Let Through Energy

11/19/2015 1:35 AM

Formula to calculate Let through energy for cable and circuit breaker?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Let through energy

11/19/2015 1:55 AM

That may be a measured value rather than a calculated value.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Let Through Energy

11/19/2015 7:27 AM

Try reading the manufacturers literature. Commonly referred to as RTFM

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7
In reply to #2

Re: Let Through Energy

11/20/2015 9:33 AM

I agree with you, except the fact , in my opinion, according to BS it has to be RTBM [ instead of RTFM in USA].

However, a Swiss/Switzerland explanation may be taken into consideration. See what ABB try to explain:

https://library.e.abb.com/public/9567591b95e3345b48257b05001b78d8/Protection%20of%20LV%20Cables.pdf

__________________
Julius
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9
In reply to #7

Re: Let Through Energy

11/20/2015 9:57 PM

I've spent too long on here.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Let Through Energy

11/19/2015 2:49 PM

I think that "Let trough energy" of a cable would only apply if you think of the cable as a fuse...

I think the first step is to learn what you are talking about.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#4

Re: Let Through Energy

11/19/2015 5:20 PM

JRaef #3 is correct..."Let through energy" applies only to a protective device.."Energy withstand" applies to a cable.

The protective device manufacturer will supply a current/time curve which can be used to calculate the maximum allowable temperature rise of the cable under fault conditions.

This maximum temperature is its temperature before the fault and its maximum allowable insulation temperature

The temp. rise is proportional to the square of the fault current times the duration of the flow (I²t).

Obviously the energy let through of the device needs to be no more, and preferably less, than the energy withstand of the cable in use.

Cable manufacturers also provide a current/time curve for each of their cables.

The two curves can be used to determine the acceptable energy withstand for your cable selection.

Register to Reply
Member

Join Date: Nov 2015
Posts: 6
#5

Re: Let Through Energy

11/20/2015 12:30 AM

Mr.Spade thanks for detail,

Meanwhile What u explained is nice informative

and i am asking is how to calculte Let through energy of circuit breaker and cables,

So that theoritically we can ensure the design.

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#6
In reply to #5

Re: Let Through Energy

11/20/2015 2:53 AM

The protective device will have a current/time curve applicable to that particular device. Generally only the 5 second operating time at the maximum available fault current would be considered. This maximum available current would take into consideration factors such as the supply energy availability, the impedance of the upstream circuit conductors etc.

You can then either read the operating time for said device straight from the curve and multiply it by the square of the corresponding current to get the let through energy and then compare that figure to the cable manufacturer's published energy withstand figures.

Or...You can plot both the cable withstand time/current curve and the device time/current curves on the same graph, choose an operating time, divide the I²t by that figure and then take the square root of that answer to arrive at the current related to that chosen time.

The let through energy MUST NEVER be greater than the energy withstand value of the cable under the particular conditions of installation involved. A cable protected by a fuse must be de-rated to 90% of that if protected by a circuit breaker.

I suggest you do some further research on the subject to gain a better understanding.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Let Through Energy

11/20/2015 9:38 AM

Er......"can be found in British Standard 7671" - is that the answer?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10
In reply to #8

Re: Let Through Energy

11/20/2015 10:03 PM

No, you need the CB manufacturer's data and then use the adiabatic equation for the cable. Nether of which are in BS7671, it skirts very neatly around the matter.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#11
In reply to #10

Re: Let Through Energy

11/21/2015 3:57 PM

Regulation 434.5.2 of BS7671 Amnd 3 : 2015 does give maximum disconnection time as t = k2S2/I2 , S is sq.mm, I amps and k values in Table 43.1. That's the adiabatic equation. And it does have lots of amp/time curves for standard fuses & MCBs.

Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); 7anoter4 (1); ganesh88 (1); JRaef (1); PWSlack (1); spades (2); TonyS (3); Tornado (1)

Previous in Forum: LaPlace Transforms for this Circuit?   Next in Forum: Fast Acting Earthing Switch

Advertisement