Anonymous Poster #1

Power Metering

12/07/2015 2:47 PM

Hello,

Please consider that I need your assistance regarding the following:

Im a consultant working on a project where a power meter of 500A needs to be installed on the main incomer of the main distribution board. The client advised that it is not a common practice to install a 500A meter and he requested to specify 2 Cut out cables protected by 250A each, but he wants to keep one power meter! Is it possible to have one power meter installed on 2 Cut out cables?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Power Metering

12/07/2015 3:24 PM

Your question makes little in the way of sense so I will not try and decipher what you are asking.

I will say that... normally, such a service would be metered by CTs down stream of the main disconnecting means. The CTS then feed into a regular revenue meter.

Better talk to an Electrical Engineer.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Power Metering

12/07/2015 3:27 PM

What planet is this project located on?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Power Metering

12/07/2015 4:29 PM

You'll need to hire a COMPETENT consultant.

You and Fire Pump Selection Boy (and other anons) are poster children for banning anonymous posters.

Pardon the redundicity.

Reply
5
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Power Metering

12/07/2015 7:10 PM

Give your client their money back, you're taking money under false pretences.

__________________
The reports of my death are greatly exaggerated.
Reply Good Answer (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: Power Metering

12/07/2015 7:59 PM

There is no better occupation than separating fools from their money; even charlatans can spend it better.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6

Re: Power Metering

12/08/2015 5:52 AM

It is common practice for high current metering to use a Current Transformer(s) - CT(s) - connected to a single meter. The cable(s) carrying the current to be metered must pass along the middle of the axis of a ring-shaped CT. High voltages above about 400 also usually have potential transformers between supply & meter.

Since the voltage & if the supply is 3 phase, 3 wire, 3 phase 4 wire or single phase is not given (which may require 1 to 3 CTs), nor country or accuracy requirement & installation is determined by mechanical constraints, only a local specialist could advise you. In this context, "wire" may actually be 2, 3 or 4 in parallel at the same voltage to handle a high current

I suggest entering "electrical supply metering" in Wikipedia or another web information site which will give explanations & pictures.

67model

Reply
Power-User

Join Date: Nov 2015
Posts: 335
#7

Re: Power Metering

12/08/2015 8:10 AM

Refer to the electrical local code and standard that should be the primary requirements. As a consultant, your professionalism is bind with your local electrical code and standard.

May be there's a secret on it.

__________________
"And ye shall seek me, and find me, when ye shall search for me with all your heart."
Reply
2
Anonymous Poster #2
#8

Re: Power Metering

12/08/2015 9:06 AM

For half of your consulting fee,you may consult with me for advice on electrical problems.

You must send payment in advance,because I may have other expenses,such as consulting other consultants when I have no idea what to do.

These consultants may be part of a forum of volunteers that may or may not have a clue also,but will advise freely.

The last ones I will consult will be the local Authority Having Jurisdiction,so all of my advice will be subject to being negated by the AHJ,and is not guaranteed to be approved by the AHJ.

None of my advice will be guaranteed to conform to any recognized engineering standards,but it will be supported by lots of opinions,therefor my results come with no guarantee,express or implied.

Therefor,All advice given should be verified with a licensed,fully qualified consultant.

For an exorbitant fee,including accommodations and travel,and daily expenses,I will be would be willing to testify as a self proclaimed,non qualified consultant in case of insurance,civil,or other lawsuits arising from the use of such advice.

I remain at your service.

I.B. Suomynona

Reply Good Answer (Score 2)
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#9

Re: Power Metering

12/08/2015 2:46 PM

You did not say if this is a 3 phase or single phase system.

A "window" type induction CT of the proper ratio can be used to accurately measure the current of two or more conductors passing through it as long as both conductors are the same phase and the current direction is the same in both conductors.

Most CT suppliers provide free installation diagrams and advice/guidance for installing their products.

If you are not familiar with CT applications it is in your customer's best business interest and in your best safety interest that you obtain the services of a competent, experienced system's protection specialist to review the application and provide safe direction.

BE AWARE THAT OPEN-CIRCUITING A LIVE CT SECONDARY WINDING IS IMMEDIATELY LIFE THREATENING.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2015
Location: Johannesburg, South Africa
Posts: 248
Good Answers: 3
#10

Re: Power Metering

12/10/2015 2:21 PM

The danger here is 1st, that your client definitely think he knows better than you and that is very very unusual if you are the consultant.

Bring a qualified person on the clients cost to explain the process to him and also do the installation, you and your client may kill somebody. The client can later deduct it from your fee.

__________________
Tragedy for Engineers is thinking they know so much that they can not learn from any body else.
Reply
Reply to Forum Thread 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Anonymous Poster (1); lyn (1); Mr. small (1); North of 60 (1); Oomborrie (1); SHOCKHISCAN (1); TonyS (1); Tornado (2)

Previous in Forum: House Wiring Has Me Puzzled!   Next in Forum: Relation of Earth Conductor Length With Fault Capacity

Advertisement