Selecting Cable Size for 2MVA Transformer

09/22/2015 1:49 AM

I need to find the cable sizes for33kV/415V 2MVA Transformer. the current in Hv side is around 35A and the LV side is around 2800A. How I find the cables for both sides? If I select 1 Core cable for LV Side what will be the size of the same? If I select 3 Core cable for HV Side what will be the size of the same?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Selecting Cable size for 2MVA Transformer

09/22/2015 2:20 AM

Pursuant to your last request for homework help, this request will also be ignored.

Do your own homework.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#2

Re: Selecting Cable size for 2MVA Transformer

09/22/2015 4:55 AM

Dear Mr.chandimas,

Is it Generator Transformer or Distribution Transformer.? This point has a definite impact.

Regarding cable selection, you should not use single core cable, sincne it will get heated due to inductance. Therefore you have to use Three and Half core cable.

The LV sisde current for a PF of 0.8 lag and 415 Volts is 3478.01 Amps, where as you have referred the LV side current is 2800 Amps which indicates the P.F is higher than 0.8. and work out to 0.993, which is higher for design aspect. You have to design the cable sizing for a PF of 0.8 lag.

Take a value for current density as 0..625 Amps (for Elec.Grade Aluminium) as absolute value and multiply this 0.625 by the De-Rating factor for the cable which depends upon 5 parameters, like above the ground, under ground, Temp.Rise with in the conductor etc., etc. Devide the LV current by the corrected current density and adopt the nearest higher size. This may work out to 0.5 Amps per Sq.MM.

Hence Cable Area Required = (3478.01)/(0.5) = 6956.02 Sq.MM rounded to 7000 Sq.MM.

Considring 150 MM width and 10 MM thick Aluminium Bus Bar, youthe required Bus Bar will be (7000)/ (!50 x10) = 4.666 Bars, and the nearest higher quantity is 5 nos. and for Neutral it will be 150 x 10 3 nos. of Bus Bar to be used.

Hence you have to use 150 x 10 x 5 nos. Bus bar for each phase and 150 x 10 x 3 nos for neutral (or ) 7 nos. of 1000 Sq. MM Three and Half Core cable which ever way you want you can select.

DHAYANANDHAN.S

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Selecting Cable size for 2MVA Transformer

09/22/2015 8:08 AM

What does your local codes say about below ground cabling installed next to an active volcano?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Selecting Cable Size for 2MVA Transformer

09/22/2015 9:54 AM

I don't like to repeat myself, but in this case I propose to open the post of 09/10/2015 Cable Problem and read my notes about how to chose a correct cable.

About if to chose three_core or single_core cable it will be another problem.

In Europe for instance three_core cables are usually employed.

In spite of the currents unbalance in parallel cables is higher, the voltage building-up and the circulating shield current-if the shield is grounded both ends I'd prefer single_core cables instead of three-core cables.

The cable will be light weight and more flexible, the heat evacuation is better then the current density is higher [less number of cables per phase].It is my opinion.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5
In reply to #4

Re: Selecting Cable Size for 2MVA Transformer

09/22/2015 10:09 AM

However, since you don't need parallel cables a 3 phases of 33/19 kV - if under fault conditions, the system would operated for a short time [1 hour or less] with one phase earthed- will be o.k. I think.

__________________
Julius
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#6

Re: Selecting Cable Size for 2MVA Transformer

09/22/2015 6:24 PM

You've got to be kidding (Joking)!!! Hopefully only you will be introduced to Dr. Darwin and win the top 5 Star Award and not kill anyone else or take down the National Grid!!

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #6

Re: Selecting Cable Size for 2MVA Transformer

09/22/2015 6:36 PM

If I am right in my suspicions, and there is any justice, chandimas10 is still a struggling student.↓

Transformer Data Sheet for Design of an Auxiliary System for a Coal Power Plant

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#8
In reply to #7

Re: Selecting Cable Size for 2MVA Transformer

09/22/2015 9:33 PM

Cheaters get more rewards today than they ever did. Why fight it. They will have a better chance building a toaster from scratch than they ever will understanding why the answer is 42.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #8

Re: Selecting Cable Size for 2MVA Transformer

09/22/2015 9:53 PM

I am rapidly losing all hope for our youth.

I have never seen so many brats who feel entitled to a free ride through life as today.

We are partly to blame because we want them to "have a better life" than we did.

Unfortunately, today that means that the kids go to school till they get kicked out, then live with their parents until the parents die, then live in the house that mom and dad worked all their lives for, until it's foreclosed for lack of paying the bills.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#10
In reply to #9

Re: Selecting Cable Size for 2MVA Transformer

09/23/2015 3:05 AM

I am- sorrowfully- agree with you. However, the young fellows are not guilty, in my opinion. The reward for long training and study is very low and continuously decreases.

__________________
Julius
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#11

Re: Selecting Cable Size for 2MVA Transformer

09/23/2015 4:47 AM

I think will be better to use a metal-enclosed substation-switchgear connected with transformer- and use busbars in order to supply and distribute the currents.

If the switchgear is located far from the transformer in an underground run-for instance- you should have to employ 21 parallel cables of 3*300 mm^2 copper/xlpe in pvc ducts .

See-for instance:

https://library.e.abb.com/public/86ce3b71c32e5e01c1257417004c3d3c/Kline%20Switchgear%20TB%203.1.2-1B.pdf

__________________
Julius
Register to Reply
Active Contributor

Join Date: Jul 2015
Posts: 23
#12

Re: Selecting Cable Size for 2MVA Transformer

09/23/2015 7:44 AM

Julius, was wondering whether there are some certain criteria or points to judge the the preference or necessity of busways to cables. I do know that busways are more expensive.

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#13

Re: Selecting Cable Size for 2MVA Transformer

09/23/2015 11:08 AM

It is wrong for anybody to supply the kid with answers !! He is in over his head and going to kill people! Screw the equipment and himself being destroyed, it people I'm worried about

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#14

Re: Selecting Cable Size for 2MVA Transformer

09/23/2015 6:34 PM

Consult the applicable electrical code for your site for the correct information.

In the USA the needed information will be in the NEC/NFPA tables.

Not sure about other critical details of the installation however ambient mean temperature, moisture, length, and duty cycle should be factored in.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#15

Re: Selecting Cable Size for 2MVA Transformer

10/09/2015 4:41 AM

Better let your electrical consultants to do all the calculation and sizing for the cables needed for the 33KV side. Don't take the risk getting some one killed with 33KV voltage.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Register to Reply 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (4); dhayanandhan (1); dj95401 (2); lyn (3); Mark1234567 (1); redfred (2); SHOCKHISCAN (1); Simon Wan (1)

Previous in Forum: CT Burst in 110 KV Switch Yard   Next in Forum: Motor Myths

Advertisement