Root Cause Analysis - Transformer

09/29/2015 4:26 PM

These dark spots in the windings could be related to what kind of problem?

Register to Reply
Pathfinder Tags: root cause analysis transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#1

Re: Root cause analysis - Transformer

09/29/2015 4:44 PM

There are a few typical issues that pop up in transformers:

  • Heat?
  • Overheat?
  • Insulation degradation?
  • Overload?
  • poor manufacturing practices?

In my opinion it looks like a heat or overheat issue?

There are other guys that will comment and they are very good transformer technicians!

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Sep 2015
Posts: 10
Good Answers: 1
#12
In reply to #1

Re: Root cause analysis - Transformer

09/29/2015 9:23 PM

Thanks for the reply! Tomorrow I will post additional information about the transformer.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#18
In reply to #12

Re: Root cause analysis - Transformer

09/30/2015 5:14 AM

Next time you post, consider holding back until you have all the information relevant to the problem, Mildred. You'll get better answers more quickly.

__________________
Good moaning!
Register to Reply
Active Contributor

Join Date: Sep 2015
Posts: 10
Good Answers: 1
#19
In reply to #18

Re: Root cause analysis - Transformer

09/30/2015 7:18 AM

OK!

Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#2

Re: Root cause analysis - Transformer

09/29/2015 4:47 PM

Has it failed? If so, what is the nature of the failure?

__________________
CRTL-Z
Register to Reply
Active Contributor

Join Date: Sep 2015
Posts: 10
Good Answers: 1
#13
In reply to #2

Re: Root cause analysis - Transformer

09/29/2015 9:27 PM

Thanks for the reply! Tomorrow I will post additional information about the transformer.

Register to Reply
4
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Root cause analysis - Transformer

09/29/2015 5:18 PM

So you untanked a transformer and have left it standing in the middle of the factory floor unprotected and now you want to know what happened to it?

What did the DGA (Dissolved Gas Analysis) show immediately before and after the fault?

How long was the transformer in service?

What protective relaying operated?

What type of fault occurred?

Where was it located?

Was any switching going on prefault?

What does the TDR (Transient Data Recorder) show?

The rest of the transformer looks relatively clean, was this the first time it was energized?

If it had been operating for awhile, how long and under what type of loading?

What were the ambient conditions?

What did the post fault tests show?

What was the BDV (Break Down Voltage) of the oil, pre- and post-fault?

What does the oil condition tests show?

NB- all of the above questions should have been answered BEFORE the unit was untanked!!

Now you have an untanked transformer absorbing moisture from the factory ambient, and it shows discolored, darkened bands of insulation predominately (and curiously) on the lower half of all three phases of the outer windings.

Is this a three winding transformer?

Has anybody visually checked the cooling passages for blockages?

What is the condition of the inner windings?

Have the outer coils been removed?

What is the condition of the laminations and support materials?

Has any tracking been noted?

Are the connections discolored or loose?

Was there any residue in the bottom of the tank?

What was the quantity of oil in the tank?

Were the coils completely covered?

What was the Top Oil (Hot Spot) temperature reading?

Did the Bucholz, SPR (Sudden Pressure Relay), and/or any Overpressure devices operate?

Are you the owner, manufacturer, or installer of the transformer?

...And you expect the answer to your one question, without providing the answers to my Twenty Five??!!

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 4)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #3

Re: Root cause analysis - Transformer

09/29/2015 6:57 PM

As the question monitor for the month of September, it is my duty to inform you that you have exceeded your allotment of questions for the month.

You have been added to the list of those who are guilty of overindulgence in interrogation.

You will be on probation for the next 23 minutes.

Similar offenses will be dealt with harshly and may include the deduction of one Atta-boy.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7
In reply to #6

Re: Root cause analysis - Transformer

09/29/2015 7:12 PM

But your Honor, I was just trying to get to the root cause of the problem, namely the OP's reliance that one picture is worth a thousand words!!

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8
In reply to #7

Re: Root cause analysis - Transformer

09/29/2015 7:15 PM

I'll take that under advisement and render my decision in 19 minutes.

Register to Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#41
In reply to #6

Re: Root cause analysis - Transformer

10/06/2015 10:38 PM

You are just angry you didn't think to ask those questions.

