Relation of Earth Conductor Length With Fault Capacity

12/08/2015 7:37 AM

Dear sir, My substation is situated at 7 th floor and all earth pits are at ground level, now my query is does earth strip length affect fault current capacity. Does transformer kept at ground level and at 7th floor will have same strip size for neutral and body

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Relation of Earth Conductor Length With Fault Capacity

12/08/2015 7:39 AM

British Standard 7671, preferably before someone gets hurt/killed, please.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Relation of Earth Conductor Length With Fault Capacity

12/08/2015 8:23 AM

The fault current won't pass down the strip to the earth nest, it will go pass through the N→E link at the transformer. (Assuming one is fitted).

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3

Re: Relation of Earth Conductor Length With Fault Capacity

12/08/2015 2:21 PM

"my query is does earth strip length affect fault current capacity."

Yes it does. All electrical conductors have an impedance-per-foot/meter factor that must be taken into consideration when designing a ground/earth grid for a substation. If the conductor is not sized properly it can be damaged and/or burned into by excessively high fault current.

"Does transformer kept at ground level and at 7th floor will have same strip size for neutral and body"

I am not clear on what you are asking. What is "body"? Are you talking about the transformer frame and enclosure? Or?

You must refer to and adhere to the applicable local code and design requirements for the application.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Participant

Join Date: Nov 2014
Location: mumbai
Posts: 2
#4
In reply to #3

Re: Relation of Earth Conductor Length With Fault Capacity

12/08/2015 9:01 PM

Sir, If by calculation transformer frame earth and neutral earth strip size at ground level coming to 300 sq.mm ( transformer installed near Earth pit at 3 meters) , then same strip size can be used for same capacity transformer which has installed at 50 meters from earth pits.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5
In reply to #4

Re: Relation of Earth Conductor Length With Fault Capacity

12/08/2015 10:42 PM

The impedance of earth conductor and earth rod should be minimum

__________________
pnaban
Register to Reply Score 2 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: Relation of Earth Conductor Length With Fault Capacity

12/09/2015 3:49 AM

Sure, and its CSA and cost should be maximum.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#10
In reply to #4

Re: Relation of Earth Conductor Length With Fault Capacity

12/10/2015 9:56 AM

Not having knowledge of or a copy of the applicable electrical code for your area I cannot accurately answer the question.

However, my advice is:

The minimum conductor size would be 300 sq. mm however you must factor in the impedance presented to the circuit by the length, type of metal, ambient temperatures, and installation method of the conductors.

1) Determine/calculate the maximum earth/ground fault current available in the circuit.

2) Consult the applicable conductor amperage table to identify the correct size of conductor/bus required to safely handle the maximum available fault current.

3) Consult the applicable conductor size and type properties table to identify "impedance-per-meter" values.

3) Multiply the "impedance-per-meter" value by the total length of the conductor/bus/strip to determine total impedance presented to the circuit.

4) Based on the results of the above steps apply OHMS Law to determine if the impedance presented by the conductor length will cause enough of a voltage drop to limit the amount of current flow through the conductor during a fault condition.

5) If the impedance presented by the length of the conductor is high enough to negatively affect the fault current capacity of the conductor to the degree the system voltage does not meet equipment protection requirements then you must increase the conductor by one (1) size larger to ensure there will be no damage to the conductor during fault conditions.

6) Note: You must be sure to identify the required conductor insulation by identifying the installation method and all site conditions that affect the current carrying capacity of the installed conductors. (Temperature, humidity, Installed in free-air, enclosed bus duct, conduit, ?)

If this does not make sense then I strongly recommend you hire an outside consultant to perform the calculations and provide their recommendations.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#7

Re: Relation of Earth Conductor Length With Fault Capacity

12/09/2015 5:14 AM

Length matters.

In your calculations and estimates "length" should appear frequently as a significant result influencing variable. If not then you are probably not on the right track or are using the wrong software tool or staring at a table on the wrong page in the standards.

A ground fault on the primary (MV?) side has different consequences to a ground fault on the secondary LV side.

Then there's lightning and structure and quiet earths as well.

That's a start for you.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8

Re: Relation of Earth Conductor Length With Fault Capacity

12/09/2015 9:53 AM

The LV side of the transformer should be firmly earthed local to the transformer. Any earth fault will take the route of lowest resistance.

If you have the correct bonding in place for circuits fed from the 7th floor transformer almost no current will pass through the down conductor. It will go direct to source and not meander up and down the building.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9
In reply to #8

Re: Relation of Earth Conductor Length With Fault Capacity

12/10/2015 5:06 AM

How about the MV to the transformer?

An earth fault on the primary needs to be considered too.

Echo what you said about LV faults.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#11

Re: Relation of Earth Conductor Length With Fault Capacity

12/10/2015 12:18 PM

I agree with PWSlack: for low-voltage see BS7671 clause 54. However, for medium voltage BS7430 it would be suitable more.

NEC allow only copper and aluminum for electrode-or equipment- grounding conductor. No length limit is recommended. The cross-section corresponds to live conductor cross-section. See, for instance art.250-66.

See also The Indian CODE OF PRACTICE FOR EARTHING IS-30043/2006? SECTION 2 CONNECTIONS TO EARTH.

__________________
Julius
Register to Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#12

Re: Relation of Earth Conductor Length With Fault Capacity

12/11/2015 4:50 PM

A suitable earth conductor attached to the building structure should be at the 1st floor and the ground grid outside the building. A suitable conductor from the ground of the transformer attached to the building steel at the 7th floor will be more than sufficient.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#13
In reply to #12

Re: Relation of Earth Conductor Length With Fault Capacity

12/11/2015 10:02 PM

Could be a concrete structure....

Also, a steel building frame is not the place to connect a PE.

Any grounding of a steel structure is not for the convenience of reticulating a convenient electrical path to ground up and through the building. The frame grounding is for protecting the frame and those who may come in contact with it.

PE must be connected to a ground point that was designed and installed for that purpose.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply