PI Value of 6.6 KV 450 KW Motor

08/28/2015 5:34 AM

When we measure PI value of each phase of star connected 6.6 KV 450 KW motor with winding 20 years old comes 2.4 each phase at 2.5 KV. When we make star point with metal clamp without touching the earth of stator frame body PI value comes as 1.4.What could be reason for Less PI value than 2.4

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: PI VALUE OF 6.6 KV 450 KW MOTOR

08/28/2015 5:59 AM

I can't tell just where you are measuring in each case, but 2.4/1.4 ~~ sqrt 3.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Sep 2009
Posts: 33
#2
In reply to #1

Re: PI VALUE OF 6.6 KV 450 KW MOTOR

08/28/2015 6:21 AM

Each phase of cable star point removed and as one phase cable as single measured along with windings of that phase is measured PI Value is 2.4 and when all cable of each phase star point joined together and measured as 1.4 PI value with one cable phase as the PI value of motor normally measured as complete phase as star or delta windings connected.What is the reason for the above

Register to Reply
2
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3
In reply to #2

Re: PI VALUE OF 6.6 KV 450 KW MOTOR

08/28/2015 9:24 AM

If the test leads are connected from motor "T" lead to ground/earth with the star point connection open and you then connect one or more additional motor windings to the winding under test via the star point connection, the current provided by the test set will be impressed onto and into the added windings according to insulation condition and impedance.

Basically you are creating parallel paths for current leakage to occur therefore the absorption current value will increase and this will decrease the PI value obtained during the testing.

"value of motor normally measured as complete phase as star or delta windings connected"

I suggest you follow standard motor winding test procedures so that the PI and other test results stay within range of known, accepted values.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: PI Value of 6.6 KV 450 KW Motor

08/28/2015 9:47 AM

A lack of understanding of how the PI values are calculated. When you place your test leads on 1 winding, only the leakage current between that winding and the surrounding metal is measured. When you connect the neutrals together you now have increased the surface area of insulation in contact with the metal; more surface area equals more distributed impedance in parallel equals a lower PI value. However there's more to calculating the PI than just Ohm's law, you also have to account for the DAR (Dielectric Absorption Ratio), temperature, humidity, time, etc.

Please consult your copy of the latest revision to IEEE 43-2000, this article may help, also check the manual that came with your tester for more insights.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#5

Re: PI Value of 6.6 KV 450 KW Motor

08/28/2015 9:51 AM

http://electromotores.com/PDF/InfoT%C3%A9cnica/EASA/Using%20Polarization%20Index.pdf

J; Here is the path to a very informative whitepaper on PI testing. As I do not know anything about what the testing methods used were nor what prior testing was performed, it would be best if you review this documentation then react accordingly.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply