20 MVA Transformer Problem.

09/09/2015 3:29 AM

we have 20 mva(15.75/6.9 kv dyn11) unit transformer.during rolling of turbine our UT draws enormous current on residual voltage of 500v.after isolating it from system same problem exist.But after draining oil from transformer when we applied 415 v on HV side a spark comes from the core side(exactly not know if it is winding or core) 2 times. After that all testing reports come normal.Kindly suggest the problem.......dga report attached

DGA TEST REPORT

S.N.

Tx. NAME

Tx. Make

MVA

S.No.

GAS CONTENT IN PPM

REMARKS

DATE

CO

CH4

CO2

C2H2

C2H4

C2H6

H2

H2O

400-900

35-130

5300-12000

15-50

110-250

50-70

60-150

1

U # 3 UT.

CGL20MT 7324/0205.09.2015

175

229

1824

8.5

536

201

<5

35

Register to Reply
Pathfinder Tags: transformer problem
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
5
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: 20 MVA Transformer Problem.

09/09/2015 5:42 AM

You have a number of problems:

1) A severe overheating problem, as indicated by high Ethylene and Ethylene/Ethane ratio, with heating to near 700ºC,

2) Local overheating (hotspot) as indicated by high Ethane levels nearly 5.75 times normal,

3) A sparking problem as indicated by Methane nearly 3 times normal.

It's time for someone with an understanding of DGA to help you further understand how to interpret the numbers, or you can learn about it from the competent engineers that you need to contract with to do a complete internal inspection of the transformer.

My guess is that the excitation system was put in service long before the unit reached 95% of rated speed or was allowed to coast down without tripping the excitation system, and the unit was subjected to high Volts/Hertz and overexcitation resulting in core and insulation damage. Now pay someone to assess the damage.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 5)
Power-User

Join Date: Sep 2015
Posts: 482
#2
In reply to #1

Re: 20 MVA Transformer Problem.

09/09/2015 8:49 AM

GA

__________________
The doctor said "just one post or reply aday in CR4, take it or leave it". I said, "what does that mean?"
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: 20 MVA Transformer Problem.

09/09/2015 4:31 PM

ANSI/IEEE Std C57.104 [1] provides guidance on concentration limits of the key gases:

Dissolved gas concentration limit (ppm)Interpretation
Hydrogen (H

2)

Methane (CH

4)

Acetylene (C

2H2)

Ethylene (C

2H4)

Ethane (C

2H6)

Carbon monoxide (CO)Carbon dioxide (CO

2)

TDCG (*)
100120150653502500720Satisfactory
101 - 700121 - 4002 - 951 - 10066 - 100351 - 5702500 - 4000721 - 1920Fault may be present
701 - 1800401 - 100010 - 35101 - 200101 - 150571 - 14004001 - 100001921 - 4630Fault probably present
>1800>1000>35>200>150>1400>10000>4630Continued operation could result in failure

(*) TDCG = Total dissolved combustible gas

http://www.openelectrical.org/wiki/index.php?title=DGA_Testing

http://tdworld.com/archive/power-transformers-rebuilt-field-site-repairs-110-kv-distribution-transformers-and-220-400-k

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: 20 MVA Transformer Problem.

09/10/2015 5:31 PM

The problem is an unwillingness to discuss the technicalities directly with the transformer manufacturer using the telephone. The solution is simple. Get dialling.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".