Register to Reply
4
Active Contributor

Join Date: Sep 2015
Posts: 10
Good Answers: 1
#11
In reply to #3

Re: Root cause analysis - Transformer

09/29/2015 9:15 PM

Thanks for the answer! (and I apologize for my bad english)

I am an electrical engineer and work for the insurer of the transformer owner.

I asked the transformer owns most of its questions, but they did not answer me ... This happens a lot in my work (limited information to conduct failure analysis).

I will indicate the answers that I have (not many ...) and, in the end, I will redo the main question:

1) What did the DGA (Dissolved Gas Analysis) show immediately before and after the fault?The owner of the transformer sent the last two DGAs before the event. Tomorrow I will show to you (I'm home now and this information is in my work ). But I inform you that there was an indication of overheated operation.
-

2) How long was the transformer in service?

The transformer was manufactured in 1998. I have no information when it came into operation.
-

3) What protective relaying operated?

The owner of the transformer did not sent me this information.
-

4) What type of fault occurred?

An arc of high energy in the X1 terminal region. Tomorrow I will show more pictures of the transformer.

-

5) Where was it located?

See answer 4.
-

6) Was any switching going on prefault?

The owner of the transformer did not sent me this information.
-

7) What does the TDR (Transient Data Recorder) show?

The owner of the transformer did not sent me this information.
-

8) The rest of the transformer looks Relatively clean, was this the first team it was energized?

No. I suppose he has come into operation around 1998.
-

9) If it had Been operating for awhile, how long and under what type of loading?

The owner of the transformer did not report on the load history.
-

10) What Were the ambient conditions?

I do not have that information.
-

11) What did the post fault tests show?

The result of TTR was presented. It resulted in error more than 0.5% in the winding 1.

-

12) What was the BDV (Break Down Voltage) of the oil, pre- and post-fault?

Only the pre-fault was sent. Tomorrow I will show to you.

-

13) What does the oil condition tests show?

Tomorrow I will present this answer.
-

NB - all of the above questions shouldnt Have Been answered BEFORE the unit was untanked !!(I requested information before the opening of the transformer, but I only received those answers after the transformer has been repaired ...)

Now you have an untanked transformer absorbing moisture from the factory ambient, and it shows discolored, darkened bands of insulation predominately (and curiously) on the lower half of all three phases of the outer windings.(I'm also intrigued by the fact that darkened marks are in the lower half of the windings THREE! I suppose these marks are related to the overheated operation, unrelated to the arc in the terminal region X1)

14) Is this a three winding transformer?

Yes.
-

15) Has anybody visually checked the cooling passages for blockages?

It was not inspected.
-

16) What is the condition of the inner windings?

Despite the repair has already been completed, I no had access to the conditions of internal coils.
-

17) Have the outer coils Been removed?

See answer 16.
-

18) What is the condition of the laminations and support materials?

It was not inspected.
-

19) Has Been Noted any tracking?

No.
-

20) Are the connections loose or discolored?

I did not understand the question .

-

21) Was there any residue in the bottom of the tank?

It was not inspected.
-

22) What was the quantity of oil in the tank?

I suppose that by the time of the event, the coils were completely covered by oil.
-

23) Were the coils completely covered?

See answer 22.
-

24) What was the Top Oil (Hot Spot) temperature reading?

I do not have that information.
-

25) Did the Bucholz, SPR (Sudden Pressure Relay), and / or any Overpressure devices operate?

Despite the transformer owner did not send the record of the protections that operated, I suppose, at least, has been the operation of the SPR.
-

26) Are you the owner, manufacturer, or installer of the transformer?

Response at the beginning of the text.
-

NEW QUESTION is:
Based on the above, I wonder if my assumption is correct that the dark markings are related to the overheated operation, unrelated to the occurrence of electric arc on the X1 terminal region.
Suppose has been a rapid event not associated with external causes (external short circuits, for example), so that the time involved in the event can not result in thermal effects (subtransient period).
With that, I would intend to aggravate the depreciation of equipment, based on the conservation status before the event.

Register to Reply Good Answer (Score 4)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#14
In reply to #11

Re: Root cause analysis - Transformer

09/29/2015 9:28 PM

Thanks for the good answer.

Looking forward to more details.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#15
In reply to #11

Re: Root cause analysis - Transformer

09/29/2015 10:50 PM

I love the way this thread has progressed.

