Neutral Grounding Transformer and Resistor Sizing

10/20/2015 12:13 PM

Neutral Grounding Transformer and Resistor sizing

Dear all

For a 200MW 18KV 0.8P.F Generator, we use generator neutral grounding transformer capacity 8MVA 18KV/220V? On what basis was chosen this transformer and how can we calculate the magnitude of grounding resistor across the secondary of the grounding transformer? thanks in advance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Neutral Grounding Transformer and Resistor sizing

10/20/2015 12:16 PM

It is not possible for any other CR4 reader to know the exact reasoning, so the best advice is to go back to the original design documents for the installation and look up the answer there.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Neutral Grounding Transformer and Resistor sizing

10/20/2015 12:41 PM

Neutral grounding transformer/resistor/protective relaying combinations are used to limit the magnitude and duration of the ground fault current to some acceptable values to reduce the internal damage and/or for protective relaying purposes.

Your job is to find the engineer that can choose what those values are and for how long you want it to flow, once you do that then it is a simple matter to use the transformer turns ratio and Ohm's laws to size your resistor, then choose the resistor and transformer short term ratings based upon the amount of time before your protective relaying operates.

Get a copy of the GE Protective Relaying Manual for the actual formulas if you have no experience in these calculations.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3

Re: Neutral Grounding Transformer and Resistor sizing

10/20/2015 6:24 PM

The neutral grounding transformer and resistor size and voltage rating is a decision based upon the original generator design criteria/specifications and is dictated by the Original Equipment Manufacturer.

There are many considerations such as but not limited to:

Machine insulation temperature rating.

Cooling type and size.

Generator winding conductor size and composition.

Type and speed of generator protection scheme.

Generator application (Base load, demand-swing,ETC.)

Altitude at installation location.

Ambient mean temperatures.

As I stated theses are some of the considerations however you need to contact the original generator manufacturer to identify their reasoning and requirements.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Anonymous Poster #1
#4

Re: Neutral Grounding Transformer and Resistor Sizing

10/21/2015 10:25 AM

Am I the only one who gets the crap scared out of me every time there's another "Hello everyone, I am working on a several-killovolt power station, and I apearantly have no qualifications for the job I'm in, because I'm asking a bunch of semi-annonymous people on the internet to advise me on how to set up and run dangerous equipment when they cannot see the equipment, or even know where the equipment is located" thread started?

Call me crazy but if you're going to be setting up a High Voltage electrical supply/substation, shouldn't you be TRAINED in how to work with High Voltage? That means you would either know the answer to these questions, or you would know how to find the answer in the safety regulations for your area, or at least have some contact information on your instructor or whichever agency is responsible for electrical safety in your area? If you're trained and qualified to work with Kilovolt-range circuits, you should have better sources for safety info than the bunch of jabronies who post here, myself included.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5
In reply to #4

Re: Neutral Grounding Transformer and Resistor Sizing

10/21/2015 11:34 AM

No you're not, I believe there's a fair percentage of responders who wonder how some of the questioners even have the cojones to expose their ignorance. In this case though I suspect OP is a newbie designer sitting in an office and will never get to see the actual equipment in service.

I asked the same question when I was a coop student in a major utility, my supervisor immediately sent me on a paper chase through three departments where I was finally able to piece together the "hows and whys" of the various neutral grounding schemes before I went to see them in action. They're usually in a cage so there's no direct danger unless you ignore the "High Voltage Do Not Enter" sign.

Of course being in a generating station has its own myriad risks, but less than 1% of office personnel ever get into one anyhow.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#6
In reply to #5

Re: Neutral Grounding Transformer and Resistor Sizing

10/21/2015 11:47 AM

"I asked the same question when I was a coop student in a major utility, my supervisor immediately sent me on a paper chase through three departments where I was finally able to piece together the "hows and whys" of the various neutral grounding schemes before I went to see them in action."

Ohh that sounds like it was fun, ask a question get sent on a 'snipe hunt' to learn the answer for yourself, with the side effect that you get to meet people from all the departments, and they get to meet you and test out your sense of humor.

Too bad that's considered 'harassment' these days. Did it REALLY hurt people to be sent out for a 'left handed smoke bender,' or for a '200 foot coil of shore line'? The point was to get the new guy introduced around, teach him where the department offices were, and show him that the working world isn't as try and boring as school portrayed it.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#7
In reply to #4

Re: Neutral Grounding Transformer and Resistor Sizing

10/21/2015 1:28 PM

I can has megavolts and resistives?

__________________
common knowledge...less common than common sense
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

adreasler (1); Anonymous Poster (1); PWSlack (1); RAMConsult (2); SHOCKHISCAN (1); The.Tinkerer (1)

Previous in Forum: CBCT On Busbar For Outgoing Feeder   Next in Forum: Sizing of AVR for Air Conditioners

Advertisement