current unbalance in same motor

07/21/2007 1:40 AM

hi,

I`m in delima
what is exact reason for current unbalancing in same motor in different phases
some times in R Phase,some time in Y Phase & some time in B phase,
& winding resistane & inductance are also balance.Mostly in Mill motor.

a) R=112 A
Y=118 A
B=142 A
R=148 A
y=117 A
b=120 A

c) R=122 A
Y=124 A
b=152 A
all these are in sam,e motor ...why it happens?l

Regards,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#1

Re: current unbalance in same motor

07/21/2007 3:30 AM

If it's not in the motor you're looking at, it's somewhere else.

That's all I can say.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#2

Re: current unbalance in same motor

07/21/2007 6:53 AM

Please check up the In coming Supply Voltage in each Phase and see that your Power supply is balanced.There may be single Phase load in your system

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#3

Re: current unbalance in same motor

07/21/2007 12:19 PM

Unbalanced voltage results in unbalanced current.Some time incoming supply itself will have this problem .

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Associate

Join Date: Jul 2007
Posts: 41
#4

Re: current unbalance in same motor

07/22/2007 8:44 AM

I would say the previous comments are on the right track incoming lines to motor.

1. Starter contacts

2 voltage to starter over time each phase

3 voltage at motor over time each phase

If these values stay constant there is a remote possibility (remote) winding insulation instability.(but all three phases?)

Is the incoming feed suppy on with a variable frequency drive somewhere down the line if so multiple harmonic disturbances could manifest itself as a changing phase voltage differential you are experiencing . 16%??

Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#5

Re: current unbalance in same motor

07/22/2007 4:23 PM

Also look at DC resistance of motor windings. Sounds a little like you may have a phase which may have over-heated and starting to short some windings. Phase voltages will affect phase currents also as others have said (backwards, in one case).

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Active Contributor
India - Member - New Member

Join Date: May 2007
Location: India - (Home town - Tamil nadu, Working - Jemshedpur)
Posts: 12
Good Answers: 1
#6

Re: current unbalance in same motor

07/23/2007 4:56 AM

If 3 phase motor:

- Check coil resistance. It should be balanced for 3 coils.

- Check insulation resistance (disconnecting star / delta links) seperatly for 3 coils with respect to earth. It shouls be infinity or >20 MOHMS equal for all coils.

- Check all switch gears (contact gaps (if required filler gauge) connected series to motor. There should be no gap in power contactor contacts or in other switch gears.

- Check for any loose connections in terminal connections or thimble crimpings. There should be no loose connections.

Note: If all above said things are ok only problem is in supply voltage. That means supply voltage is imbalanced.

Regards,

Vinod.P

__________________
Regards, Vinod.P, Engineering Deptt, LAFARGE , India
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2012
Posts: 14
#15
In reply to #6

Re: current unbalance in same motor

01/30/2012 10:23 AM

sir,

What should i do,If a total MCC gets imbalance current in one phase. We have checked out the load current at PCC it was normal.but one thing i found out is the system is unbalanced ie:In=80A. Is there any permissible limit for this Neutral current.Please do reply me.

Register to Reply
Commentator

Join Date: Feb 2007
Posts: 60
#7

Re: current unbalance in same motor

07/23/2007 8:16 AM

Dear friend

A good idea would be to calculate the sequence components of the currents for each of the three different values.

Perhaps you reach to the conclusion that the unbalance will be dependant in which phases it occurs.

I think it is a path you may follow.

Regards

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#8

Re: current unbalance in same motor

07/25/2007 1:06 AM

Tadagids--

I would expect that equipment problems, such as contact resistance or winding faults would be unlikely to be in different phases at different times. The earlier posts are all correct that an unbalanced voltage to the motor will cause an unbalanced current. In the USA, the standard motor designs have predictable characteristics, which are in graphs in the NEMA (National Electrical Manufacturers' Association) handbooks. I don't have one in front of me right now, but a voltage imbalance usually causes a much larger current imbalance. The real problem is that an imbalanced current between the phases causes circulating magnetic eddy currents in the steel laminations, which leads to overheating of the windings and motor failure. I had a large blower motor in an industrial setting, which had about a 4 or 5% voltage imbalance, but a 15 to 20% current imbalance. Although every phase current had been within the nameplate rating for the motor, it burned out.

Check your voltage, phase to phase as well as phase to ground (if it is on a 4-wire wye system). Write each one down. Find the average of the three voltages, and then calculate the % each one is away from the average. If your plant receives its power from someone else, talk with them and explain your problem. They may be causing problems for many people.

