For lower cross section cable current capacity in ground is more than current capacity in air but same is reversed for higher cross section.Please help by explaining the reason..
The maximal current through a cable depends on the resistivity which leads to heat amount/ length unit and the capability to transfer it to the environment.
Heat generation is proportional to current density x conductor area and heat transfer is proportional to contact area with environment x heat conduction / convection factors but decreases with insulating properties of the mantel. If diameter is low the ration heat transfer area to conductor are is bigger and the insulation is thinner so that convection could be preponderant.
In ground the nature of the ground and its content of water can lead to vzery different results.
In my opinion, it depends on many factors as ambient
temperature, insulation and sheath, number of conductor and number of cables,
the limits of "lower cross section cable" and other.
Usually up to 2 k.m./W earth thermal resistance and up to 30oC ambient it is correct up to 6 awg [16 sqr.mm copper
conductor XLPE insulation].The explanation could be as follows:
The thermal flux[ equivalent] resistance will be the same
in the inner part-in insulation and jacket[sheath]. What will be different is
the outside thermal resistance.
Let's take IEC 60287-2-1 definitions:
cable in free air
T4=1/(π* De* h* Δθ^0.25) ; T4=K/DeK is relatively constant then T4 decrease with the cable diameter.
cable in ground : T4=1/(2*π)* roT* ln(2*u) ; T4=A*[B-ln(De)]While A*[B-ln(De)]<K/De
then Iground>Iair.