Diesel Generator

11/13/2015 2:36 AM

Hi,

We have three diesel generators working in parallel A,B,C

The Generator A is able to synchronise with B and C but it did not take the load (P=0 KW)

and if I increase the speed it will trip by over speed.

NB: The load sharing system is well working before, and the load was shared between 3 generators.

Could you please help me to reolve this issue

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Sep 2015
Posts: 482
#1

Re: Diesel Generator

11/13/2015 4:36 AM

Yes, why not generator sets can not be connected in series?

__________________
The doctor said "just one post or reply aday in CR4, take it or leave it". I said, "what does that mean?"
Register to Reply Off Topic (Score 9)
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#6
In reply to #1

Re: Diesel Generator

11/13/2015 7:24 PM

Because doing so would most likely let the smoke out of the generators as well as some or everything operating and connected to the downstream bus.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Power-User

Join Date: Sep 2015
Posts: 482
#7
In reply to #6

Re: Diesel Generator

11/15/2015 1:19 AM

I'd intentionally throw that to the guy, so that it will activate his thinking.

__________________
The doctor said "just one post or reply aday in CR4, take it or leave it". I said, "what does that mean?"
Register to Reply Off Topic (Score 3)
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#2

Re: Diesel Generator

11/13/2015 4:55 AM

Is the circuit breaker for genset A closed?

Have you checked your droop control setpoints?

Have you checked the field exciter circuitry, is A operating on reverse power?

Have you tried raising the frequency of A slightly above that of B & C? - It may not come in until you do that.

Have you checked governor setpoints?

Typically for parallel gensets, increasing throttle settings should not increase speed, but should increase its load share - so - if you are, as you say, getting an output from the genset, but it is not going online, and the speed increases, then check the items that I have listed above. It may be a controller failure.

Register to Reply
Participant

Join Date: Nov 2015
Posts: 4
#8
In reply to #2

Re: Diesel Generator

11/15/2015 6:11 AM

Hi,

Thank you to your answer.

- The circuit breaker for genset A Closed

- The exciter checked and we have 400V 50HZ

- Yes I tried to raise the frequency of A till I reach 50HZ

I will replace the controller till I receive the software from vendor

Register to Reply Off Topic (Score 5)
2
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#3

Re: Diesel Generator

11/13/2015 5:55 AM

I think that A is not really connected and that the breaker is tripping out as soon as you try to connect it. If it were connected, increasing the throttle would increase KW and not increase speed.

Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Diesel Generator

11/13/2015 9:25 AM

Was this unit being returned to service after some sort of maintenance? If so then you need to check the wiring from the instrumentation transformers all the way back to the controller, plus any interconnecting wiring between the units. Crosswired droop compensation may cause a similar event.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Participant

Join Date: Nov 2015
Posts: 4
#9
In reply to #4

Re: Diesel Generator

11/15/2015 6:16 AM

The engine was running and it stop by emergency shut down (gas detection)

Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#10

Re: Diesel Generator

11/15/2015 11:30 AM

Not quite sure why OPs responses in #8 & 9 were marked OT since they provide feedback and clues as to what's going on. If the unit trips on some sort of gas detection protection then you must investigate the reason for the trip before proceeding, especially if this unit is on a platform or in a classified area.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Participant

Join Date: Nov 2015
Posts: 4
#11
In reply to #10

Re: Diesel Generator

11/15/2015 12:21 PM

Investigation done and the platform started again but we still have a problem to start the third standby generator

Register to Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#12

Re: Diesel Generator

11/16/2015 7:06 PM

Manuals available? Call to the manufacturer, or distributor? See #5 for reference.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#13

Re: Diesel Generator

11/17/2015 9:44 AM

Previous state:

Load Sharing System was working, load was shared between generators A, B, and C.

Current state:

Generator A running, but not sharing load.

Suggestion:

  1. Confirm that Generator A is still properly connected to Load Sharing System.
  2. Inspect the Load Sharing System, that is the likely 'common point' of the problem.
  3. Go into the internet and look up a skill called 'Toubleshooting.'
    1. Learn it.
    2. Live it.
    3. Love it.
__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

adreasler (1); Legolaz (2); lyn (1); Munster (1); Nader (3); RAMConsult (2); Rixter (1); SHOCKHISCAN (1); spades (1)