HVAC Chilled Water System

11/28/2015 4:04 PM

In HVAC chilled water circulated system, it is always economical and efficient to select one under sized DRV/Balancing valve for AHUs, Chillers and pumps. For example if the line of chiller out is 6" then a DRV of 5" operated with fully opened condition will save first cost of component instead of selecting 6" DRV to be operated in a throttled conditions. In my service of over 35 years, i had face twice or three times problems in such selection being in adequate which i ratified by reboring the valve seat and spintle little down.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: HVAC Chilled water system

11/28/2015 4:34 PM

so?

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: HVAC Chilled water system

11/28/2015 4:55 PM

The second part of that post contradicts the first.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: HVAC Chilled water system

11/28/2015 5:00 PM

Go ahead.

The odds are in your favor.

Register to Reply Score 1 for Off Topic
2
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#4

Re: HVAC Chilled water system

11/28/2015 5:46 PM

Since you didn't ask a question, I can only guess you are trying to impress us with your knowledge and skills. After insulting everyone here, I would suggest you try that with some other site.

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: HVAC Chilled water system

11/28/2015 8:17 PM

<Exit, stage left>

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6

Re: HVAC Chilled water system

11/28/2015 9:18 PM

" It is important to note that the direction of flow must confirm with the direction of the arrow on the valve body and that the valve must be installed with a minimum of 3 D (3 x nominal pipe diameter) straight pipe in the upstream side. "

http://www.flow-techs.com/Double%20Regulating%20Valves.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: HVAC Chilled water system

11/28/2015 10:55 PM

The arrow (if any) on a valve does not always refer to the direction of normal flow through the valve. Instead, it may refer to the direction in which the valve can stop flow. Those are not the same thing, but the variations can be complicated to explain, and even would-be "valve engineers" sometimes get them wrong.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#11
In reply to #7

Re: HVAC Chilled water system

11/30/2015 2:42 PM

I'm in no way expert on valves, and I'm certainly NOT saying you are wrong, but...

1. Wouldn't the normal flow direction be the same as the direction it can stop flow for ordinary valves?

2. Wouldn't the normal flow direction be the opposite from the direction it can stop flow for anti-backflow valves?

eg.

Unless I'm mistaken, normal flow for the valve shown is to the left, as indicated by the arrow, and flow is prevented in the opposite direction.

Any comments, corrections, or clarifications?

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#12
In reply to #11

Re: HVAC Chilled water system

11/30/2015 4:50 PM

That is a check valve, which is different from an ordinary valve.

In refrigerant control and some other valves, the arrow does NOT necessarily mean what you think it means. The specific variations can be lengthy to describe, which is why I didn't try, but they depend on which side of the valve is under the greater pressure when the valve is meant to be closed, and also to special characteristics of solenoid valves, regulators, etc.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#8

Re: HVAC Chilled Water System

11/30/2015 10:38 AM

If you had to enlarge the intentionally selected under-sized valve after installation to meet system flow demand requirements, then there is not any economical advantage what-so-ever gained by purchasing and installing the under-sized valve.

In fact quite the contrary is true in that the system now has a custom, one-of-a-kind modified valve that will cause severe costly maintenance issues and poor flow control for the customer.

Just so you understand:

Operating the 6 inch valve in the 70-80% range ensures the most accurate linear flow control possible is attained which translates to accurate temperature control, lower maintenance costs, and higher system reliability.

Operating a 5 inch valve in the 90-100% range ensures the flow will be erratic and not linear at all causing system control to be unreliable and increasing maintenance costs.

Initial cost should be the last option to consider when designing and installing any HVAC system as the added energy and maintenance costs build up very quickly and often cause premature failure of the system components and poor system operation.

This is a typical example of a very poor decision based upon false budgetary savings.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Oct 2015
Posts: 11
Good Answers: 1
#9

Re: HVAC Chilled Water System

11/30/2015 12:01 PM

Look into the Cv of the valve. It has to do with the flow characteristics of the valve.

I often explain it this way. When you turn the water to a garden hose, you can crack the valve open and get a little flow. Turn it a quarter turn and you get about 50% of the full flow. Going another quarter turn you get about 80% of full flow. Then you can turn the knob 3 more times and the flow doesn't really change at all. - This valve have poor flow chararcteristics for controllability.

When a valve is too big you'll get 80% flow when the valve in 30% open, so you end up trying to controll everything between 0-30% open. This causes the valve to wear out fast with something called 'wire drawing' effect.

If you put a 6" valve in a 6" line, it will likely be difficult to control. You may need a 5" or 4" valve. If you want to just guess and not deal with Cv you can just go down 1 size.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#10

Re: HVAC Chilled Water System

11/30/2015 2:34 PM

http://www.engineeringtoolbox.com/valve-selection-guide-d_35.html

As a follow up to my earlier reply the above link will supply extremely valuable information on proper control valve selection for achieving linear flow characteristics.

There are many other such documents available on the web for free downloading from other reliable, competent sources.

Most valve manufacturers offer cage, seat, shaft, and "spintle" replacement options that include a new valve information tag illustrating the modifications so as to avoid future issues caused by undocumented valve modification.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dkwarner (1); Fredski (1); JohnMechEngr (1); Kilowatt0 (1); lyn (2); SHOCKHISCAN (2); SolarEagle (1); Tornado (3)