11/13/2015 6:52 AM

Given the Total Capacitance of an energized, 300KV cable. How do we calculate the no load charging current in Amps in the cable?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Charging Current in High Voltage Cable

11/13/2015 7:02 AM

You can't without knowing the source impedance and the impedance between the source and the line. Even then it's tricky, as (obviously) the impedance between the source and and any point along the line will vary with the distance.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply Score 1 for Off Topic
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Charging Current in High Voltage Cable

11/13/2015 8:56 AM

The same way one calculates the current it takes to charge a lumped element capacitor with the same capacitance.

It requires an understanding in differential equations. Circuit theory would help, too. If your source is AC instead of DC then you could even get into transmission line theory that Oliver Heaviside developed. The reflected wave from an open load will blow your mind, along with some possible fuses.

Go forth and educate thyself.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3

Re: Charging Current in High Voltage Cable

11/13/2015 9:06 AM

Refer to "Conductor Properties" (NEC Chapter 9 Table 8) for identifying the impedance of the cable. Be sure to read all of the footnotes and references.

Once you determine DC resistance/impedance per foot then multiply the total length of the cable by that factor to get total impedance.

Apply Ohms Law of I=E/R to determine charging current.

This method will only be as accurate as the parameters entered and only if DC voltage is used to charge the cable.

A call to the cable manufacturer will yield more accurate numbers on the impedance factors which will drastically improve results of the calculations.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply Score 1 for Off Topic
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Charging Current in High Voltage Cable

11/13/2015 9:18 AM

Since you only seek the steady state solution Ohm's Law works fine, just remember to use the correct voltage (which is the entire point of this homework/quiz/interview question). How did you answer it?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5
In reply to #4

Re: Charging Current in High Voltage Cable

11/13/2015 9:21 AM

Ahem, Ohm's law is for resistance not capacitance. There is no "C" in Ohm's law.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Score 1 for Off Topic
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6
In reply to #5

Re: Charging Current in High Voltage Cable

11/13/2015 9:29 AM

In AC there is, just substitute impedance for resistance as in I=V/Z, and as a reminder, they're all vector quantities.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#8
In reply to #6

Re: Charging Current in High Voltage Cable

11/13/2015 10:31 AM

Yes, all three variables are complex vector quantities. As I said, Oliver Heaviside's transmission line equations will be needed. Remember it was Oliver that coined the term "impedance".

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#10
In reply to #8

Re: Charging Current in High Voltage Cable

11/13/2015 1:34 PM

Victor knows his vectors. Ask him.

Roger Murdock: Flight 2-0-9'er, you are cleared for take-off.
Captain Oveur: Roger!
Roger Murdock: Huh?
Tower voice: L.A. departure frequency, 123 point 9'er.
Captain Oveur: Roger!
Roger Murdock: Huh?
Victor Basta: Request vector, over.
Captain Oveur: What?
Tower voice: Flight 2-0-9'er cleared for vector 324.
Roger Murdock: We have clearance, Clarence.
Captain Oveur: Roger, Roger. What's our vector, Victor?
Tower voice: Tower's radio clearance, over!
Captain Oveur: That's Clarence Oveur. Over.

Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#7

Re: Charging Current in High Voltage Cable

11/13/2015 10:17 AM

"How do we calculate the no load charging current in Amps"

What other units would it be?

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#12
In reply to #7

Re: Charging Current in High Voltage Cable

11/13/2015 5:01 PM

nano, micro, milli, kilo, mega, giga, tera, peta

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Commentator

Join Date: Apr 2011
Posts: 57
#9

Re: Charging Current in High Voltage Cable

11/13/2015 12:15 PM

Charging current

Thus, a capacitive charging current to earth results in the following formula:

I C = Uo. w. Cb (A/km)

With

Uo = Operating voltage (kV)

w = Angular frequency (1/s)

Cb = Operating capacity (μF/km)

Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Charging Current in High Voltage Cable

11/13/2015 3:19 PM
  • If it is less than the current needed to satisfy the load requirements, then don't worry about it.
  • If it is more than the current that the correctly-sized protective devices can withstand, then the devices will operate. So don't worry about it.
  • If the cable fails before the protective devices operate, then the installation is faulty and will need to be reassessed and rebuilt. Proper Electrical Engineering beforehand will obviate that possibility. If a qualified Electrical Engineer has designed it, then don't worry about it.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#13

Re: Charging Current in High Voltage Cable

11/14/2015 6:30 AM

In my opinion, in a 300 kV cable[173 kV phase-to-ground, See for instance NEXANS Voltage 160/275 (300)kV.]:

http://www.nexans.com/Corporate/2013/60-500_kV_High_Voltage_full_BD2.pdf

the capacitance does not depend on cable layout configuration but the resistance does.

Also the inductive reactance. If no-load is connected at the end of cable the resistance, reactance and

capacity will be in series. For a short length cable the simple "Ohm Law" could be applicable.

So, as already said, for a precise answer you have to know more about this cable.

However, for an approximate result you may neglect the resistance and even the inductive reactance, in my opinion. About 150 to 300 A per km[0.15 to 3 A per meter] it could be possible.

__________________
Julius
Reply Score 1 for Good Answer
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#14
In reply to #13

Re: Charging Current in High Voltage Cable

11/15/2015 1:08 PM

300 Amp per km??? So a 10km cable draws 3,000A before it carries any load? Especially curious when the largest 300kV cable in the Nexan catalog you cite (and makes no mention of charging current) has an ampacity of only 2,400A.

I would leave opinions to the Presidential debates, the engineering facts are as follows:

For single- conductor and three-conductor shielded cables

I= (0.323*f*k*kv)/(1,000*G) A/phase/mile, where f=frequency in Hz, k=dielectric constant of the insulation (XLPE is around 2.3), kv=line to line system voltage in kV, G= 2.303*log10 (2ri/d) where ri = inside radius of sheath and d = outside diameter of the conductorgeometric factor (which varies between 0.5 to 1.5) based on conductor shape, insulation thickness, and mean periphery of insulation.

Using 50Hz, 2.3, 300kV, and 1.0 in the above yields about 11.1A/ph/mile or approximately 7.0 A/ph/km, and can vary between 5 and 14 A/ph/km depending on the actual cable type. NB- inductive and capacitive reactances are very dependent upon the physical layout of the cables, while resistance isn't (except for the small proximity effect)

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#15
In reply to #14

Re: Charging Current in High Voltage Cable

11/15/2015 2:06 PM

Thank you RAMConsult, my mistake: I divided by 18 the capacitance but also the reactance!

However, 9 to 14 A per km it is close to actual. If the capacitance-as declared- it is from 0.14 to 0.22 microF/km the the capacitive reactance has to be Xc=1/(2*pi()*f*Cap) f=60 Hz Xc=18947-12057ohm I=300000/SQRT(3)/Xc I=9.14-14.36 A/km

Calculated the capacitance is less a bit [0.14 it is 0.12 and 0.22 it is 0.19] but a think the manufacturer knows it better.

__________________
Julius
Reply
Reply to Forum Thread 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); Candlez (1); JohnDG (1); lyn (1); Mikerho (1); PWSlack (1); RAMConsult (4); redfred (3); SHOCKHISCAN (1)

Previous in Forum: Diesel Generator   Next in Forum: Tuning Up a Variable Q Circuit

Advertisement