Since you work for the insurer of the company that roasted this transformer, you might want to review your company rules on how much the insured must comply with an investigation for full payment.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Active Contributor

Join Date: Sep 2015
Posts: 10
Good Answers: 1
#20
In reply to #15

Re: Root cause analysis - Transformer

09/30/2015 7:40 AM

Thank you! Next time I will put all the information on the main question.

Actually I work in an engineering firm that provides services to many insurers. In theory, the insured should provide all the information, but it hardly occurs (Brazil's problems, you know...).

And if there is delay in research (due to information request, for example), our office ends up being blamed. So in most cases, have to do the analysis with limited information, you know? ...

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#17
In reply to #11

Re: Root cause analysis - Transformer

09/30/2015 12:45 AM

Excellent reply..

It does warm you heart to get a reply to questions..

My take on your post is this and I conduct in my line of work something called DIFA, Dismantle, Inspection and Failure Analysis.

The questions you have answered either "Not checked", "Not inspected", "Not been told", "Not received information"... etc, are the questions you need to GET answers for.

It might help if you talk to the senior management and explain the following;

1. the omission of information required, and give them a list of info you NEED NOW, will only lead you to make your own conclusions, and you MIGHT not rule in their favour (I guess they are trying to claim?)

2. You need to be able to inspect anything and everything you want to and items so stated in replies to you.

3. You are there to ensure that things are done in a proper manner

4. You are there to help them and NOT work against them. (most important)

For me.. any information requested and then hidden or not provided is an admission of guilt and/or bad practice.

The load history is vitally important, as a transformer does not overload itself!! Also the trip settings, as previously stated by other contributors to your OP

They are trying to claim, you, I guess have to authority to reject the claim. You have to ensure they understand that, as a lack of information from them does not allow you to make an educated decision.

__________________
The square root of nothing is what you make it!
Register to Reply
Active Contributor

Join Date: Sep 2015
Posts: 10
Good Answers: 1
#22
In reply to #17

Re: Root cause analysis - Transformer

09/30/2015 7:54 AM

Thank you!

I fully agree with what you said. Usually we try to conduct a good inspection (following the recommendations of IEEE C57.125-1991) and request the documents beforehand, but some insured do not collaborate in any way ... And unfortunately, as I do not work in the insurance (I am only a service provider), I have no authority to reject the claim.

Nevertheless, soon I'll post more information on this case and you will understand what is my real question.
See you later!

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#24
In reply to #22

Re: Root cause analysis - Transformer

09/30/2015 9:19 AM

You do not directly control the insurance claim money, but you do control your report. It is normal for any report to include appropriate comments on the ease or difficulty to obtain information on an incident.

As for the conditions on the day of the failure, you should be able to at least identify the weather conditions from archived news reports.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#33
In reply to #11

Re: Root cause analysis - Transformer

09/30/2015 3:04 PM

Thank you for such a detailed and concise reply.

Very refreshing when a typical poster asks a question and then disappears!

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#34
In reply to #33

Re: Root cause analysis - Transformer

09/30/2015 4:06 PM

Certainly not OT!

Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#36
In reply to #34

Re: Root cause analysis - Transformer

09/30/2015 8:11 PM

I second that.

Register to Reply Off Topic (Score 4)
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#4

Re: Root Cause Analysis - Transformer

09/29/2015 6:32 PM

I would add:

Insulation aging/degradation.

Possible arcing sites.

Normal discoloration of the winding insulation is a remote possibility.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5
In reply to #4

Re: Root Cause Analysis - Transformer

09/29/2015 6:55 PM

The location and type of damage is fairly obvious, but I'm waiting for answers and more pictures before making any assumptions as to the probable cause. Only the OP can provide those previously requested details, plus those which require a close internal inspection, so everything is pure conjecture until then.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#28
In reply to #5

Re: Root Cause Analysis - Transformer

09/30/2015 10:18 AM

Yes I agree. Hopefully they will send it out to a competent repair shop for analysis to determine what is taking place.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#9

Re: Root Cause Analysis - Transformer

09/29/2015 7:39 PM
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#10

Re: Root Cause Analysis - Transformer

09/29/2015 8:06 PM

Heat.

That is the root cause.

HEAT!!!!!!!!!!

Heat causes the organic coatings to revert back to their original constituents. (Elements/molecules/atoms)

Carbon is one. Carbon is black.

Toast looks black when it is burned.

Your transformer is TOAST.

