Manual Accuracy Testing of Watthour Meters

10/03/2015 1:05 PM

Hi and good day to you Sirs / Ma'am.

I am a young engineer from Asia, currently i am working with meter testing.

We all know that with meter testing we need a reference standard with a comparator for an automated testing, but in cases where in comparators does not exist how can i test such meters? And of course testing with such method (manual) will result inaccuracy however for the sake of learning is how can i conduct a test with just a reference standard my basis will be KWh obtained from the reference standard. and can you recommend a good number of revolutions that i can use for the basis of my manual testing? As of now i am familiar with just the parts like phantom load, comparator and reference standard. I want to pursue a career with metering and i want to put my knowledge with regards to this field to the next level. I can take professional criticism for the sake of learning.

Thank you so much and pardon me if i am a bit naive with regards to my question.

Register to Reply
Pathfinder Tags: Watt hour meter tesing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Manual accuracy testing of watthour meters

10/03/2015 2:22 PM

Maybe this will guide you.....

http://www.usbr.gov/power/data/fist/fist3_10/vol3-10.pdf

...not this....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
Associate
Engineering Fields - Power Engineering - New Member

Join Date: Oct 2015
Posts: 33
Good Answers: 2
#4
In reply to #1

Re: Manual accuracy testing of watthour meters

10/03/2015 10:36 PM

Thank you Sir @SolarEagle this will definitely be of great help.

@lyn Hi Sir, thanks for the information as well

@tchtech thank you sir, but is there a more proper or documented way on how to test such meters using a reference standard, phantom load, some manual switches but without the comparator? I am using a digita reference standard where in it gives the accumulated KWh but since it has no comparator it does not automatically give the accuracy of the said meter.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#5
In reply to #4

Re: Manual accuracy testing of watthour meters

10/04/2015 12:14 AM

Most meter manufacturers have a procedure of testing prior to the meter being sold/leaving the factory to ensure accuracy.

Why not contact the meter manufacturer!

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Manual accuracy testing of watthour meters

10/03/2015 4:55 PM
Register to Reply
4
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#3

Re: Manual accuracy testing of watthour meters

10/03/2015 4:57 PM

Just use a resistive load like a heater and measure the input amperage and voltage then multiply those together to get the wattage and multiply that number times a specific run time.

If your heater draws 10 amps at 240 volts it is using 2400 watts. If that load ran for one hour it would use 2.4 kilowatt hours of electrical power. If you ran it through your watthour meter and it reads anything significantly different than 2.4 kilowatt hours used then obviously it needs fixing.

Register to Reply Good Answer (Score 4)
Power-User

Join Date: Sep 2015
Posts: 482
#6
In reply to #3

Re: Manual accuracy testing of watthour meters

10/04/2015 7:59 AM

If I am to build a kilowatt meter, I will do the same ,install a voltmeter and and ammeter then process readings by means of calculator circuitry with the possibility to correct the reading for calibration purposes-then it's pretty neat that way.

I agree, one way of doing it manually is to measure the voltage and amperage of the circuit by a "reliable and calibrated tester", though he might have difficulty to know the KVA-hr readings as this would mean he has to measure all the time. A data logger would do just that convenient in his absence. Fluke has this type of tester though cost might be around 4 grand.

__________________
The doctor said "just one post or reply aday in CR4, take it or leave it". I said, "what does that mean?"
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#7

Re: Manual Accuracy Testing of Watthour Meters

10/05/2015 11:22 AM

Disk type power meters require special tools and test equipment to correctly check and adjust the disk rotation speed and distance of travel.

Each individual meter requires skilled tasks that are specific to original manufacturer, meter application, and type of meter.

You must obtain the OEM manual for the specific meter in question and follow their required procedures otherwise the results will not be accurate and the meter may be damaged beyond repair.

The number of disk revolutions is proportional to the amount of current flowing through the meter and is based upon the meter scaling.

As already stated: Running a known value of current through the meter for a known period of time will yield whether the meter is operational however it will not yield accurate results unless the source is stable and of the correct magnitude.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8

Re: Manual Accuracy Testing of Watthour Meters

10/05/2015 11:48 AM

Your basic premise; i.e., "...the number of revolutions..." Indicates that you have not researched the meter testing process which requires a particular load vs. time sequence to ensure that the meter is accurate at any operating point, any power factor load, and for any time period, especially if the meter is going to be used for revenue/billing purposes. There's plenty on the web, Google is your friend.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Associate
Engineering Fields - Power Engineering - New Member

Join Date: Oct 2015
Posts: 33
Good Answers: 2
#9
In reply to #8

Re: Manual Accuracy Testing of Watthour Meters

10/05/2015 8:00 PM

Hi guys i appreciate your responses with regards to my concern here. Yeah honestly i am on a process of grasping something new, though it is hard initially but i enjoy the process since it will result into learning something new. It is good to know that there are a lot of people that is also interested in my chosen area.

Thank you so much

Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#10
In reply to #9

Re: Manual Accuracy Testing of Watthour Meters

10/05/2015 11:24 PM

Do your own homework. You were assigned it not us. Ask your instructors, those who know what they want as an answer, and they can teach you how to get it.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

brich (1); Legolaz (1); lyn (1); mrbrightside (2); old salt (1); RAMConsult (1); SHOCKHISCAN (1); SolarEagle (1); tcmtech (1)

Previous in Forum: Optimizing the Design of a Magnetic Circuit Actuator   Next in Forum: Practical Applications of Flyback and Forward Converter?

Advertisement