/2016 9:54 AM
Register to Reply
Register to Reply 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (2); Mark1234567 (3); RAMConsult (3); Rixter (3); roykav (9); Tornado (1); Wal (1)