Find out what burned it!

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#35
In reply to #10

Re: Root Cause Analysis - Transformer

09/30/2015 6:30 PM

Hey! You're on to something! Maybe the reason the OP isn't replying is because he/she/it is "toasted"!

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Aug 2012
Location: Land of Fruits and Nuts
Posts: 4481
Good Answers: 54
#16

Re: Root Cause Analysis - Transformer

09/29/2015 11:56 PM

Years ago, I worked for the DOD and I've seen this before. Definitely was overheated. To much current, but why?

Definitely need more information.

__________________
Enjoy and be happy! Life is too short!
Register to Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Oct 2013
Location: Texas.Baytown
Posts: 697
Good Answers: 26
#21

Re: Root Cause Analysis - Transformer

09/30/2015 7:50 AM

Heat.

__________________
If you want to know how well a broom works you do not ask the guy selling the broom or the guy who designed the broom, you ask the guy using the broom.
Register to Reply
Active Contributor

Join Date: Sep 2015
Posts: 10
Good Answers: 1
#23

Re: Root Cause Analysis - Transformer

09/30/2015 8:43 AM

Hello guys!
I'll put some more information and photos about this case:
It is a transformer 7.5 / 9,375 MVA, 13.8 / 34.5 kV. The event ocurred on 06/10/2015. I have NO information about the circumstantial conditions, record of the protections that operated, voltage, current and load.
Following the RAMConsult questions:
1) What did the DGA (Dissolved Gas Analysis) show immediately before and after the fault?

The diagnosis made based on the NBR 7274 (Brazilian standard based on IEC 599) indicates overheating (T> 700 ° C) for the sample of 07/17/14 (the last DGA).
--

4) What type of fault occurred?

An arc of high energy in the X1 terminal region.




--
12) What was the BDV (Break Down Voltage) of the oil, pre- and post-fault?

Break Down Voltage in the last sample: 70,9 (min 30).
--

14) Is this a three winding transformer?

Yes.


--
NEW QUESTION is:Based on the above, I wonder if my assumption is correct that the dark markings are related to the overheated operation (indicated by DGA), unrelated to the occurrence of electric arc on the X1 terminal region.Suppose has been a rapid event not associated with external causes (external short circuits, for example), so that the time involved in the event can not result in thermal effects (subtransient period).
With that, I would intend to aggravate the depreciation of equipment, based on the conservation status before the event.

Register to Reply
Power-User

Join Date: Sep 2015
Posts: 482
#25
In reply to #23

Re: Root Cause Analysis - Transformer

09/30/2015 9:35 AM

Discoloration was on bottom part of the thing. Could be a collateral damage both from heat and chemical reaction, perhaps.

__________________
The doctor said "just one post or reply aday in CR4, take it or leave it". I said, "what does that mean?"
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#31
In reply to #23

Re: Root Cause Analysis - Transformer

09/30/2015 2:04 PM

If the event happened on 6/10/2015, why is one of the images dated 4/29/2015 ?

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Active Contributor

Join Date: Sep 2015
Posts: 10
Good Answers: 1
#32
In reply to #31

Re: Root Cause Analysis - Transformer

09/30/2015 2:22 PM

Sorry... The event happened on 01/21/2015.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#37
In reply to #23

Re: Root Cause Analysis - Transformer

10/01/2015 10:33 AM

From the information you have provided it is apparent that the transformer suffered overheating over an extended period of time resulting in subsequent insulation damage and eventual failure.

Without a baseline accurate determination of the root-cause(s) is not going to be easy.

The cause of overheating must be identified if future transformer failure is to be avoided.

Here are some suggestions of things to consider:

Is the transformer large enough to handle the applied load without suffering from overheating? (Often over a period of time additional small unplanned and undocumented electrical loads get attached to a transformer which eventually overtax the unit and cause failure.)

Are all transformer cooling apparatus and system flow paths operating properly? (Fans & thermostat(s) operational and set correctly? Cooling media of the correct type, and clean? Are the radiators clear of obstruction and correctly oriented? )

Has the transformer oil been properly and consistently maintained for the life of the unit? (PM interval? Oil filtered regularly on a consistent interval? Oil tested and recorded/documented on a regular consistent interval?)

Is the available power supply to the transformer within OEM specifications? (Voltage stable and within min-max limits? Is the system frequency within specs?)

Is there a high number of VFD or other frequency manipulating devices present in the system? (If so, Has the system been tested to identify any/all harmful harmonics?)

Abnormally high voltage spikes can definitely cause this type of transformer failure.

How old is the unit? (It could well be at the end of life.)

Hope this helps.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
2
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#39
In reply to #23

Re: Root Cause Analysis - Transformer

10/01/2015 11:17 AM

There was already a fairly high level of carbon monoxide (CO) in the pre-fault sample, and much higher post-fault. CO is usually a sign of general overheating (overloading), which breaks down the paper insulation. If that wasn't the root cause of the failure, it certainly would contribute to it.

The level of Ethylene (C2H4) was also fairly high. Ethylene takes quite a bit of energy to cause it to form, so it suggests a localized, very hot spot such as a loose connection, poor weld/braze joint, etc. That may be the actual item that initiated the fault, with deteriorating insulation due to overheating making it possible. There was no acetylene (C2H2), so there was not any significant arcing that took place under the oil.

I hope that helps.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jul 2012
Location: Madison, WI.
Posts: 2074
Good Answers: 77
#26

Re: Root Cause Analysis - Transformer

09/30/2015 9:39 AM

Root Cause?

Having to ask an anonymous internet forum for the answer?

__________________
Knowing is the end result of learning, not believing.
Register to Reply
Active Contributor

Join Date: Sep 2015
Posts: 10
Good Answers: 1
#27
In reply to #26

Re: Root Cause Analysis - Transformer

09/30/2015 9:46 AM

I exaggerate when I wrote that I would like to know the root cause ...
Actually what I'd like to know is whether you agree with my assertion that the dark markings are related to the overheated operation (indicated by DGA - see #23), unrelated to the occurrence of electric arc on the X1 terminal region (see #23).
Suppose has been a rapid event, not associated with external causes (external short circuits, for example), so that the time involved in the event can not result in thermal effects (subtransient period).

Register to Reply
Power-User

Join Date: Sep 2015
Posts: 482
#29
In reply to #27

Re: Root Cause Analysis - Transformer

09/30/2015 10:33 AM

I could not imagine an electric arc in there. I presumed, when an arc happen, it will consequently burn the surrounding insulation instantly bigger and bigger. It will not reach the point of discoloration, infact, it will result to something more catastrophic than those, I think.

__________________
The doctor said "just one post or reply aday in CR4, take it or leave it". I said, "what does that mean?"
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#30
In reply to #27

Re: Root Cause Analysis - Transformer

09/30/2015 10:41 AM

Unless the oil is actively pumped to cause hot oil to exit to out of the bottom of the transformer case, wouldn't the hottest part of the transformer be at the top? I am assuming uniform heating (no shorts) of the transformer. I suspect the dark but not charred regions at the bottom of the images should be there on a cool transformer. The site of the arc agrees with this observation.

I recommend you contact the builder of this transformer and ask for an undamaged image for comparison.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#38

Re: Root Cause Analysis - Transformer

10/01/2015 10:35 AM

In my opinion the transformer has to be ONAF and was loaded at 9 MVA without ventilation.

The oil was overheated and the lower half of the winding paper was impregnated with oil soot.

Comparing the test results from 2013 with 2014 it seems to me that in the last operation year the oil was degraded by heat.

However, I am not positive this is the cause of short-circuit on phase 3.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#40

Re: Root Cause Analysis - Transformer

10/03/2015 5:09 AM

"An arc of high energy in the X1 terminal region" said ronaldosalles.

Since 13.8 kV windings are Delta connected there is no grounding connection on low voltage side. That means the exterior equipment or cable was grounded somewhere too.

It could be the grounded part of X1 it is an "old fault" from fabrication or mounting process and was not detected by protection system in time.

__________________
Julius
Register to Reply
Register to Reply 41 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); Autobroker (1); Brave Sir Robin (1); brich (1); Crabtree (1); Fredski (1); Legolaz (2); lyn (5); Munster (1); Original_Macgyver (2); PeterT (1); RAMConsult (3); rashavarek (1); redfred (3); ronaldosalles (9); SHOCKHISCAN (4); texasron (1); Unredundant (1); WJMFIRE (1)

Previous in Forum: DC Voltage for Safe Batteries Banks   Next in Forum: Transformer and Generator Running in Parallel

Advertisement