Generator Step Up Transformer Scheme

12/01/2015 4:52 AM

Dear all,

Please share your knowledge for the below,

We have a plant which 10nos. of 415V, 1600kVA gensets individually connected to 415V/11kV transformers then to synchronising and distribution panel. the generator neutrals are solidly earthed. this plant is for 2year operation only and its on rental base. so we need to minimumise the cost of execution. the questions are here.

1) The generator step up transformer is generally low voltage side delta and high voltage side star, I hope the reason is to provide ref. protection for the transformer high voltage side pls. let me know any reason other than this

2) If the generator neutral is earthed and transformer low voltage side is delta, which protection can be provided for the genset winding fault. (differential protection v need to avoid since it is not economical). is it it ok if one single element earth fault relay operating by a neutral CT provided in the genset star point to earth path?

3) Since there is transformer in between the genset and switch board is this relay will operate for external fault? or is it will operate as a restricted e/f for between generator and transformer low voltage side?

ie if the e/f setting of genset neutral protn. relay is 20% and the user end e/f setting is higher than this, genset should not trip (discrimination)

4) The concern is generator shall be protected for winding faults. but v need to avoid differential relay. pls note the cost diffence between diffrntl relay and e/f relay is around 3500$ and 6nos. of cl-x CTs per unit, an extension box is required to accommodate the cts in genset neutral. Other than winding fault genset having all protections as its own relay (over current, short circuit, reverse power)

5) The distance between genset to the sync panel is around 50meters and the cables can be consider as in a fault free zone. its in ladders

Thanks for your valuable information

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Generator step up transformer scheme

12/01/2015 6:25 AM

Consult a qualified Electrical Engineer locally, for it would appear that none is available to help with this design activity.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2015
Posts: 335
#2

Re: Generator step up transformer scheme

12/01/2015 6:56 AM

I seconded PWSlack.

__________________
"And ye shall seek me, and find me, when ye shall search for me with all your heart."
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3

Re: Generator Step Up Transformer Scheme

12/01/2015 9:34 AM

1) Adequate system protection can be facilitated on a DELTA or WYE system. The reason for having a WYE distribution system is usually to allow lower voltage-to-neutral circuit capability to meet attached equipment requirements.

2) Avoiding differential protection in my opinion is a suicidal decision. What you need to be considering is what the cost will be for replacing a generator or multiple generators should conditions arise that require differential protection. (The cost of differential protection compared to cost of replacement.)

The earth fault relay protection should be considered as a separate component.

3) The physical location of the CT(s) and their connection(s) determine the protection zone.

I strongly suggest you hire an outside, competent electrical protection specialty company to look at your system and provide guidance before proceeding.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#7
In reply to #3

Re: Generator Step Up Transformer Scheme

12/02/2015 12:41 PM

Thanks, mostly differential protn. Provides for high voltage systems only. I don't know y no any genset manufacturers r not providing it as in built provision in their relay.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Generator Step Up Transformer Scheme

12/01/2015 11:33 AM

The obvious people to ask about this are the people you're hiring the equipment from.

They may just have a vested interest in protecting "their equipment" from incorrect installation by you the customer.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: Nov 2006
Posts: 2
#5

Re: Generator Step Up Transformer Scheme

12/02/2015 12:02 AM

Dear Gentleman,

In reference to your first point, regarding design of Transformers and keeping its LV side as Delta and HV side as Star, the important reason is to optimise engineering and cost of the raw materials.

In case of LV side, current is more. due to delta configuration Phase Current gets reduces by root 3 times, i.e. Ph I = Line I/root3. hence less copper in the LV winding.

Similarly, in case of HV side, due to star configuration Phase Voltage gets reduces by root 3 times, i.e. Ph V = Line V/root3. hence less insulation in the HV winding.

the above concept plays major role while designing a transformer.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#6
In reply to #5

Re: Generator Step Up Transformer Scheme

12/02/2015 12:31 PM

Thanks, your reply is very clear

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8
In reply to #6

Re: Generator Step Up Transformer Scheme

12/02/2015 6:10 PM

"...your reply is very clear...", while true, is totally irrelevant/unrelated to your questions about protective relaying.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#9
In reply to #8

Re: Generator Step Up Transformer Scheme

12/03/2015 12:46 AM

sir, i was awaiting you, he mentioned about transformer design concept only, ie why the transformer low voltage side is delta and high voltage side is star. of course its not related with protective relaying. but im sure there is something since you remarked it. request your valuable recommendations.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#10

Re: Generator Step Up Transformer Scheme

12/03/2015 2:00 AM

1. The low voltage delta is there to provide a path for certain harmonics and/or zero sequence currents so that they don't crossover into the high voltage side. "Hope" plays no role in serious engineering design.

2. "...need to avoid since it is not economical...", really? In actuality these small generators usually don't have the individual neutral leads brought out for the requisite differential CTs, instead a single CT is located in the neutral lead after the star point.

3. It is not intended to operate on faults outside the protection zone, but it depends upon being properly set up.

4. One thing that won't be sensed is a fault in the last 20% of the winding closest to the neutral.

5. So you believe that 50 meters of cable laying unprotected in a cable tray is a "...fault free zone..."? Cables do fail, and the zone between a generator and its transformer is in the an area with the highest potential available short circuit current.

If you value your client's installation you should immediately step aside and seek competent engineering assistance.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#11
In reply to #10

Re: Generator Step Up Transformer Scheme

12/03/2015 5:14 AM

dear sir,

its job in hand and under negotiation for cost reduction, its true that normally for low voltage gensets there wil b no space to provide diffntl cts in the neutral side, if v need to put they have to go for non standard design which is cost impact. so v r thinking to put 1no. nuetral ct in the star to earth point of genset. my question is as you said if it will not operate for a fault in the transformer secondary (external). the percentage of protection can be changed no? instead of 20% we can set it to 10%. for cable protection the relay in the genset will take care. For transformer secondary wil provide ref. relay. how ever as u advised we may ask assistance from a protection co-ordinator.

thanks

Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#12
In reply to #10

Re: Generator Step Up Transformer Scheme

12/05/2015 7:45 AM

Dear sir, please refer the attached scheme and would you advice about the protection provided, regarding..

Genset having its own protection relay, will this operate on any over current even in the transformer secondary also? so it will protect the cable. e/f relay provided will protect the winding, 85%. differential protn. is not considered. scheme is typical for 10nos gensets

thanks

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

lpandey (1); Mr. small (1); PWSlack (1); RAMConsult (2); roykav (5); SHOCKHISCAN (1); TonyS (1)