Dear all,
Please share your knowledge for the below,
We have a plant which 10nos. of 415V, 1600kVA gensets individually connected to 415V/11kV transformers then to synchronising and distribution panel. the generator neutrals are solidly earthed. this plant is for 2year operation only and its on rental base. so we need to minimumise the cost of execution. the questions are here.
1) The generator step up transformer is generally low voltage side delta and high voltage side star, I hope the reason is to provide ref. protection for the transformer high voltage side pls. let me know any reason other than this
2) If the generator neutral is earthed and transformer low voltage side is delta, which protection can be provided for the genset winding fault. (differential protection v need to avoid since it is not economical). is it it ok if one single element earth fault relay operating by a neutral CT provided in the genset star point to earth path?
3) Since there is transformer in between the genset and switch board is this relay will operate for external fault? or is it will operate as a restricted e/f for between generator and transformer low voltage side?
ie if the e/f setting of genset neutral protn. relay is 20% and the user end e/f setting is higher than this, genset should not trip (discrimination)
4) The concern is generator shall be protected for winding faults. but v need to avoid differential relay. pls note the cost diffence between diffrntl relay and e/f relay is around 3500$ and 6nos. of cl-x CTs per unit, an extension box is required to accommodate the cts in genset neutral. Other than winding fault genset having all protections as its own relay (over current, short circuit, reverse power)
5) The distance between genset to the sync panel is around 50meters and the cables can be consider as in a fault free zone. its in ladders
Thanks for your valuable information