CBCT On Busbar For Outgoing Feeder

10/20/2015 4:19 AM

Dear All,

We have CBCT mounted on contactor incoming busbar inside panel and contactor outgoing connected with armoured cable to motor.

Now we are facing false tripping of Earth Fault During motor starting and running (approx. 7-8 amp un balance observed)

We have thoroughly checked motor and cable there is no actual earth fault or earth leakage in the circuit.

Kindly advise....

Regards,

T.D.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: CBCT on Busbar for outgoing feeder

10/20/2015 4:38 AM

Do you have a neutral cable running ? Since it is a motor load, it is unlikely. However, if a neutral is there, it should be passing through the CBCT. In such a case there should be no tripping. (Pardon me if i have stated something obvious to you).

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Commentator

Join Date: Jun 2011
Posts: 79
#2
In reply to #1

Re: CBCT on Busbar for outgoing feeder

10/20/2015 4:49 AM

First of all thanx for your reply

There is no Neutral cable running from contactor to motor (only three phases)

Three busbar passing through CBCT at contactor incoming and contactor outgoing connected to Motor cable (3C)

Regards,

T.D.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: CBCT on Busbar for outgoing feeder

10/20/2015 5:02 AM

Yes, as expected. No issue there.

The unbalance you observed...is it vectorially zero? If not, we should wonder where the remaining unbalance current is goimg ... that might be causing the nuisance trip. If the incoming cable before the contactor has a neutral, it would be terminated at some point, and may provide a return path for the unbalanced component.

The basic point is (i am sure you know it, pardon my reiterating) that all current-carrying conductors must pass through the CBCT, and vector sum of all their currents should be zero in a healthy system, even if there is an unbalance. Please see how this can be checked at your installation.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#4

Re: CBCT On Busbar For Outgoing Feeder

10/20/2015 9:28 AM

Is this a new installation or an existing set-up which has worked OK previously?

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: CBCT On Busbar For Outgoing Feeder

10/20/2015 12:01 PM

Imbalance is not the same as an earth fault. One may easily have imbalance without a current flowing in the earth conductor; in extremis it is called a "single phase installation".

Please clarify.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6

Re: CBCT On Busbar For Outgoing Feeder

10/20/2015 12:49 PM

I would check to make sure your voltage is correct for that motor, on all three legs...Is there a delta leg, is it required, is it wired properly?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7

Re: CBCT On Busbar For Outgoing Feeder

10/20/2015 1:43 PM

"...false tripping of Earth Fault During motor starting and running...", if it trips on starting how can you measure the running current? If you're blocking the trip signal and getting a 7-8Amp imbalance, you still haven't told us anything, it could be on a 1,000Amp motor or a 10Amp motor.

You also need to check that the CBCT is sized properly and isn't saturating during any starting or load transients, then check that all the wiring is the same length, sized properly, the connections are correctly polarized, and made-up tightly. This assumes that you have verified that the motor is not at fault (no pun intended).

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: CBCT On Busbar For Outgoing Feeder

10/21/2015 8:52 AM

On starting, a motor can be expected to pull 5-7 times its full load current for a brief period while it accelerates from rest.

It is a fallacy to expect one protection device to provide both overload and cable protection. That is why, in BS7671 and other places, there are two protective devices, often a set of fuses to protect the wiring and often an overload device to protect the motor. The topic of coordination is well covered in the standard.

Please describe how the installation in question differs from that recommended by BS7671 and why?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856