In my example above, when I called the electrical utility (late in the afternoon), they called more and more electrical linemen out until they finally found a bad splice in their high-voltage distribution system about 2 km away from our plant.

-JMM

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9
In reply to #8

Re: current unbalance in same motor

07/25/2007 1:26 AM

That's right. You need to understand that the current imbalance percentage is logarithmically proportional to the voltage imbalance. A 1% voltage imbalance can easilly show up as a 3% current imbalance, but that 4% V creating a 20% I is to be expected as well.

So if your supply voltage balancing changes during the work day, you can expect a current imbalance to be seen in your motor. This is especially prevalent in summer months where you might have a lot of 1 phase Air Conditioners coming on and off randomly during the peak hours. There is no way for the utility to predict and compensate for the load swings, so the voltage gets unbalanced.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#10

Re: current unbalance in same motor

07/25/2007 4:16 AM

This is my dilemma. You gave these three statements:

what is exact reason for current unbalancing in same motor

all these are in sam,e motor

Mostly in Mill motor.

The first and second statement says that it happens only to one motor. The third statement seems to say that it also happens to other motors but, most of the time, it happens in the Mill motor. Which is it? Does it happen only to one motor? Or does it happen to other motors as well? How you troubleshoot will depend on your answer.

If it happens only to one motor, then I'd check the motor itself, the cables, the contactor, breaker, terminal blocks, or anything else that is associated only with that motor. A problem with your utility provider will not result in only one motor acting this way.

If it happens with other motors, then you have a bigger problem. You'll have to search in the feeders, maybe the substation or, as someone said, you'll have to check with your electrical utility.

I just wanted to point out that accurate statements will go a long way in diagnosing the problem.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Anonymous Poster
#11
In reply to #10

Re: current unbalance in same motor

07/25/2007 5:55 AM

Friend,

It`s true such incident happens in our 8 Nos. Mill Motor which are located in different location & supply source is different load center.

Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#12
In reply to #11

Re: current unbalance in same motor

07/25/2007 9:02 AM

I feel the load pofile to be checked. In mill , loads are not uniform, which may result in current unbalance.

__________________
BNDas
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#13

Re: current unbalance in same motor

07/27/2007 4:02 AM

On distribution boards fed from 3-phase supplies, it is not unknown for a site electrician to add new single phase loads starting from the top left. As the red phase is usually at the top of a board, that phase tends to see the greatest current and consequently the lowest voltage. If a 3-phase motor is connected elsewhere, then these single phase loads will produce a difference in currents and voltages at the motor.

If the motor is under its full-load-current and its correctly-set overload is still holding in, then normally there isn't a problem. If there is a persistent problem, then one needs to look again at motor sizing, spreading the single phase loads across the other phases instead, and techniques to reduce loads like low-energy lighting and power factor correction. It's all part of the bread-and-butter of the site Electrical Engineer.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#14
In reply to #13

Re: current unbalance in same motor

07/29/2007 5:42 PM

Good Moaning in return, Crabtree--

I disagree with your saying "If the motor is under its full-load-current and its correctly-set overload is still holding in, then normally there isn't a problem."

If the current is sufficiently unbalanced, such as by a voltage imbalance of 3% or more, the increased magnetic fields in the steel laminations can easily overheat the windings, even when the currents are all below name plate values. This will cause insulation failure just as easily as overloading will. Most motor starters are supplied with Class-20 overload relays, which will respond only seldom to this sort of a problem. Motor starters with IEC type Class-10 overload relays frequently will respond to the current imbalance, but this is not always assured. Starters with closely sized fuses for running overcurrent protection will do no better than Class-20 overload relays.

However, there have been many (usually older) motors which were rated very conservatively on their nameplate, so imbalances such as have been described were fairly easily handled.

As I read "between the lines" of the original post and the later additions to it, I suspect that this application is in an area with a poorly or inadequately engineered power distribution system, and possibly also has few (or no) code compliance requirements.

--JMM

Register to Reply
Register to Reply 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Bill (1); biswanath.das (1); Crabtree (1); elbf2801 (1); jmueller (2); JRaef (1); martin-electrical (1); nesubra (1); sathish-47 (1); V.I.Abraham (1); Vulcan (2); winotp (1)

Previous in Forum: Motor Efficiencies   Next in Forum: Control cable

Advertisement