Anonymous Poster #1

Overloading of S1 Duty Motor

12/04/2015 9:57 AM

Dear sir, I have S1 Duty motor with "B" class insulation used for winch type application in material charging buckets. This is intermediate duty. In present condition When bucket moves up with material it takes 120% of full load current but during downwards movement after material discharge it takes around 65% of full load current. Motor winding temperature is stable around 93 DegC.

There is continuous up-down movement with 130 Sec up moment time, 130 sec down moment time and 10 sec rest time during material charging & discharging. Motor is of 345 KW, 440V AC. Motor is running with VVVF drive.

Motor is running in this condition for more than last 6 months. Regarding the same I have following questions:

1. How much overloading can be allowed in S1 duty motor?

2. It is advisable to increase the charging material quantity furthermore in which overloading may be around 130% in up cycle?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: Overloading of S1 Duty motor

12/04/2015 10:08 AM

if its really an S1 its continuously duty rated

Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#2

Re: Overloading of S1 Duty Motor

12/04/2015 5:27 PM

1) Maximum nameplate current rating. Overloading a motor continuously will cause it to prematurely fail.

2) No, it is not a good idea to further overload the motor at 130%.

Since the motor is already experiencing a 120% overload condition I would suggest you purchase a new motor large enough rated to handle the increased load if you want the equipment to operate reliably.

It would be best for you to contact the Original Equipment Manufacturer of the motor and ask them your questions if you want to be absolutely sure.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Overloading of S1 Duty Motor

12/04/2015 5:43 PM

You should monitor temperature, that's the bottom line....class 'B' insulation I think is good for 20k hrs @120°C....

http://www.pdhonline.org/courses/e156/e156content.pdf

https://www.youtube.com/watch?v=cMG2hTac39M

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Overloading of S1 Duty Motor

12/04/2015 6:33 PM

What is the service factor of the motor?

This should be on the nameplate.

93°C is not too hot.

You can run the motor at 130% load if you want.

Even 150% load may be OK.

You won't know until you try it.

Let us know how it works out for you.

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10
In reply to #4

Re: Overloading of S1 Duty Motor

12/07/2015 9:17 AM

Lyn, for motors in the IEC world there is no such thing as "Service Factor" as we know it in NEMA world. All of their motor designs are what we would consider a 1.0SF, with the possible exception of S9. All the rest of their design designations, S2 -S8, are variations of what we would call "intermittent duty", S1 is continuous duty, but no Service Factor at all.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11
In reply to #10

Re: Overloading of S1 Duty Motor

12/07/2015 12:46 PM

Thanks. Yes, I lived/worked in the NEMA world.

Looking at his operating temperature it would seem the motor is not being overworked.

Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#5

Re: Overloading of S1 Duty Motor

12/05/2015 5:40 AM

Are the materials used in the motor winding made according isolation class B (max 130°C) and is the temperature rise in de motor limited to a temperature rising according class B (50 to 130 gives an allowed temperature rise from 80°C)?

Or

Are the materials used in the motor winding made according isolation class F (max 155°C) and is the temperature rise in the motor limited to a temperature rise according class B (50 to 150 gives an allowed temperature rise from 100°C)?

In this latter case, you have a much more safety margin.

Reply
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#6

Re: Overloading of S1 Duty Motor

12/05/2015 7:01 AM

For this application you should select S4 duty motor. Sorry no overloading permitted on such motors.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7

Re: Overloading of S1 Duty Motor

12/06/2015 1:06 AM

I agree with suresh Sharma. The actual duty has to be S10.

In my opinion, if no pause is expected- the motor operates continuously in this cycle-no overload is permitted. If I1=120% within 130 sec and I2=65% within 130 sec the average current Iav=sqrt((I1^2*t1+I2^2*t2)/(t1+t2)) is 96.5%

__________________
Julius
Reply
Anonymous Poster #1
#8

Re: Overloading of S1 Duty Motor

12/06/2015 8:37 AM

Thanks to all for your valuable feedbacks

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Overloading of S1 Duty Motor

12/06/2015 3:43 PM

If it were allowable then, logically, it wouldn't be an overload! Thanks for this post, for it has considerable amusement value. Do keep a list of motor suppliers and some fire extinguishers to hand, for they will inevitably be needed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#12

Re: Overloading of S1 Duty Motor

12/30/2015 9:26 PM

Duty cycle is related to the number of starts per hour, It has nothing to do with overloading the motor. You will need to use the correct KW motor to stop the motor from overloading and select the correct duty cycle to prevent premature failure.

Reply